Bank of Tubular Heaters Shuts Down

03/18/2009 1:10 AM

I recently occured with a problem in tubular heater, where in my bank of 50 heaters when idle show meggar( insulation) at infinity, but when the heater bank is switched on after 8 - 10 mins the entire bank shuts down, again when the meggar ( insulation) is checked it shows at infinity.

Does any one know why does this problem arise, as i have come across this problem for the first time in my life.

Regards

Rakesh

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#1

Re: breakdown of tubular heaters

03/18/2009 2:04 AM

Dear ,

I have come across this problem many times n past. I would like to share with you ...

This is the behaviour of insulation material on the verge of getting faulty. Very principle that resistance of insulating material decreases with rise in temperature.... the cumulative local heating effect in the hot spot at weaked portion of the insulation goes on reducing the dielectric value at localised weaked portion... ultimately after few cycles, permanantly damaging the insulation.

In your case, all the 50 heater elements are not faulty.

You may locate the faulty tubular heating element by switching ON the heating elements in groups... say 10 at a time, .... you shall immediately locate the group of 10 elements wherein one heating element is on the verge of dyeing.

Like wise, you shall locate the faulty element.

regards.

__________________
Exploring the Science of Electricity
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jun 2008
Posts: 10
#2
In reply to #1

Re: breakdown of tubular heaters

03/18/2009 4:14 AM

Hi,

Thanks for the prompt reply and a solution to my problem, just curious to know where are you located.

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#3
In reply to #1

Re: breakdown of tubular heaters

03/19/2009 1:32 PM

Divide and conquer has been and is a great strategy for things like this. Once in a blue moon (rarely) there will be a situation where the fault current from a large number of units is sufficient to cause a trip when the problem is general degradation of a large number of similar devices.

Try Mr. Potter's strategy first but realize that there may be more than one culprit if the problem is not found quickly by using it.

Have FUN!
TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Anonymous Poster
#4
In reply to #3

Re: breakdown of tubular heaters

03/21/2009 9:49 AM

thank you sir

Regards

Rakesh

Register to Reply Off Topic (Score 5)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".