Removing Excess Moisture from Refrigeration Systems

05/29/2009 10:29 AM

I'm working on a 50 ton chiller which had frove up and ruptured the plate and tube evaporator. the refrigerant (R-22) leaked out and then the water which is at approx 30 psi was forced into the leak and filled the refrig. system with water. I have drained 20 gallons of water out of it and there is many more gallons trapped in low spots, this system has an air cooled condensor. I have used CF-20 in the past for cleaning burnt systems but don't know how well it will work with moisture. If anybody has any suggestions I would appreciate it.

Register to Reply
Pathfinder Tags: moisture refrigeration
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2008
Location: Meherrin Virginia
Posts: 319
Good Answers: 6
#1

Re: How do I remove excess moisture from refrigeration system

05/29/2009 1:05 PM

Am I missing something here? why not a vacuum?

__________________
If you fail to follow through, you will fail.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: How do I remove excess moisture from refrigeration system

05/29/2009 1:17 PM

I would say compressed air blow it out.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#5
In reply to #2

Re: How do I remove excess moisture from refrigeration system

05/30/2009 6:29 PM

......not compressed air.............that has water in it...............once repaired you blow dry nitrogen through the system.

Before system evacuation and charging, you could fit a large adsorbent (not absorbent) filter drier in the system.

By the way in Australia you have to be certified to work on any refrigeration system.

..........nice to know people still pollute the atmosphere with HCFCs.

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#3

Re: Removing Excess Moisture from Refrigeration Systems

05/29/2009 11:45 PM

OK, there is a lubricating oil in the system. This has to be removed and the system flushed with an acceptable solvent until it is clear of all the old freon and water and oil.

Some parts might be damaged/corroded by the water, so refer to the maker for guidance. You might need to replace some mechanical components. There are components called 'inline dryers' installed from before. They need to be replaced or baked out in vacuum (if possible).These dryers have a chemical water absorber and are freon tolerant. Suggest you ask the maker.

You then draw a vacuum on the system and recharge it with the proper amount of freon and lubricant into the compressor sump. This is a routine task for a refrigeration mechanic. They know the details. What I gave you is an outline. You may be wise to hire specialists. The system might have a leak on the low pressure seal side and draws in air with water? This gradually decrements the efficiency of the circuit and if the water dryers get saturated you can have free water circulating as ice or fluid. Ice is abrasive and water is not conpressible and enough can blow the heads off your compressor when it tries to compress water liquid(which it cannot do)

__________________
Per Ardua Ad Astra
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#7
In reply to #3

Re: Removing Excess Moisture from Refrigeration Systems

05/31/2009 7:03 AM

Hi aurizon,

.....chemical water absorber and are freon tolerant.

I think, that as you pointed out, the absorbent driers are a better option than the adsorbent driers, as they can hold a large volume of water. Once the system is proved to be thoroughly "dried out"............then install the adsorbent driers.

After major work, as this obviously is, it is a good idea to install a 10 micron felt core filter on the suction line to protect the compressor from damage..........once the system is thoroughly clean, this filter can be removed.

All these filters are and driers are in-line............on larger systems you can also have by-pass filters fitted.

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
2
Associate

Join Date: Apr 2009
Location: Kansas USA
Posts: 47
Good Answers: 7
#4

Re: Removing Excess Moisture from Refrigeration Systems

05/30/2009 12:23 AM

I am reminded of the many times in my career when there was a catastrophic
chiller or rack failures related to large amounts of water in the system in the 70's
There was large amounts of water in all these systems
some water was poured in by unhappy pipe fitters on one job
some jobs were due to chillers freezing up

All rebuild contractors I watched back then relied on vacuum pumps then aggressive drier changes
for weeks until tests showed a low water content
Myself I wouldn't hook my pumps up to pure water as they don't give
vacuum pumps away either
I too would consider high volume air pressure to sweep the visible water out
Then multiple sweeps with dry nitrogen and vacuums with electronic vac gauges
then multiple drier core changes
Your chiller equipment reps always are a good source of support

But always think about this
Most of the those failures I witnessed were followed by second and third failures
as they set a priority one on getting the water out and rebuilding the compressors
but no one bothered
to find the real cause of the rupture or water entrance into the refrigeration system
One large chiller failure was caused by mud in the chiller from mud coming from
the air washer type cooling coil on a reconnaissance photo lab air handler
and they didn't clean all the mud out and after 3 rebuilds under warranty
the contractor went broke

The most important part of our job is to find the cause of the failure
or you will be back under warranty at your expense

JR
www.rorenet.com

Register to Reply Good Answer (Score 2)
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#6

Re: Removing Excess Moisture from Refrigeration Systems

05/30/2009 9:30 PM

How about hot N2, followed by pulling a vacuum like you normally would have to do. You can set up a test (I think it is called a chandler test) to test the system for moisture once you think you are close and it will ballpark your dewpoint for you

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#8

Re: Removing Excess Moisture from Refrigeration Systems

05/31/2009 9:58 AM

I have been there

You will need multiple vacuum pumps and lots of pump oil, and even more patience.

Keep an pulling a vacuum until the oil stops turning milky white. You will be changing the oil several times a day, for many days.

Register to Reply
Power-User

Join Date: Sep 2007
Location: Cleveland, Ohio
Posts: 100
Good Answers: 2
#9

Re: Removing Excess Moisture from Refrigeration Systems

06/02/2009 9:48 AM

I suggest you look up methods of moisure removal in your refrigeration manuals.

Try using a high capacity vaccuum pump with a trap piped between the compressor and the vaccuum pump. Wrap the trap in dry ice and insulate. This will trap the water before it fills your vaccuum pump.

__________________
THEOILGUY55
Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aurizon (1); betomachine (1); Icarus (1); jgroberson (1); MOBI (2); otha (1); ozzb (1); THEOILGUY55 (1)

Previous in Forum: ISO 25178 Standards for Surface Roughness   Next in Forum: pressure vessel

Advertisement