Survey on 120/240 volt North American Residential Services

07/13/2008 11:19 AM

This is a survey for use in a paper.

  • Please do not offer any explanation for your answer as it may influence others in how they vote.
  • Please post your answers anonymously so not to influence the interpretation of the data or influence others in how they vote.
  • Please consider sending in a response as the quality of the data is a direct result of the sample size.
  • If you wish to explain an answer or offer a comment please send it to my CR4 mailbox.

-----------------------------------------------------------

Question...

On a North American 120/240 volt 3 wire residential service, is there a 180° phase shift present between (L1 & Neutral) and (L2 & Neutral).

Answer...

A) Yes... there is a 180° phase shift present between (L1 & Neutral) and (L2 & Neutral).

B) No... there is no 180° phase shift present between (L1 & Neutral) and (L2 & Neutral).

Question...

Please place yourself in one of the following groups.

Answer...

C) Electrical Engineer.

D) Engineer, but not Electrical.

E) Electrical Trades person.

F) Trades person, but not Electrical.

G) Other then one of the above.

Question...

H) I reside in North America.

I) I do not reside in North America.

Question...

J) How many years of experience do you have?

-----------------------------------------------------------

A suggested response may look like...

"A - C - H - 25"

Or

"B - E - I - 15"

Thanks folks...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Pathfinder Tags: survey
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 12:35 PM

The problem with trying to do a research poll on a forum such as this is that once people start posting answers, a good percentage of responders will read the previous answers and just go along with the perceived majority.

If you are serious about this, either set up an anonymous email address to send responses to, or post this in another forum that has a Polling feature, usually those using php forum protocol. In those, you get radio buttons (click check boxes) to indicate your responses but you do not see the overall response progress until after you submit. Then once your respond, you see the graph of responses and are locked out from responding again.

One issue though, you are usually limited to 3 questions so you will need to condense your poll a bit.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3
In reply to #1

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 1:25 PM

Your points are well founded. The data will be used to determine if a full blown study is called for. Hopefully the people who respond will do so based on their convictions. We will factor in your comments.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8
In reply to #1

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 4:51 PM

I see and concede your point.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#41
In reply to #8

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 4:32 PM

When you get close enough to the can to read the label, and you see it says "worms", why do you feel the need to open that can?

A - G - H - 30

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#2

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 12:55 PM

North

B-D-H-50

"Guest"

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 1:46 PM

How about 'C' the question isn't right.
If neutral isn't a phase..e.g it's tied to ground/earth it can't be phase shifted relative to anything.

So that's

C, Felis Domesticus G,I, 30

Del anon

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #4

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 3:02 PM

Re-read the question. The question is... "is there or is there not a phase shift between the "L1 & Neutral" relative to the "L2 & Neutral".

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#6
In reply to #5

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 4:31 PM

That is badly worded... If it means a phase shift between L1 and L2 why doesn't it say so?

"L1 & neutral" is a meaningless expression....unless it means the phase difference between 'L1 and neutral'....which as I said before doesn't exist...!

The mentioning of neutral at all is confusing, ambigiguous and irrelevant.

If I really have to spell it out...image I have the two leads from my KrisDelTM Phaseomatic phase meter each with a croc' clip on the end......

To measure the phase difference between "L1 & Neutral" and "L2 & Neutral" I must connect a croc' clip to each of those two ponts.
How the heck do I connect to "L1 & Neutral" ???? or "L2 & Neutral" ???...
Do you see it is nonsense?

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #6

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 4:49 PM

No it is not a "meaningless question". On our system here in North America, we have a potential difference of 120 volts between either of the two lines and the neutral and a potential difference of 240 volts from line to line.

Some people claim, while others do not, that there is a 180 degree phase shift between the two 120 volt systems.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#9
In reply to #7

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 5:05 PM

" On our system here in North America, we have a potential difference of 120 volts between either of the two lines and the neutral and a potential difference of 240 volts from line to line."

EXACTLY .... between 2 points L1 & L2

THE MENTION OF NEUTRAL IS IRRELEVANT & CONFUSING

It is like asking what is the difference between.
1&5 and 7&3 ?
It is gobbledegook!

Please read #6 carefully, if you really can't understand the explanations I shall unsubscribe quiety...

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#10
In reply to #9

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 5:19 PM

I am not asking about L1 to L2. I'm asking about a phase difference between "L1 to the neutral" then from "L2 to the neutral". Perhaps you might want to skip this exercise.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#14
In reply to #10

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 2:08 AM

Sorry if I'm being an arse.
I'm not trying to wind you up for the hell of it...there is obviously some missunderstanding of basics somewhere...maybe I'm being thick ... but I think there is no 'phase difference between "L1 to the neutral" ' as you put it.

The phase difference is between L1 and L2... each of which may be measured referenced to any common point.
So to carry out my phase meter (or 'scope) explanation, the meter would have some common connection, like the ground clips on a scope probe...but neutral would not need to be connected at all.

Sorry if I've wound you up or been a pain, cheerio

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#18
In reply to #14

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 5:51 AM

Del the cat, in the USA the line drop in to the home is 240 ac with a neutral. 3 wires from the pole. The transformer on the pole is a center tap output being fed from one of three phase lines from the power plant.

In the home the circuit breaker panel has the 3 wires in L1 L2 neutral also a ground wire tied to a ground rod. If it is the main panel then the neutral and ground ARE tied (bonded) together. Remote panels have 4 wires back to the main panel and the neutral and ground ARE NOT connected in the remote panel.

I hope this helps.

Now to what the OP is asking; In AC there is only one phase feeding the transformer in so there only one phase out.

