Cavitation in centrifuge pumps

09/17/2007 12:08 AM

We are installing cooling tower with 3M height x 5M x 6M. Cooling tower is 1M underground. Cooling tower pumps will be in pump room 25 meter away from cooling tower. Suction pipe will be from cooling tower bottom, travel 25 meter underground & connected to pump which is at 0.7 Meter above ground. Does this arrangement will create any cavitation problem?

Register to Reply
Pathfinder Tags: cooling piping Pumps
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Biology - New Member Hobbies - Musician - New Member APIX Pilot Plant Design Project - Member - New Member Hobbies - CNC - New Member Fans of Old Computers - ZX-81 - New Member

Join Date: Jan 2007
Location: Centurion, South Africa
Posts: 3921
Good Answers: 97
#1

Re: Cavitation in centrifuge pumps

09/17/2007 2:02 AM

It is highly advisable to have somebody inspect the plans and do proper calculations.

Alternatively you should give more detail.

Temperature of water? Flow rate? Suction pipe diameter? NPSH of pump? etc etc.

__________________
Never do today what you can put of until tomorrow - Student motto
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#5
In reply to #1

Re: Cavitation in centrifuge pumps

09/18/2007 2:42 AM

Assuming that the level of the water in the cooling tower sump is kept above the pump suction level then this is not an unusual design. As to whether you will get cavitation or not, it is a matter of supplying the information as suggested by Hendrik.

__________________
If you can't explain it simply, you don't understand it well enough. (A.E.)
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#2

Re: Cavitation in centrifuge pumps

09/17/2007 10:39 AM

Probably, and quite probably at some point you will flood the cooling tower. As Hen the cat suggests, have a local pump expert carefully review the plans and proposed setup and design the problems out before construction starts.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Power-User

Join Date: Dec 2005
Posts: 200
Good Answers: 8
#3

Re: Cavitation in centrifuge pumps

09/17/2007 11:17 PM

Cavitation is certain if the system is gravity fed.

__________________
Corn Stoves
Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#4

Re: Cavitation in centrifuge pumps

09/18/2007 1:28 AM

First you will flood the tower, then you will have cavitation problems for a while...

__________________
Aged man is not old man...
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#11
In reply to #4

Re: Cavitation in centrifuge pumps

09/19/2007 11:36 AM

I do not entirely agree with your sequence, it really depends on the system set-up and operation.

I have seen cooloing towers start up and operate successfully with the pump suction elevated 1 to 1.5M above the cold water basin level. The trick is in the details.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Commentator

Join Date: Apr 2007
Location: Mid Atlantic Region
Posts: 72
#12
In reply to #11

Re: Cavitation in centrifuge pumps

09/19/2007 12:49 PM

You are right. If losses through the suction pipe are low, temperature of the water isn't too high, and the NPSHR of the pump is low - there should be no problem with a 1 to 1.5m lift.

Register to Reply
Anonymous Poster
#6

Re: Cavitation in centrifuge pumps

09/18/2007 3:59 AM

We design & install cooling systems every day from 10kW to 100 MW 2"NB to 48" pipe

Register to Reply
Commentator

Join Date: Apr 2007
Location: Mid Atlantic Region
Posts: 72
#7

Re: Cavitation in centrifuge pumps

09/18/2007 5:49 AM

As others have said - it depends in part on the liquid level in the sump/base of the cooling tower, and additionally the line losses to each pump - not all suction lines are created equal, the water temperature - warmer water is more prone to cavitation, and the design of the pump - not all pumps are created equal.

If you employ a local pump person, you need to be certain he has only your interests in mind - i.e. don't count on the guy selling you the pump to give you the whole and accurate picture. Beyond the sale of the pump - he's also looking forward to selling you repair parts and services.

Good Luck.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#8

Re: Cavitation in centrifuge pumps

09/18/2007 8:20 AM

You can refer this to the pump manufacturer who can confirm whether your pipe size layout etc is in order and there will be no cavitation. Many pump manufacturers have computer simulation and can easily check this.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Anonymous Poster
#9

Re: Cavitation in centrifuge pumps

09/18/2007 8:25 AM

Don't create a design problem, put the pumps imediatly adjacent to the cooling tower in a flooded suction manner.

Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#10

Re: Cavitation in centrifuge pumps

09/19/2007 1:15 AM

You are requested to provide the following data at least :

a. Piping isometric for suction line with all dimensions and sizes, showing all fittings, flanges, elbows, valves, .... etc.

b. Piping material.

c. NPSH of the pump.

d. Water Flow rate.

e. All pump data.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply
Active Contributor

Join Date: May 2007
Posts: 13
#13
In reply to #10

Re: Cavitation in centrifuge pumps

09/22/2007 4:03 AM

Suction pipe line diameter is 350mm. Pump capacity is 375m3/hr. 3 pumps connected parallel, 2 will be in use 1 stand by. Water temp will be 35-38 deg c.

Register to Reply
Commentator

Join Date: Apr 2007
Location: Mid Atlantic Region
Posts: 72
#14
In reply to #13

Re: Cavitation in centrifuge pumps

09/24/2007 8:24 AM

Good information. Additionally, what is the difference in height between the liquid in the bottom of the cooling tower and the centline of the suction of the pumps? What is the discharge pressure generated by the pumps, What speed do the pumps run (RPM)? Do you know the diameter of the impellers of the pumps? Am I correct in thinking these are single stage pumps? Do you have access to the pump curves?

Register to Reply
Power-User
Popular Science - Cosmology - New Member

Join Date: Aug 2007
Location: Virginia
Posts: 122
#15

Re: Cavitation in centrifuge pumps

09/29/2007 9:35 AM

The centrifuge pumps Ive seen are fairly solid. Only time cavitation would be a problem is if the pump was to far from the source (vertical distance, which also depends on viscosity) or the input line was to small. To predict this ask pump manufacturer for max vertical on the input. Keep the input line the same ID as the opening on the pump itself. I like to keep a slight restriction in the output on a flat run to keep the pump at a higher working pressure but if your going vertical you don't need that at all ... LOL

__________________
The major difference between a thing that might go wrong and a thing that cannot possibly go wrong is that when a thing that cannot possibly go wrong goes wrong it usually turns out to be impossible to get at or repair...Douglas Adams
Register to Reply
Register to Reply 15 comments