Moving Air Through a Conduit

07/27/2009 2:49 AM

I am trying to figure a way to use a solar powered blower to move the 64-degree air in a mining tunnel to cool an area 80 feet away. The outside temperature at our location in the Arizona desert exceeds 100 degrees every day and many nights of the summer.

While we are used to dealing with it during the day, the nights can be hard to rest or sleep. Currently we address this with generators and air conditioners that almost; but not quite, get it done. Also, it takes 2 hours to begin cooling down, fuel and dealing with the generator noise.

Since the mine tunnel is only 80 feet away it seems that it should be possible to move the 64 degree air to the 36' fifth wheel living and sleeping quarters. We are planning to use some type of solar powered blower to pass the air through a conduit. Any suggestions about just what material or apparatus to use would be appreciated.

My question is does it matter where the blower is placed in the conduit? There is little solar available near the tunnel, but an abundance at the trailer. If the blower and solar panel are placed on the trailer will it pull as much cool air as it would if it were blowing from the tunnel?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Moving air through a conduit

07/27/2009 3:01 AM

Good Q.
HVAC isn't my thing, but I have a suspicion that a fan may push better than it pulls.
There may be a problem insofar as you can't keep sucking air out unless there is air flowing back in somewhere else, but presumably ventilation shafts would provide this?
Conduit material, wood is cheap, quick and a reasonable insulator.
Have fun...
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#26
In reply to #1

Re: Moving air through a conduit

07/31/2009 5:18 AM

that is what I was thinking

__________________
If you never do anything you never have problems.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jan 2007
Location: UK S.Northants
Posts: 485
Good Answers: 19
#2

Re: Moving air through a conduit

07/27/2009 5:37 AM

As you suck air out from the bottom of the shaft warmer air will be drawn in from the top, the surrounding rock should cool this, it has a greater capacity than your living quarters. Watch out for air leaks or you will be cooling the outside or sucking hot air depending on the location. It should suck as well as it blows but you will need to insulate / shade the conduit so you don't pick up heat en-route and defeat the cooling process you worked so hard to get. Is there enough shade to the quarters also?

Good luck!

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Moving Air Through a Conduit

07/27/2009 9:03 AM

It's better to push air than to pull it, but it will work. Where will you get the make-up air? Never mind. See above^ posts.

Funny, the first two answers were from people who probably don't need AC more that 10 days a year.

Be careful, there's an excessive heat warning in effect till tomorrow and it's supposed to hit 113 today. Come on in to town and cool off. You can swim in my pool, if you'd like.

Register to Reply
Associate

Join Date: Jan 2009
Posts: 43
#4

Re: Moving Air Through a Conduit

07/27/2009 11:12 AM

Thanks guys. You bring up a point I had not considered. That is the make-up air. The location to suck or push from is the tunnel entrance which is also where the air enters the mine. It travels about 2,000 feet and comes out up the mountain side.

I'm thinking it would then be necessary to extend the intake further down the shaft. I would then need to calculate the rate the air is moving into the tunnel and the rate of suction out the conduit. Correct? and if so, what kind of formula would I use?

I'm assuming I will need a 12 volt motor and blower with an inverter and solar panel. How would I calculate and/or find these components?

Thanks again

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#5
In reply to #4

Re: Moving Air Through a Conduit

07/27/2009 11:35 AM

'Calculate'? Sorry I don't understand the word .
I'm an experiment with what I have to hand paw sort of cat.
I'd say one of the most importand factors may be to have a close fit between fan and duct, else it will just circulate the air around itself.
A bit of experimentation will probably be quicker and cheaper than working it all out and then finding it's wrong
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Active Contributor

Join Date: Jul 2009
Location: Western Australia
Posts: 24
#6

Re: Moving Air Through a Conduit

07/27/2009 11:25 PM

Use 6" aluminium foil concertina air con ducting. It will resist the radiant heat.

Use your fan to blow and it will not collapse. Normal mine shaft/drive ventilation is done in exactly the opposite way using plastic vent bag.

Keep in mind if the shaft/drive vent is up the mountain the air will convect out the vent, so warm air will always be entering the lower entrance. best to locate your air pickup a long way in.

Register to Reply
Commentator

Join Date: May 2009
Posts: 64
Good Answers: 6
#7

Re: Moving Air Through a Conduit

07/27/2009 11:30 PM

A blower is more effective pushing air than drawing air. In suction you create negative pressure in the duct/conduit, so you will require a rigid duct otherwise it may collapse.

Generally speaking you will require more 65F air than the normally used 55F air used by AC units. Off the top of my head I guesstimate you need 1500 to 3000 cfm to get the job done at these temperatures (a lot of air for a small space). Also, as pointed out by others, you will need to place the inlet deep enough into the mine shaft to prevent short-circuiting of the hot air into your conduit, so it could be double the length - say 200 ft. Size of the duct would be about 16" diameter.

Finally let's address the power required. To run this set-up will likely require between a 1 and 2 hp motor. Will the solar panel provide this type of power during the day? How will you power it at night?

Water is far easier to move, and is has much greater heat capacity due to density. Perhaps some type of run-around water loop would work much better.

Something to consider.

Cheers.