Now if you are looking at the AC it self then one half is positive and the other half is negative. But at different times. Even if you used a scope to look at it the peaks would not line up. The positive to negative peaks are 180 degrees out. This is used in AC to DC circuits with Rectifiers.

Sorry for the rambling. And my apology to the OP for discussing this here.

metalSmith's

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#23
In reply to #14

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 7:55 AM

Hi Del... No you have not wound me up nor are you being an "arse".

I did not want the discussion we are having to take place. I really needed to gauge the "understanding" level of the people who responded. The mere fact we are discussing this at this point, kills the validity of any data I might have been able to collect. That is why I asked for both anonymity and no discussion.

Our 120/240 volt 3 wire residential service used in North America consists of two 120 volt sources. These sources are derived from a common magnetic core driven by a single phase high voltage winding in the utility transformer.

We connect the two windings in series. We call the connection point between the two windings the "neutral" and tie it to ground as our reference.

So... some people call the two power lines "L1" & "L2" while others call them "Phase A" and "Phase B".

The end result is that some people say that the first 120 volt source "L1 TO THE NEUTRAL" is shifted by 180° relative to the the second source, which is "L2 TO THE NEUTRAL".

This, the use of the neutral as our reference point, has contributed to this situation.

Notice I try not to offer an opinion as to which answer is correct, "yes there is a phase shift" or "no there is not a phase shift". I will have to follow JRaef's suggestion and move this effort elsewhere.

If anyone does wish to continue this, please move it to the private message system.

Rick...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#31
In reply to #14

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 9:35 AM

Del, in being such a pain, you are pointing out a serious difficulty within the international discussion of electrical practices.

I say ground, you say earth

We use 60Hz, you are 50

I do get the sense that eventually some of the electrical safety differences on how a system gets safely grounded (sorry, earthed to the rest of the world!) will eventually be resolved, but as individuals we do need to open our minds to understand how others understand and describe the issues.

To further cloud the issue, I occasionally get involved with AC grounding, DC negative returns, DC grounding within the same building. Throw in some lightning protection, and there ends up a lot of buried copper for worker safety. It is critical that we all end up on the same page and understand where these electrons end up when things go awry.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Anonymous Poster
#44
In reply to #10

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 4:58 PM

I have to agree with Del! There is no "phase difference between either L1-Neut. or L2- Neut. There is only a difference in phase between L1-L2. Neutral is a common (Hence the name NEUTRAL. ie: the definition from Webster-


Main Entry:1neu·tral Pronunciation: \ˈnü-trəl, ˈnyü- Function:noun Date:15th century

1 : one that is neutral 2 : a neutral color 3 : a position of disengagement (as of gears)

In three phase systems there is a 90 degree shift from L1-L2 and another 90 degree shift from L2- L3. This cancels out the EMF thereby reducing hysteresis and allowing maximum current flow.

Non- eng Electrical tradesman 22yrs. exp

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#47
In reply to #44

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 7:58 PM

A voltage must always be measured between two points. (There may be considered to be a potential at a point in a field or along a wire, but that potential only has meaning in reference to some other point that is considered zero potential).

Thus the voltage of L1 or L2 is meaningless without defining some point as zero. The only logical zero point for 120V use is neutral, since it is common zero for both phases. In that case, one voltage is the voltage between L1 and neutral (L1-Neut.), and the other voltage is that between L2 and neutral (L2-Neut.), and YES, there IS a phase difference of 180° between those two voltages (L1-Neut. and L2-Neut.)

Likewise a phase shift or phase difference (at least as used in AC power voltages) only has meaning if there are TWO AC voltages. If you measure between L1 and L2, you are measuring a single voltage, so there can be no phase difference.

You must be using a pocket version of Webster! Mine includes adjective definition #7: "in electricity, neither negative nor positive; uncharged" If that doesn't imply zero Volts, then what does it imply?

You say: "In three phase systems there is a 90 degree shift from L1-L2 and another 90 degree shift from L2- L3. This cancels out the EMF thereby reducing hysteresis and allowing maximum current flow." In 22 years, you still haven't learned that the principal advantages of three phase power stem from three equal 120 degree phase shifts, which overlap such that one of the phases is always near peak, so a device can turn on at any instant and have power available at that instant.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#76
In reply to #47

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 9:23 AM

I have learned enough to have been licensed as a Journeyman in 4 seperate states.

How many licenses do you hold? have you held?

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#78
In reply to #76

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 11:24 AM

Only one, but approaching 60 years of working with electricity/electronics in one form or another. My current partner/employer never asked if I had a license, only if I could solve his problems. That I have been doing for a dozen years after retiring from my first career (Physics).

So is it 90° or 120°?

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#81
In reply to #76

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 2:02 PM

What is a 'Journeyman' and why do you need a licence??

In the UK we have engineers, technicians and mechanics Where does Journeyman fit in?

John.

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#82
In reply to #81

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 2:10 PM

after 5 years apprenticeship you test to become a journeyman. Traditionally Journeymen travelled the countryside working under different Masters to develop their trade.

Here in the states we have Electrical Engineers that design the systems, Journeymen who install and repair/ maintain, train apprentices. The license requirement is a way for the local governing body to get more money, with the added benefit that where required the person doing the work is qualified.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Power-User

Join Date: Aug 2007
Posts: 479
Good Answers: 9
#83
In reply to #81

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 2:12 PM

E*

*"Electrical" tradesman who has completed training; no longer considered an "apprentice" in the trade union. Note: "E" herein as defined in original post by "North of 60".

