Cable Size Calculation Problem

05/28/2008 11:33 PM

could anyone help me solving this problem for cable size?

The cable should be installed from the Secondary of the transformer to Main Distribution Panel.

The distance(between the Secondary and MDP) is 520m, and we should use 600V CV cable.

The Transformer is 3 phase 1,500 kVA. It transforms 10kV into 380-220V.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#1

Re: cable size calculation problem

05/28/2008 11:55 PM

Since the length is substantial, i would suggest using 6 runs of 300 sq mm single core copper (SWA/XLPE) for each phase.

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Active Contributor

Join Date: May 2008
Posts: 13
#2
In reply to #1

Re: cable size calculation problem

05/29/2008 2:05 AM

I think as far for the selection of cable for 1500 kva transformer we have considered even the voltage drop because the distance is quite far from the main distribution panel so i would suggest you better go for 1c-630sq mm (11 cables) 3 cables for each phase and 2 neutrals. Correct me if iam wrong.

Register to Reply
Anonymous Poster
#3

Re: cable size calculation problem

05/29/2008 2:38 AM

hi,

more than answering ur question I am curious to know how u managed to insert the diagram?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: cable size calculation problem

05/29/2008 3:04 AM

Use the camera button in the reply message editor to select a picture file. The original poster has scanned the diagram into a file and done just that.

Sparkstation's postings give some idea of what can be done.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Participant
Malaysia - Member - New Member

Join Date: May 2008
Posts: 3
#5
In reply to #3

Re: cable size calculation problem

05/29/2008 3:46 AM

Thanks for the answers, but could you guys show me how do you do all the calculations to decide the size of cable to use?


-> Just click on the camera icon to add pictures

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#7
In reply to #5

Re: cable size calculation problem

05/29/2008 4:01 PM

Voltage drop in the UK is limited to 4 % (I believe -- correct me if I'm wrong, PW or Del), so you want no more than that in 520 m.

Copper has a resistivity of 1.7 X 10-8 Ohm - m. Resistivity = Resistance X Cross Sectional Area / length. Rearranging, Resistance = Resistivity X Length / Cross Sectional Area, or Cross Sectional area = Resistivity X Length / Resistance.

Voltage drop = Current X Resistance. Current in a 500 kVA (1 of 3 phases) line at 220 Volts is 2273 Amps. Maximum resistance of conductor for 4 % drop at 220 volts is 8.8 volts / 2273 amps = 0.00387 ohms.

Minimum Cross Sectional Area (sq. meters) = 1.7 X 10-8 ohm-m X 520 meters / 0.00387 ohms, or 0.00228 sq. meters, or 2283 sq. mm. for no more than 4 % voltage drop.

Of course, it's better to have less voltage drop.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply Score 1 for Good Answer
Participant
Malaysia - Member - New Member

Join Date: May 2008
Posts: 3
#9
In reply to #7

Re: cable size calculation problem

05/30/2008 1:55 AM

thank you for the detailed calculation Bill, I really appreciate it, but, according to the AWG table, there is no such wire with the cross section area of 2283 sq. mm. it seems too big.

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#10
In reply to #9

Re: cable size calculation problem

05/30/2008 7:56 AM

True, there's not a conductor that I know of which has a cross-section of 2283 sq. mm., but 2_2000 MCM has a cross-section of 2700 sq. mm., or 3_1500 MCM has a cross-section of 2526 sq. mm.

This similar to what ahmed952 suggested: use 3_630 sq. mm. cables for each phase, however doing so will yield a voltage drop of a little over 4 % at full load. Four 630 sq. mm. cables for each phase will keep you under 4 % at full load.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#6

Re: Cable Size Calculation Problem

05/29/2008 11:45 AM

Would it be easier to move the location of the transformer, using either overhead or underground HV cables?

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Guru

Join Date: Sep 2007
Location: Wrong end of the yellow brick road in Oz
Posts: 930
Good Answers: 15
#8

Re: Cable Size Calculation Problem

05/30/2008 12:36 AM

I guess the supply is fed from the street to a transformer just inside the boundry of your property by your electricty supplier?

At the levels your talking about, don't just calculate on the cable guage (I generally run on about 10A per mm2 )

You also have to look at the effect of voltage drops on each and every termination point.

There is a company close to here, they measured the voltage drop from 1 end to the other, about 1/2Km, similar distance to what your using, and calculating the voltage drop in the wiring, they were still falling short, until they measured the drop across each termination, Transformer -> wire, wire -> wire, wire -> load.

__________________
Qn, Whats the differance between a Snake and a Onion? Ans, No one cries when you chop up a Snake
Register to Reply
Anonymous Poster
#11

Re: Cable Size Calculation Problem

05/30/2008 8:28 AM

6 set of (4) 600kcmils copper with 75 degree c. insulation. Will give you 2,520 amps of conductor.

