design model of a HVAC for a chemical process plant

02/12/2008 11:51 PM

I would like to design a HVAC plant for a chemical process plant (API's), please provide me the data for 3000sft.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#1

Re: design model of a HVAC for a chemical process plant

02/13/2008 11:18 PM

What's your plant volume, required air turnover rate, temperature, relative humidity etc?

__________________
If only you knew the power of the Dark Side of the Force
Reply
Participant

Join Date: Feb 2008
Posts: 2
#2
In reply to #1

Re: design model of a HVAC for a chemical process plant

02/14/2008 1:19 AM

3000 sft x 8' ht., about 20-25 air changes, 22-25 temp.65%

Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#3

Re: design model of a HVAC for a chemical process plant

02/18/2008 12:09 AM

Your plant air volume is 3000 x 8 = 24,000ft3.

With 20 - 25 air changes/hour, you'll need a fan or blower that can handle 8,000 to 10,000cfm or air.

To achieve 65% RH at 22oC to 25oC, you can either cool the air first then remove the moisture, or you can remove the moisture first, then cool it. You'll need to consult a psychrometric chart for the information.

There are two ways to dry the air, refrigerated drying, or chemical adsorbents.

I'm not a HVAC engineer, so I can only provide you with some guidelines so that you'll have a basic idea what to raise when you meet with the HVAC engineer you're consulting for the project.

__________________
If only you knew the power of the Dark Side of the Force
Reply
Participant

Join Date: Feb 2008
Posts: 2
#4

Re: design model of a HVAC for a chemical process plant

02/24/2008 6:21 AM

What is your heat load ? Lets assume You need 50 BTUH/SF. 3,000 Sf X 50 =150,000BTUH, =12.5 tons system ( 15 tons )

To control A/C go to: www.kunne.us

Also, www.palmbeachrd.com

Teppo K. Jokinen ( BSME )