Sorry for butting in.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#84
In reply to #81

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 7:21 PM

Electroman,

The terms "master, journeyman, apprentice" are derived from the old guild terms for people learning a craft or trade, all the way back into the middle ages. This use of the terms is much older than our country's existence on the west side of "the pond". Laws usually require an apprentice to work under the direct supervision of a journeyman or master for 2-3 years before being eligible to take a journeyman's exam. A journeyman must work for an additional 2-3 or more years under the supervision of a master (but not direct continuous supervision) before being allowed to take a master's exam. Certain types of schooling can substitute for these years of work experience--an associates degree in a similar technical trade for the apprenticeship, and an engineering degree for both. However, the test is mandatory before receiving the status.

These craftsman's licenses are issued by the governmental authority with legal jurisdiction. They can choose to administer their own tests or accept results from independent (private) testing agencies, or reciprocally accept licensing from a nearby governmental authority, or accept certification by a trade union. I have taken tests which were entirely written, and others with both a written and an oral portion. In some jurisdictions, the inspector can have you arrested on the spot if you are not carrying a craftsman's license while doing the work. More commonly, however, they will simply order all work to cease until the licensing has been taken care of.

Work has to be done by a licensed contractor who employs a person with a master craftsman's license. Many jurisdictions also require the contractor to be licensed as a businessman (with insurance, etc.). Thus, to do work within a city, I usually need two or even three separate licenses before I can be issued a permit for the work. After the work is done, I still have to get an inspection to satisfy the jurisdiction that the work was done in accordance with all applicable laws/codes. If there is county-wide or state-wide licensing of craftsmen, then the only local license(s) I would need are business and/or contractor. 'Tis expensive to do all this.

Cheers--JMM

Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#85
In reply to #84

Re: Survey on 120/240 volt North American Residential Services

07/17/2008 2:03 AM

'craftsman's licenses '

What a horrible juxtaposition of words...many true craftsmen have never taken an exam in their lives.

My Brother was a Taxidermist for the Natural History Museum in London....
Currently does leatherwork for Rolls Royce and restores old underlever shotguns..

No 'certificates' or 'Licences' there...

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#86
In reply to #84

Re: Survey on 120/240 volt North American Residential Services

07/17/2008 8:50 AM

Thanks for the explanation JMM.

It all sounds a bit of a bureaucratic nightmare to me!

We have some daft laws recently passed which means a householder can not fit or modify any electrical wiring in a bathroom with out a certificate of compliance from a qualified inspector... It doesn't matter that you may be a fully trained electrician working in your own house, you would still need to have the inspection done...

Of course most people don't bother, as who is going to enforce it, or even know that you've done the job??

Crazy situation!!

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#87
In reply to #86

Re: Survey on 120/240 volt North American Residential Services

07/17/2008 12:17 PM

And here WE are, prattling on about how WE live in the land of the free, and have our liberty, and yet Big Brother seems to live in OUR house, not yours. Go figure, huh?

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 6)
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#52
In reply to #44

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 11:30 PM

Wow!

__________________
There is more to life than just eating mice.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#75
In reply to #44

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 9:20 AM

this was me too!

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#89
In reply to #44

Re: Survey on 120/240 volt North American Residential Services

07/17/2008 1:15 PM

90 degrees?? Seems to me to be 120 degrees in 3 phase...

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#90
In reply to #89

Re: Survey on 120/240 volt North American Residential Services

07/17/2008 2:47 PM

I'll check the fletchings on my arrows...

Yup 120o it is

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#91
In reply to #90

Re: Survey on 120/240 volt North American Residential Services

07/17/2008 3:47 PM

You got ELECTRIC arrows?!? WOW! (What a shocking revelation...)

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#94
In reply to #90

Re: Survey on 120/240 volt North American Residential Services

07/18/2008 10:02 PM

FYI - if needed:

Two-phase systems (90° between phases -shift-difference, in an other situation: lag - lead) maybe still exist in some Ancient US State(s). Also maybe in special processes or outside NAFTA. Remember Servos?

Three -phase (0°, 120°, 240° or -120°, 0, +120° = A,B,C or U,V,W or x,y,z or L1,L2,L3 or T1,T2,T3 etc...).

Two phases are almost like three phases, right? First - grow up, second -learn, third -apply.

Gogo La Giraffe

Register to Reply Off Topic (Score 6)
Anonymous Poster
#12
In reply to #9

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 11:17 PM

We had a discussion about this a few months back...

Del, I disagree on this one... If I only connect to L1 and L2, either (A) There is a phase difference between them and I measure a voltage (presumably 240VRMS), or (B) there is no phase difference and I measure close to zero Volts.

But I am a very visually oriented person; I want to SEE the phase difference. To see it, I need to connect the ground of my 'scope (powered through isolation transformer) to neutral, and connect one channel to L1 and the other to L2. When I do, I get the results as Follows:

A-G-H-57

Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#11

Re: Survey on 120/240 volt North American Residential Services

07/13/2008 6:56 PM

The question has two possible meanings.

If you hook your scope ground to L1 (OK, use an isolation transformer - ruin my fun) and the probe to L2, there is no phase difference.

If you connect the two neutrals (no, I don't know why there are two neutrals - there just are) and then hook the scope ground there, one channel probe to L1 and t'other channel probe to L2, you get a 180° phase shift (just hit the ole A+B) button).

You might consider reposting with a diagram.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#28
In reply to #11

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 9:18 AM

But you responded with "B" in your original response to the poll . . . Given your 'scope test, you have just proved it to be "A."

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#30
In reply to #28

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 9:32 AM

Well, of course. Remember that I'm both an engineer and a liberal. So, if you ask a question, I give at least four answers:

1) choice "A"

2) choice "B"

3) there's not enough information

4) I don't want to hurt the self-esteem of those who are wrong

Anyway, in the middle of my scope experiment and answer, I realized that I would have answered differently if I had done that first.

