We have a situation where a 4160V delta: 480V wye transformer was installed without the typical neutral to ground bond. The only grounding is to the cabinet via the steel conduit.
All loads are three phase and no neutral is run with the secondary condutors.
When we measure A:B, B:C or A:C we get 480V. When we measure A or C to ground we get 480V. When we measure B to ground we get "0" volts.
We were expecting to see 480V to ground on all three phases. While the voltage to ground is technically "floating", I had always assumed that there was sufficient inductive coupling to ground that under most conditions phase to ground voltages would be close to what they are on grounded systems of the same configuration.
Having found the "0" volts to ground on B phase, we believe that one of the B phase coductors is damaged and is creating a single B phase to ground fault. We want to isolate the fault, correct it and then bond the neutral point to ground.
Before we start taking things apart, can anyone confirm that this thinking is correct or incorrect? Is there any other reason why we would measure B phase to ground as "0" unless it was in fact grounded?
On undground systesm, wouldn't it be more noe