Anonymous Poster

South-Africa in need

05/11/2009 2:00 PM

how do i install two stop start station on coveyor but it must have timer to stop operation after time a period , if anybody can help me with a wire diagram and tell me what the best components wil be to use on a 3 phase motor

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#1

Re: South-Africa in need

05/11/2009 3:42 PM

"Start" button simultaneously starts conveyor and time delay (TD) relay. At end of timing cycle on TD relay, contacts in parallel or series with "Stop" button can perform same operation as "stop" button. If "Stop" button is normally closed (NC), then wire normally closed TD relay contacts in series with contacts of "stop" button. If "Stop" button is normally open (NO), then wire TD relay NO contacts in parallel with contacts of "stop" button.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: South-Africa in need

05/12/2009 2:32 AM

Here is an circuit and hope it will able to help you

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2007
Posts: 21
Good Answers: 1
#4
In reply to #2

Re: South-Africa in need

05/14/2009 3:41 AM

I can see a few shortcomings in the circuit

1. A control breaker or fuse is not incorporated. This could be overlooked though where MCB 2 also doubles as the control breaker. However, because of its size it would only serve as a means of isolation and can not offer any protection to the control circuit.

2. In the event of an overload before the timer's set time elapses, the motor will not be disconnected. Although the overload relay O/L A break (NC) contact will open but the contactor KM1-1 coil will be maintained via the timer T1 NC contact.

__________________
One does not need a mirror to look at what one is wearing on the wrist
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5
In reply to #4

Re: South-Africa in need

05/14/2009 3:51 AM

You are right. The line after the timer contact that goes to the timer coil should be removed out. You need to put a MCB for the control circuit for protection.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Associate

Join Date: Jan 2008
Posts: 32
Good Answers: 1
#3

Re: South-Africa in need

05/12/2009 4:42 AM

Simply purchase an inexpensive PLC and install it; You can stat / stop / and program in time parameters............all for one price and a nice neat installation.

old golfer

Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bill (1); oldgolfer (1); Simon Wan (2); solaaderinwale (1)