A foolish consistency is the hobgoblin of little minds. Ralph Waldo Emerson

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#77
In reply to #28

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 9:24 AM

90 degrees out

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#33
In reply to #11

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 10:59 AM

At my home (and every other one I have checked across the US), all neutrals connect to the same buss bar. There are not two neutrals. Someone mentioned that remote panels had ground and neutral separate. I'm not sure what is meant by that - I've never seen a residence with multiple breaker panels.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#38
In reply to #33

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 3:11 PM

Someone mentioned that remote panels had ground and neutral separate. I'm not sure what is meant by that - I've never seen a residence with multiple breaker panels.

I wasn't that "someone," but remote panels do have separate buses for ground and neutral, with ground being connected to the panel case (and of course to ground through the main panel) but with the neutral bus being insulated from the case. Of course, if things are wired up, the remote neutral bus is connected to the remote case too -- back though the neutral to the common neutral/ground bus in the main panel. I'd have to think for while about why this arrangement might be necessary. This article shows a pretty typical remote panel.

__________________
There is more to life than just eating mice.
Register to Reply Off Topic (Score 6)
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#53
In reply to #33

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 11:45 PM

dkwarmer and Blink Hello,

What I was talking about in home electrical is; true, most homes only have one circuit panel and the neutral & ground buses ARE tied/bonded together there they are one and the same at that point. There potential should be zero voltage to any thing other than L1 or L2 then it would read 120VAC. of course the potential between L1-L2=240VAC.

The other is sub-panels it could be a retro-fit to an older system,the new system feeding the old or could be an addition needing more space or garage/work shop, or a mobile home, power from the pole to the meter head to a main breaker then 4-wire in to the distribution panel inside.

Like I'd had said to feed the sub-panel the 4-wire cable black/red/white/green go to

black-L1, red-L2, white-neutral, green-ground. The neutral buss and the ground buss should have the tie/bond bar disconnected so the cables carry back to the main panel the neutral and ground separately. The reason is the neutral is to only carry the only the return current from the device. Then the ground only carries the fault current if there is a failure of the device provided it has a ground prong.

By separating the ground and neutral helps to prevent ground loops by having only one common tie point in the main panel.

metalSmith's

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#80
In reply to #53

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 12:29 PM

Thanks. I had never heard the term ground loop used for powerline AC frequencies, only at much higher ones.

Dick

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#79
In reply to #33

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 11:32 AM

This is referred to as bonding. Bonding is where the Neutral and ground are electrically bonded to achieve the same difference of potential. Examples:

  • the main panel in a home has the neutral and ground bonded.
  • If, however, you install a seperate panel in a garage or outbuilding; That neutral would not be bonded to ground.
  • This allows for only one return path to ground markedly reducing the chance for an electric shock.
__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#13

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 12:49 AM

North of 60--

A, E, H, 37+.

Perhaps the wording in the first section should have said "phase difference".

--"anonymous user"

Register to Reply
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#15

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 2:55 AM

If we call the neutral line 0V, then at 0 degrees, L1 is +120 and L2 is -120. At 90 degrees, all three wires are at 0V. At 180 degrees, L1 is -120 and L2 is 120. That would have to be considered 180 degrees out of phase, wouldn't it? If the (L1 - neutral) signal and the (L2 - neutral) signal were in phase, we wouldn't have 240 V from L1 to L2.

What would the other view be?

In this article, one paragraph reads:

  • Power systems in American households and light industry are most often of the split-phase variety, providing so-called 120/240 VAC power. The term "split-phase" merely refers to the split-voltage supply in such a system. In a more general sense, this kind of AC power supply is called single phase because both voltage waveforms are in phase, or in step, with each other.

But just above that statement is this one:

  • If we mark the two sources' common connection point (the neutral wire) with the same polarity mark (-), we must express their relative phase shifts as being 180o apart. Otherwise, we'd be denoting two voltage sources in direct opposition with each other, which would give 0 volts between the two "hot" conductors.

"relative phase shifts". Hmmm. Seems we could say that one is "phase shifted relative to the other by 180 degrees". Or we could say "180 degrees out of phase". If there are two waveforms, there is only one phase shift, (of 180 degrees); there are not two phase shifts that are 180 degrees apart. The waveforms are 180 degrees apart.

I imagine the confusion is exacerbated by the fact that we call the wires of a three phase system "phases", whereas a phase does not really refer to a physical object -- it is a measurement in degrees of rotation.

__________________
There is more to life than just eating mice.
Register to Reply
Anonymous Poster
#16

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 4:03 AM

B, G, H, <1

Register to Reply
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#17

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 4:47 AM

my answer is B-F/E-H-22

I have been in consumer/Industrial Electronic repair 14+yr

The last 8yrs has been in CEM's systems manufacture and integration and testing.

CEM=Continuous Emission Monitoring


metalSmith's

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply
Power-User

Join Date: Jul 2008
Location: Chester, SC, USA
Posts: 308
Good Answers: 19
#19

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 6:28 AM

A-G-H-25

__________________
...That's why we call it "Research"!
Register to Reply
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#20

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 6:46 AM

So, here's what I think the problem is. I went to the best visualization I know for checking phases: a lissajous figure. The trouble is that I can't figure out how to connect a scope in the strict meaning of the OP. So, for my two cents, it becomes only a semantic exercise until that is clarified.

North of 60, sorry to so disregard your original instructions, but when you ask engineers...., well

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#32
In reply to #20

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 10:45 AM

From my way of thinking, The OP mentioned neutral. I think we can all agree that the neutral is connected to ground/earth (and either the center tap of a single winding, or the common point of two equal windings, of the transformer supplying the energy).