The 1500kVa transformer will have 2,275 amp output on the secondary side of the transformer

Register to Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#12

Re: Cable Size Calculation Problem

05/30/2008 9:45 AM

Am I to assume this is an industrial setup and not domestic as suggested by an earlier poster? If it's industrial, it maybe cheaper to install a new transformer closer to the MDB! I may be wrong ( so please correct me if I am ) but coming directly off the secondaries of the transformer would require some kind of switch gear/fuses directly after the transformer so that the LV line could be isolated without touching the HV side and also to protect the transformer if a fault should happen on the LV line!

Would be good to know what you intend doing with all of those Amps and if you intend to use them all at the same time but as yet, you haven't told us so I won't be able to offer you more than 2cents worth!

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Anonymous Poster
#13
In reply to #12

Re: Cable Size Calculation Problem

05/30/2008 11:27 AM

Moving the transformer closer to where the power is required and extending the high voltage primary feeder would substantially reduce the amount of copper required on the secondary of the transformer to the incoming main circuit protective device and reduce copper required and the installation cost.

Less distance, less copper, less cost.

Register to Reply
Anonymous Poster
#14

Re: Cable Size Calculation Problem

06/02/2008 2:05 PM

Hi,

In your case you have to consider only the voltage drop. I assume that you will install the cables on ladder or tray, therefore the temperature and laying factor are not really important (but not extrem situation) because of the length.

To solve this Problem, please give following data

1. Max. allowable voltage drop

2. According which regulation; IEC, VDE, BS?

3. What net you have? TN-S; TN-C?

4. Just for information; what cable type you use for? XLPE, PVC, EPR

Best wishes from black forest

Wormnhaque

Register to Reply
Anonymous Poster
#15

Re: Cable Size Calculation Problem

11/27/2008 6:41 AM

1500 KVA 1000 KVA 3000KVA

CABLE COMPLETE DETAILS SINGLE CORE AND MULTI CORE

Register to Reply
Anonymous Poster
#17
In reply to #15

Re: Cable Size Calculation Problem

11/27/2008 7:13 AM

1500 KVA 1000 KVA 3000KVA

CABLE COMPLETE DETAILS SINGLE CORE AND MULTI CORE

Register to Reply
Anonymous Poster
#19
In reply to #17

Re: Cable Size Calculation Problem

07/16/2010 11:20 AM

sorry i dont know friend

Register to Reply Off Topic (Score 5)
Anonymous Poster
#16

Re: Cable Size Calculation Problem

11/27/2008 6:46 AM

1500 KVA 1000 KVA 3000KVA TRANSFORMER COMPLTE CABLE DEATILS WITH DIAGRAM

Register to Reply
Anonymous Poster
#18
In reply to #16

Re: Cable Size Calculation Problem

06/07/2009 10:35 AM

Very interesting.would like to know any CT/PT are to be installed at the outlet of the secondary transformer immediately or near the MDB which is away at around 35 meters away from the transformer.The transformer rating is 120 kva and how much voltage drop can be anticipated and maximum current can be considered.Pl. excuse if anything wrong in furnishing the details as i have very little knowledge in ele. eng.

Register to Reply
Anonymous Poster
#20

Re: Cable Size Calculation Problem

08/24/2010 4:27 PM

I=S/1.732*Vsec, WHERE S=VA,

therefore, I=1500kVA*1000/1.732*380Vsec

=2279A.

Consult NEC Cable sizes, for example: 250mm2 has 354amps.

I=2279A/354A=6.4

Say 7 sets of (4C 250mm2).

That's it!

Also consider Voltage Drop of the Cable, cable manufacturer has a complete definition regarding this matter..

Vd should not exceed 5% from transformer down to the last equipment.

Let say, 1% from transformer, 2% from MDB to DB, then 2% from DB to last utilizing equipment..That's the standard i usually used. When exceed get higher size.

CR4 Admin – E-mail address removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.

thank you!

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#21

Re: Cable Size Calculation Problem

01/26/2017 12:08 PM

Dear Mr.kreyszig,

The cable selection is decided on the following.

1. Voltage Drop

2. Type of Cable that is to be used.

3. De-Rating Factor applicable

4. Thermal Rating or Temp. Rise allowable.

5. Power Factor in the system.

6. Loading pattern - whether steady load or intermittent over load/no.of starts if motor is connected.

DHAYANANDHAN.S

Register to Reply
Register to Reply 21 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ahmed952 (1); Anonymous Poster (8); Bill (2); chaterpilar (1); dhayanandhan (1); kreyszig (2); Mr. Truman Brain (2); PWSlack (1); Snaketails (1)