Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/11/2009 10:48 PM

At the output of a 3 phase power generator not conected to any load, if you short phase A through some impedance to ground then is there voltage at neutral pin?

My guess is you see phase A... Neutral increases as any phase decreases. but is that only for flowing current? phase B and C are not yet connected. No current is flowing from phase B and C, just phase A is flowing.

Assuming power generator not grounded, neutral is not connected to ground, and circuit breaker did not trip.

thanks, -PITB

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Neutral Voltage = ? if Phase A is Shorted in 3-Phase

06/12/2009 3:17 AM

For a little while there might be a voltage. It will stop when either:

  1. The circuit protective device operates, or
  2. The generator self-destructs.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2

Re: Neutral Voltage = ? if Phase A is Shorted in 3-Phase

06/12/2009 3:25 AM

Obviously there will be a neutral voltage.

Assume it is a good generator (balanced , nice one )

The generator will generate voltage (EMF) irrespective of the current is there or not,

So the voltages are say V(0o), V(120o) and V(240o), neutral being at 0.

Now as you conect an impedance Zaon A phase say I take it as the first one for simplicity

The total impedance on that phase will be

Z = Zin+Za,

Current Ia(Φ) = V(0o)/Z(θ) will flow

If you do the sort of the back tracing you will land up in a Voltage at phase A at V'a (ø).

I think a phosor diagram may make it a bit clear

The neutral will now float to a voltage as phasor sum of V'a (ø)+ V(120o) + V(240o)

So this is irrespective of the current flowing or not.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply Score 1 for Good Answer
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/12/2009 9:13 PM

One has to ask, for a voltage to be measured, you need to measure from two points. So how do you wish to measure the potential difference, from the neutral to what? If you intended to measure from the neutral to ground, given your example, you should see the same as going from phase A to the neutral.

If the neutral of the generator is not tied to ground and no other other phases is connected to ground, through an impedance or not, there is no route back to the source so there is no current flow. This is analogous to a corner grounded delta system.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Associate

Join Date: Nov 2007
Location: Air Force Base
Posts: 45
#4
In reply to #3

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/12/2009 9:48 PM

You're right, I meant to say : is neutral high compared to power source ground? Thanks -PITB

Register to Reply
Power-User

Join Date: Sep 2007
Location: Sheboygan, WI USA
Posts: 372
Good Answers: 13
#5

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/12/2009 11:26 PM

I was in Canada starting a couple induction hydro-generators. There was an existing 3MW synchronous hydro-generator at the same site. There was a couple mile long transmission line to town. A tree branch fell on one phase of the transmission line a half block from the hydroplant, all of the generators tripped off-line.

Then the utility from town remotely closed the 3MW unit back into the transmission line, -they had some protective relay out for test- and the phase voltages went beserk.

The LCD voltage meter face blew about 8ft across the room, a voltage protective relay blew a 1 watt resistor and several other problems including a blown PLC.

I was told the line voltage between the remaining two phases went at least 1.73 times normal.

__________________
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
Register to Reply Score 1 for Good Answer
3
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#6

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/13/2009 2:56 AM

In a 3 phase system with the neutral isolated from ground, by connecting phase A (or B or C) to ground through some impedance, the neutral will raise its potential close to the potential of the A phase, the voltage for the phase A would drop close to the voltage across the grounding impedance and the other two phases would raise the voltages compared to ground, close to the value of phase to phase voltage. Eventually the phase to ground insulation for phases B and C would suffer the most.

__________________
The time is ......now
Register to Reply Good Answer (Score 3)
Anonymous Poster
#7

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/13/2009 6:25 AM

The major question is here: relative to which circuit point this voltage would be measured? If it is measured, as usualm compared to neutral point - any change in voltage value will be occured. On the contrary of huge current will flow across the shortening impedance

Register to Reply
Anonymous Poster
#8

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/13/2009 6:29 AM

The major question is here: relative to which circuit point this voltage is measured. If it will be measured compare to the neutral point, as usual, any change will occure place. On the contrary of huge current will flow across the shortening impedance.

Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#9
In reply to #8

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/13/2009 6:47 AM

The voltage is measured relative to the ground, the neutral being isolated. The current is proportional to the electrical capacity of the circuit - it is a capacitive current in nature. The generator has a small winding electrical capacity so the current should be small. If the neutral is grounded then a huge current will flow across the impedance, and that is called shortcircuit. Having isolated neutral and only one phase grounded is not dangerous for the consumer but for the system's pahse to insulation. The phase to phase voltage does not change significantly.

__________________
The time is ......now
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#10

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/13/2009 9:32 AM

Answer No3 by 'North of 60' sums it up.

If the generator is not grounded (fully insulated from earth) then there is no complete circuit back to the generator from any phase at the outlet via the earth loop - so no current flows.

If any phase is shorted to earth, and you connect a voltmeter between neutral and earth, you will get a reading of that phase voltage.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#11
In reply to #10

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/13/2009 10:25 AM

If the generator is not grounded (fully insulated from earth) any of current will flow across impedance which ia shortening one of phases to a ground. Two remain phases of course are opened. For current producing as minimum two phases have to be connected by their impedances to a ground. In this case the same question remains: between which circuit point the voltage is measured. Thus, a voltage more than zero may be measured between ground and generator neutral if as minimum two phases are connected to ground. In the case when a generator neutral is grounded the same question: between which point the voltmeter will be connected. To answer this question the equivalent electric circuit is to be drawn and is to be calculated.

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#12

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/13/2009 11:25 AM

As Guest - post 11 says, you need to draw the equivalent circuit.

In doing so, it will help to imagine the ground system as being a single conductor - an earth-wire.

The phase wire (via an impedance ?) is 'shorted' to one end of the earth-wire. The other end of the earth wire running back to the generator (which is fully insulated and not grounded) will thus not be connected to anything. Hence no circuit, and hence no current.

A meter connected across the open circuit of 'earth' and 'neutral' will show phase voltage.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Apr 2009
Posts: 20
#13

Re: Neutral Voltage - What if Phase A is Shorted in Three-Phase?

06/15/2009 11:39 AM

If the neutral is not connected to ground then connecting phase A to ground has no affect on the generator and perhaps not to any load the generator is wired to, if the load is not grounded anywhere. The BIG problem is that the generator frame may be connected to the neutral so anyone standing on the ground and touching the generator framework is not going to like the result!!!!!! Lethal is the operative phrase!

Register to Reply Score 1 for Good Answer
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); CoronaCameraMan (1); horace40 (2); nikolay (2); North of 60 (1); pain in the butt (1); PWSlack (1); RcEe (1); sb (1)

Previous in Forum: Power Generation Basics   Next in Forum: Schneider Quantum Modicon PLC

Advertisement