The word neutral implies zero Volts. The only way we can have two 120V supplies is for the neutral to be zero. The only way we can get two 120V supplies to add to 240V is if the positive side (at a given instant) of one 120V supply is connected to the negative side (at the same instant) of the other 120V supply.

So for your Lissajous figure, you connect the 'scope's ground to... ground(neutral)! Then you connect vertical to L1 and horizontal to L2, or vice-versa.

I personally prefer to to use the lissajous for observing frequency differences (when reasonable ratios exist), and to observe horizontal displacement of the signals on a chopped dual-trace 'scope for observing phase differences (channel A to L1 and Channel B to L2 or vice-versa).

The only way I could consider the two voltages to be in phase is to make zero be L1, but then we don't have two 120V sources, we have a 120V source between L1 and neutral, and a 240V source between L1 and L2

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#40
In reply to #32

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 3:50 PM

I agree with every word, comma, and period* in this post. GA I say.

*Although I suppose a period at the end of the post would be a nice touch.

__________________
There is more to life than just eating mice.
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#46
In reply to #40

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 6:02 PM

Oops! Ah here it is: (.) and thanks!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#48
In reply to #32

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 8:11 PM

I think using Lissajous figures on an oscillograph to look at phase is an OF thing. When I got my back against a wall and can't think of anything better to do, I often revert to tricks of yesteryear.

I guess the real problem (for me) with this question is what it means to be in phase or 180° out of phase in an electricity system. We call an ordinary transformer single phase, yet the two ends appear to be out of phase relative to a CT. We can't call 240VAC two-phase, so what is it? Does single phase mean out of phase (and, if so, I gotta sneaky question about how a Variac knows how to keep this straight).

I don't know. Do you have a good way to always think about this? I know how to work with the %^@@* stuff - I just don't know how to talk about it.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#49
In reply to #48

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 8:55 PM

"an oscillograph" I think I saw one once, but I can't remember where...

I'm an OF too (assuming we both have the same interpretation of OF) I got my first little start in electricity just as WWII was ending...

I thought that is why they use the term 'split phase' for the 240V, to avoid misunderstanding. The term 'out of phase' MUST refer to a comparison of TWO AC voltages, so NO, single phase does NOT mean out of phase.

My way of looking at it is always with respect to zero volts. As I've said in two other posts in this thread, zero must be the common connection for the two 120V lines. We don't have 240V at all unless we move zero to either L1 or L2. (we must use an isolation transformer to do this with common oscilloscopes) The neutral is only used for safety on a 240V device. With only 2 wires (L1 & L2), phase has no meaning except in terms of instantaneous time from zero crossing.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#54
In reply to #49

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 5:39 AM

I wondered if you would pick up on that. I cut my teeth on one, though I didn't begin messing with electricity till Ike was in the White House.

I think the whole question is maybe complicated by how we measure. I appreciate your answer and I have to think about this some more.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Off Topic (Score 5)
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#51
In reply to #48

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 11:28 PM

I just read through a bunch of definitions for "phase," phase angle," and "phase shift." This page itself provides various definitions for phase shift, some nearly contradictory. Many of the entries on this page are from linked glossaries, which define phase, phase angle, phase cancellation, etc.

If you read through enough of these glossaries, you will find many definitions fully 180 degrees out of phase with other definitions. Perhaps we all go through phases in life during which these definitions shift. Some will lead in understanding these new definitions, others will lag. As we move through the cycles of life... (oops, gotta stop, I'm starting to wretch).

If you pick some reasonable definition for "phase" out of this soup, then add the word "single," three," or "split" in front of "phase," then you get another level of confusion. Here's one pretty good definition of phase (from the Glossary of Studio Monitor Terms:

  • Phase: the relative measurement of a period of time referenced to the start point of a cycle of a periodic waveform.

Then, "three phase current" would mean "three relative measurements of a period of time current." There. That clears everything up pretty well.

This sort of substitution can make common wiring tasks much easier to understand. You've probably heard the potentially confusing statement: "To reverse the rotation of a three-phase motor, just swap any two phases." This is far less confusing if we substitute the definition for phase each time the word appears: "To reverse the rotation of a three-relative-measurements-of-a-period-of-time-motor, just swap two relative measurements of a period of time."

Another approach to this stuff is to just wear rubber soles and keep one hand in your pocket all the time. Would you rather watch an oscilloscope or a real TV?

__________________
There is more to life than just eating mice.
Register to Reply Off Topic (Score 6)
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#55
In reply to #51

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 5:43 AM

Well, one is more entertaining, but the other one has more content. I keep forgetting which is which.

Thanks for the links.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Aug 2007
Posts: 479
Good Answers: 9
#61
In reply to #32

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 9:08 AM

The only way I could consider the two voltages to be in phase is to make zero be L1, ........

Well, that is not the only way. You could make zero be L2 and follow along with the rest of your argument exactly as before.

Your answer is the best one.

Register to Reply
Power-User

Join Date: Nov 2007
Location: Dominican Republic
Posts: 278
Good Answers: 10
#21

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 7:45 AM

B-D-I-38

Register to Reply
Anonymous Poster
#22

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 7:52 AM

"A - D - I - 30"

Why have I posted "off topic"?

North of 60 has probably given up with his original quest.

Register to Reply Off Topic (Score 5)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#24
In reply to #22

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 7:57 AM

Ya pretty much...

I'm going to post this else where, as suggested by JRaef, when I do I'll post the URL here.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#25

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 8:32 AM

A-C-I- 38

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply
Anonymous Poster
#26

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 8:55 AM

Two observations:

1.) For your new survey you might like to distinguish between (or conjoin) electrical engineer and electronic engineer for the UK audience.

I regard myself as an electronic engineer and so answered D not C.

