Distance Between Earthing Rods

02/05/2009 2:58 PM

I have installed 100KVA transformer and for neutral earthing i want to get minimum resistance.I am going to put 04 Nos. rods.how much distance should be between earth rods

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Hobbies - Car Customizing - Dances with Trees Canada - Member - because I can Hobbies - CNC - too much fun Hobbies - Target Shooting - paper shreader

Join Date: Mar 2008
Location: Ottawa, Ontario, Canada
Posts: 769
Good Answers: 10
#1

Re: Distance Between Earthing Rods

02/05/2009 3:22 PM

See local regulations, this is all covered in the code book. It will also have to be tested and confirmed once installed. Soil makeup has a lot of influence as to earthing effectiveness.

Good luck with that.

__________________
Kevin "Dances with Trees" Willey
Register to Reply Good Answer (Score 3)
Member

Join Date: Oct 2008
Location: UK
Posts: 8
#2

Re: Distance Between Earthing Rods

02/06/2009 1:26 PM

2.2 times the driven depth between each rod (IEEE, BS7430).

So, 2.4m deep set needs to have ~5m separation. Remember, they don't need to be in a line, they can be deployed in a grid if space permits.

A grid ('duplex') is considered better configuration because if one of the conductor runs is cut, you still have an operational earth because the fault current can flow down the remaining leg, whereas, a single line ('spur') has to be sized to take the entire current and is lost when damaged.

Make sure you conductor is sized to cope with an imported fault from the HV suppply as well; your DNO should be able to provide you with calculated fault data.

Have fun.

Register to Reply
Participant

Join Date: Feb 2009
Posts: 1
#3

Re: Distance Between Earthing Rods

02/06/2009 2:24 PM

as for my knowledge is concerned your earth rod should be 3 meter deep and the distance between the rod is 15 m as per standard

Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Dances with Trees (1); engineer zulfiquar ali (1); user-deleted-1092 (1)