2.) At the top of the page next to the title there is a check box for I want to post anonymously, which nearly everyone ignored.

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#27

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 9:12 AM

Having read many of the responses, I must first agree with JRaef, and then with Del.

I think one of the problems you face is that people who have no knowledge of electricity wouldn't know that the wording in question one was good or bad, much less which answer would be right.

Given that, I'm not even going to answer any of them.

By the way, I'm a professional electrical engineer.

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Power-User

Join Date: Aug 2007
Posts: 479
Good Answers: 9
#68
In reply to #27

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 2:08 PM

"Given that, I'm not even going to answer any of them"

Oh, why not? The correct answer relative to neutral depends thusly:

When Phase "B" mirrors Phase "A"

"A-D-H-30"

When Phase "B" is the reflected image of Phase "A"

"B-D-H-30"

I have solved this riddle. It is the merely the difference between a mirrored composite image and one which passes through a prism.

Explains why it is called "split phase".

Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#69
In reply to #68

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 2:52 PM

I've got a bad case of A-D-H-D-46

And the real answer is: A-C-H-46!

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply Score 1 for Good Answer
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#70
In reply to #68

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 2:56 PM

Kinda like how this thread goes a long way toward explaining "split personality", huh?

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 6)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#73
In reply to #70

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 7:41 AM

See what happened with similar tread/ "Stupid question..." for possible L1-N-L2 (in standard: -120V-0V+120V).

I believe you and maybe North of 60 could write any CONCLUSION?

Register to Reply Off Topic (Score 6)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#29

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 9:24 AM

B, D, H, 30 +/-

Anonymous!

Now I will see if I got any of the questions right!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#34

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 11:14 AM

Wow... another thunderstorm.

From start = Question...is it a joke? Somebody needs a Nobel Prize or Ph D in Education? I believe Del sees that way. He (or maybe she - so Pardon Milady!) probably has dozens, hundreds or more of similar pieces, ready to edit e-Pamphlet "Britons about Americans in the Electron World". But if his/her view it is a joke he/she still tried to write something with a sense, to try "a debate in English".

Let me rewrite a story from a Deep South Community College. Y'all could recon it as a penny worth one ( less then 0.01 B. Pound, maybe 1/240 of £).

"At the end of the first semester with the first Lab Experiment in AC Circuits Lab, $99.99 years old Bob the Instructor gave his students a test with question # 13, exactly like the one on the top of this discussion. In the list of multi-choice answers were the same A,B + additionally C answer. C answer was: "None of the above".

Which answer is correct? ....... (fill the blanks)

To prove his point Bob gave his students two sets of oscilloscopes:

1st: dual-channel Fluke with common (COM) for both channels

2nd: two single channel scopes, both with insulated COM.

It took less than 10 minutes to confirm correct answer. Each students started Report's CONCLUSION with words: .................... (fill the blanks).

The End

Gogo La Giraffe"

P.S. Del - I love you man (if woman-oh no- not here!...). You showed me in your question "12v 20AH.." that Euro-Continental people have smaller hour (e.g. 20 Ah in their catalogues) and French Volt is just a v.

P.S.2. I wish I could read here some of the French jokes about Great Britons.

P.S. 3 I gave Very Good/Well note to JRaef. But in my CONCLUSION I would state that the best way to start almost any question I found is in other thread with " Real stupid electrical question.. " which already has over 100 answers. On the other hand my old professor said" There are no stupid questions but there are stupid answers."

>>>>> Strong winds Gentlemen Sailors!>>>>>>

Register to Reply
Anonymous Poster
#35

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 11:41 AM

A-G-H-40

Register to Reply
Anonymous Poster
#36

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 12:38 PM

A-E-I-20

Trust the American electrical system to be more complicated than it needs to be!

Register to Reply
Guru
Popular Science - Weaponology - New Member Hobbies - Fishing - New Member

Join Date: May 2007
Location: Aloha or
Posts: 659
Good Answers: 19
#37

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 1:35 PM

a-d-h-38

__________________
Closed biased minds are utterly impervious to any factual evidence which contradicts their beliefs
Register to Reply
Anonymous Poster
#39

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 3:17 PM

Am I the only one here to find this thread rather disturbing?

Most of the engineers on here are from the USA but yet they don't understand what form the electricity supply is in their houses??!!!!!

I am amazed / astounded / astonished / but also very disappointed.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2006
Posts: 4484
Good Answers: 246
#42

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 4:39 PM

Hi, North of 60.

Just wanted to apologize for my contribution to derailing the intent of your thread. I agreed with JRaef's first post, and in addition had the feeling that identifying oneself (as, for example an EE w/30 years experience... or as "other" with 1 year) would further color the responses beyond the tendency to post in concert with the majority view. I took your post number 8 as a sign that you felt the thread was already derailed, or that there might be a better survey technique.

I think it is a good thread (although the question seems a bit ambiguous), and warrants further discussion, because it appears there is some disagreement regarding the phase relationship of the two 120 volt supplies. It would be interesting to know, I think, if that means that people do not agree on 1. the actual wiring or 2. the meaning of the word "phase" (chemical engineers know what "three phases" mean: solid, liquid, and gas ) 3. the location of the zero reference, or 4. other stuff.

BTW, another problem with conducting the survey here is that you may find that your sample size is much too small to make any conclusion, especially given the number of variables measured. For example, you might not be able to say anything at all about the perceptions of "highly experienced electrical engineers residing in North America" because the sample size of people meeting those three qualifications is much too small. (Also, be aware that most CR4 members are teetering on the brink of insanity, so your survey results would have to have a disclaimer to that effect.)

In your future surveys, perhaps you could have one survey for only experienced EEs and another for only experienced E techs (or something along those lines) and not have respondents identifiable to others in any other way.

__________________
There is more to life than just eating mice.
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#43
In reply to #42

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 4:58 PM

"(Also, be aware that most CR4 members are teetering on the brink of insanity, so your survey results would have to have a disclaimer to that effect.)"

ROFLMSAO!!! Thanks for the vote of competence!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#63
In reply to #42

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 9:16 AM

Thanks Ken...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Anonymous Poster
#45

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 4:59 PM

B--- E---22

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#74
In reply to #45

Re: Survey on 120/240 volt North American Residential Services

07/16/2008 9:19 AM

this was me. I was logged in on another comp. sorry.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Anonymous Poster
#50

Re: Survey on 120/240 volt North American Residential Services

07/14/2008 10:57 PM

A-E-H-28

Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#56

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 7:46 AM

All answers show something strange. According to simple Truth that in Engineering/Physics the only one answer could be True we got A and B as a correct answer from the persons with this education and experience. Strange?

No the answer TVP / # 30 / cited below gives proper opinion about The Question and available only two possible answers A and B:

Well, of course. Remember that I'm both an engineer and a liberal. So, if you ask a question, I give at least four answers:

1) choice "A"

2) choice "B"

3) there's not enough information

4) I don't want to hurt the self-esteem of those who are wrong

Anyway, in the middle of my scope experiment and answer, I realized that I would have answered differently if I had done that first.

I see I must to send this to my Bob the Instructor (if he still teaches). Maybe he will change his multiple choice answers from 3 to 4. By the way his students' CONCLUSION started with "It depends..." - see Gogo La Giraffe's story.

Above Answer 4 rather does not apply to the students, right?

Register to Reply
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#57

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 7:48 AM

Where we are after almost 60 answers?

After reading all of them I probably see answer 20 to be the most valuable, let me cite part of it:

Well, of course. Remember that I'm both an engineer and a liberal. So, if you ask a question, I give at least four answers:

1) choice "A"

2) choice "B"

3) there's not enough information

4) I don't want to hurt the self-esteem of those who are wrong

Anyway, in the middle of my scope experiment and answer, I realized that I would

have answered differently if I had done that first.

So I should write to my Bob the Instructor (if he still teaches in the South) to maybe correct his test question # 13. His story had his students' CONCLUSION first words: "It depents..."

In this discussion CONCLUSION should start with same words.

Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#58
In reply to #57

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 7:55 AM

"...In this discussion CONCLUSION..." ...is a myth! You can't fool ME mythter, there IS no conclusion to THIS discussion!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#60
In reply to #58

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 9:06 AM

Why?

Register to Reply Off Topic (Score 5)
Power-User
Technical Fields - Education - New Member Technical Fields - Technical Writing - New Member

Join Date: Sep 2006
Posts: 367
Good Answers: 1
#59

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 8:56 AM

This tread should apply to North American electricians/master el./engineers with associate - bachelor - master degrees or maybe only Ph D owners?

Del the CAT brought "refreshing" UK /EU point of view. Somebody mentioned a history of USA / Canada NEC editing. Its changes' history which suppose to follow changes in the el_technology. My questions would be:

Is it true that EU in the end of XIX and beginning of XX century had 110 V ac as a standard? And with increase of loads (Watts & Amps) demand they switched to 220 Vac?

In their, not exactly parallel decision (Internet should be invented then!), N. Americans left standard 110 (frankly moved to 120Vac) with their small appliances when higher power consuming (ranges, dryers, HVAC etc.) created 240V standard that in the new needs of two voltages led to 120/240V, 60 Hz single phase secondary winding in residential house services. And this system has not guaranteed a power per phase balance as well in L1-N/L2-N/L1-L2 sections.

EU/UK residents living mostly in apartment buildings could have only one standard 220 Vac appliances supplied by single phase feeders from 231V secondary transformer windings, with mostly underground (under-earth?) cables grid. Or even having 220/380 Vac 3-phase motors (smaller in size per kW than single phase 230 Vac ones Made in Canada) supplied from 3-phase 400/231 V, 50 Hz.

In the different world on this side of Atlantic home owner + electric company delivering energy via overhead lines saved on installation of small cylindrical single-phase transformers on the wooden poles.

It is good. The experts from both side of Atlantic have still jobs just to adapting designing projects down "by others" and manufacturers keep the monopoles on their regional markets.

Why nobody's drawn the diagram of 120/240 V, 60 Hz service with terminals to connect the scope(s)? It would be less confusion and even insults. North of 60?

In transformers N. Ams have Open Delta and other connections used for three single-phase loads, EUs 3-phase Zig-zag to fight with time-changed 3-phase unbalance.

More cables in EU, more O/H lines in America - in the grids below 50 kV (arbitrary value)

UN cannot make forcible resolutions for EU, UK, US etc.in this matter.

Anybody could add or correct this hi-story? Andy G.? Del the.? .....

Any links?

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#62

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 9:14 AM

This was a rather simple request... answer the questions and stay anonymous and offer no explanation.

The questions were built using methodology that addressed MY need.

Question one is binary... either there is a difference in the phase angle (or whatever language you think is appropriate to use to ask the question) between the two 120 volt sources, relative to each other, or, there is not. Period!

About the only change I think I should have made to question #1 is to add a third option for "I don't understand the question and as such, I don't know how to answer it".

This effort is blown and the only usable data it has returned is to validate JRaef's comment at the beginning.

I'm rather disappointed and will look for another venue for this research.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#64
In reply to #62

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 11:30 AM

Hello North of 60, This is no insult intended here just jest!

You don't play fair, I'm taking my Questions and going somewhere else to play!

Good luck with your test, when you get it set up again and you would like our
input to skew it for you just post a link here.

metalSmith's

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#65
In reply to #62

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 12:46 PM

Hey, it's not unusable data! Just change the research topic to "can electrical and other engineers follow simple printed instructions to solve simple uncomplicated problems". I think you have enough responses to derive an answer...

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#66
In reply to #65

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 12:57 PM

Thanks for the chuckle...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - Olde Member!! Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jul 2006
Location: Dunstable, England
Posts: 2821
Good Answers: 45
#67
In reply to #65

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 1:54 PM

PMSL

John (typical engineers eh??)

__________________
A little knowledge is a dangerous thing - Googling is far worse!
Register to Reply Off Topic (Score 6)
Anonymous Poster
#93
In reply to #62

Re: Survey on 120/240 volt North American Residential Services

07/18/2008 9:32 PM

Or (it is almost like asking:)

Q: Is Red:

A. White

B. Black

so is it Binary? Yes or No? True or False? On or Off? Smart or Stupid?

We believe this method of explanation (almost stupid) is called AD ABSURDUM.

Trying to fool engineers?

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#95
In reply to #93

Re: Survey on 120/240 volt North American Residential Services

07/18/2008 11:58 PM

I totally disagree!

(Assuming that you are responding to Question 1 being a binary question)

I believe question 1 is truly binary: Either there is a 180° phase difference, or there is not. I don't believe anyone is saying there is a 120°, 90°, or any other alternative angle between the two voltages.

I can understand (although not agree with) those who look at it from the point of view of a transformer having a single center-tapped winding supplying the electricity. They think and say that those two halves of a winding are in phase with each other, and they are correct, IF you accept one or the other end of that winding as zero volts.

But , to me, that is a major error. The vast majority of household devices in North America run on 120VAC, and if I'm not mistaken, the vast majority of homes have two sets of circuit breakers, one set connected to one end of that power transformer, and the other set connected to to the other end of the transformer, and ALL of them use the center tap as the common point. The only way we can talk about both sets of circuit breakers providing 120V, is for the center tap to be considered ZERO Volts.

If there is a third way of looking at it, please educate me!

In the original Question 1, There are 2 possible points of view, where depending on what point is considered zero, one of the answers is true and the other one is false. THAT is a binary question!

Neither of the answers to your question is true (except to a totally color-blind individual: a person who can see only red light might consider your answer A to be correct; a person who cannot see red light, but can see one or more other colors, might consider your answer B correct). A person with normal human vision has no way to select one or the other of your 2 possible answers.

I believe it is your response that is ABSURDUM!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#98
In reply to #95

Re: Survey on 120/240 volt North American Residential Services

07/19/2008 8:32 AM

Well said, and thank you.

My role in this debate is now one of "observer". At some arbitrary point, I'm gonna consider the data gathering phase complete and start to build a picture that represents the exchange of ideas.

Funny... while my original intent was pretty clear and matched my papers needs, the "input" received by the posters has allowed to me to expand the expected result a little bit. This mess may yet serve part of my requirements.

Thanks everyone...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#109
In reply to #98

Re: Survey on 120/240 volt North American Residential Services

07/21/2008 9:14 AM

Thus proving yet again, it is an ill wind indeed that blows NO good!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#110
In reply to #109

Re: Survey on 120/240 volt North American Residential Services

07/21/2008 9:19 AM

I don't quite get your meaning.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#112
In reply to #110

Re: Survey on 120/240 volt North American Residential Services

07/21/2008 9:28 AM

You said you might yet get some useful data out of "this mess" for your paper... (did I misread you?)

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#113
In reply to #112

Re: Survey on 120/240 volt North American Residential Services

07/21/2008 9:31 AM

Oh OK. Yes... the "whole" picture is going to be used "broaden" the point I was trying to make in the paper. I did not expect this twist, perhaps I should have.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Off Topic (Score 5)
Guru
United States - US - Statue of Liberty - New Member Hobbies - Fishing - New Member

Join Date: Nov 2007
Location: Gone to Alabama with my banjo on my knee...
Posts: 5595
Good Answers: 20
#115
In reply to #113

Re: Survey on 120/240 volt North American Residential Services

07/21/2008 9:39 AM

Given this lot is twisted enough to open wine bottles by their very presence, I should think you might have done!

__________________
Veni, vidi, video - I came, I saw, I got it on film.
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jul 2008
Location: Layton, Utah USA
Posts: 21
Good Answers: 2
#71

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 3:00 PM

B - E - H - 12

Register to Reply
Power-User
United States - Member - Western Wisconsin

Join Date: Mar 2007
Location: Wisconsin USA
Posts: 305
Good Answers: 25
#72

Re: Survey on 120/240 volt North American Residential Services

07/15/2008 4:36 PM

A, F, H, 17

__________________
Troy
Register to Reply
Guru
Hobbies - HAM Radio - New Member

Join Date: Oct 2006
Location: Vancouver (not BC) Washington (not DC) US of A
Posts: 1261
Good Answers: 12
#88

Re: Survey on 120/240 volt North American Residential Services

07/17/2008 12:45 PM

BCH 38

Register to Reply
Register to Reply Page 1 of 2: « First 1 2 Next > Last »

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (13); Bill (3); Blink (7); DGCYS (1); dkwarner (11); Electroman (5); EnviroMan (12); Fraggle48 (1); jmueller (2); JRaef (1); metalSmiths (5); North of 60 (14); noshorts (6); Ried (2); Sciesis2 (3); silvCrow (1); southern123 (14); sparkybust (1); Troy36 (1); TVP45 (7); user-deleted-1105 (8); user-deleted-9 (4); wcfloyd (1)