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#8
In reply to #7

Re: Moving Air Through a Conduit

07/27/2009 11:43 PM

Someone suggested aluminium concertina tubing. This will not work as it is exposed to ambient air all the way and the air inside will be turbulent = excellent heat transfer, so you will lose the cool air to some degree. Another problem is viscous drag. Unless you are pipe is 2 feet in diameter you will get drag reducing the volume pumped.

you need an insulated tube, which can be a square wooden cage with plastic inside and out and a one inch air gap open at the end. Since you can get 2" square wood cheaply in 8 foot lengths, make them 8 feet long then tape them together and run them from the open shaft to the cabins and draw from 100 feet inside. use a squirrel cage blower, a house blower, with a 2 foot port, and make sure the motor is not in the air stream. You can also seal and pressurize the high point and seal and duct from the low point.

hard to do with solar as you will need 1/2 HP, but it is doable.

__________________
Per Ardua Ad Astra
Register to Reply
Commentator

Join Date: Jun 2009
Posts: 58
Good Answers: 1
#9

Re: Moving Air Through a Conduit

07/28/2009 12:51 AM

I would agree with Duane on this. It is far easier and more efficient to use water in this case. Think about an air cooled engine as opposed to a water cooled one.

What you have here is a geothermal source of cooling. If you a split unit air conditioner you can use the evaporator as the heat exchanger. Run 80 feet x 2 of 1" to 2" piping into the mine, coil the end that[s in there and bury it. If there is any pooling of water in there you are set, if not dig a hole and use the ground to absorb the heat. The water circulating through your evaporator should eventually stabilize somewhere below 80 degrees. Bury or insulate the piping to reduce heat absorption.

Here is a website to describe it. http://siamgpi.com/solarpower/geothermal-cooling.html

If not, why not sleep in the mine?

Register to Reply
Associate

Join Date: Jan 2009
Posts: 43
#10

Re: Moving Air Through a Conduit

07/28/2009 1:25 AM

I'm getting quite the education here and it is appreciated. I had not considered water, but going that way has more possibles and would be more convenient.

Water is coming out of the tunnel 24\7 at a rate of 7 gallons a minute and is 64 degrees. It flows into a pond that is no more then 20 feet from the sleeping quarters. It also remains cool in the pond as it is well shaded.

As suggested, if this would do the job I just need to know how to use it; also basically described earlier. BTW, sleeping in the mine was becoming a reality if it could not be handled otherwise.

With appreciation,

AZ Miner

Register to Reply
Power-User
New Zealand - Member - Member Australia - Member - Member

Join Date: Oct 2008
Location: Auckland, New Zealand
Posts: 463
Good Answers: 43
#12
In reply to #10

Re: Moving Air Through a Conduit

07/28/2009 1:53 AM

Hi AZ Miner,

In Australia some years ago you could buy portable domestic evaporative air coolers. Basically a box the size of a window airconditioner, fitted on 4 sides with aborbent straw material with a small pump drawing water from the base resevoir to the top of each panel and the water running down the straw walls. A fan blowing air across/through the walls provided air cooling to the surrounds. In these the water was recirculated and topped up but you could tap off the mine/pond flow. It increased the humidity but did cool. It was usually on wheels to move from room to room.

Maybe you could divert the water from the mine to quarters prior to the pond and discharge it to horizontal feeders (roof guttering) or pipes feeding to an absorbent curtain, with the excess drained to the pond, and some form of fan arrgt to push air thru the curtains. Or direct the water to a series of smaller curtained individual coolers with the drains connected to a common return to the pond. Even this added to an existing small fan may benefit.

Might need some odd plumbing and carpentry but as a method should give some relief to temperature without any great cost.

Good luck.

Register to Reply
Guru

Join Date: Jun 2009
Location: Bangalore, India
Posts: 725
Good Answers: 24
#14
In reply to #12

Re: Moving Air Through a Conduit

07/28/2009 2:06 AM

Good idea. Such as this?

http://ag.arizona.edu/pubs/consumer/az9145.pdf

bioramani

__________________
bioramani
Register to Reply
3
Commentator

Join Date: May 2009
Posts: 64
Good Answers: 6
#13
In reply to #10

Re: Moving Air Through a Conduit

07/28/2009 1:59 AM

You could go a number of ways with this depending upon your financial and power limitations.

1. Closed loop system: Run your water in a closed loop with coils of HDPE weighted down at the bottom of the pond. This would require a pumping system (much less power required than air), some 1 to 1-1/2" pipe (available in 300 to 500 ft coils used in geoexchange system) connected to some fan-coils in the trailer to recirculate and cool the air.

2. Open loop system: Use the water directly with an inlet and outlet to the pond in the piping without the sunken coils. You will get better thermal performance and require less piping. If the water is clear and clean of debris (you have to be careful of pump seals and dirt) this may be okay.

3. Heat-pump: Use the water as a heat sink for a heat-pump system to do get best cooling performance with a closed loop system. This system requires the most power of the systems and more money (maybe) but is the most likely to provide you with proper cooling comfort.

Finally, I would like to add that evaporative cooling may also be an option. With 7 gpm of water flow you could use some of this to spray down the outside of the trailer on a continuous basis. This would keep the outside of the trailer cool by absorbing heat from the mass of the trailer as well as an additional evaporative cooling effect of the water. Evaporation of water will absorb a lot of heat due to the phase change.

I used to live in a house that had a west facing wall made of brick which adjoined my living room. During the hot summer months I would often go outside and water down the brick to cool off the wall so I could comfortably sit in the living room. I have seen a few buildings which have installed lawn sprinklers on the roof to keep them cool, although nowadays such use of water may be prohibited due to local water restrictions.

Cheers.

Register to Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#18
In reply to #10

Re: Moving Air Through a Conduit

07/28/2009 11:10 AM
__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Guru

Join Date: Jun 2009
Location: Bangalore, India
Posts: 725
Good Answers: 24
#11

Re: Moving Air Through a Conduit

07/28/2009 1:50 AM

Is the tunnel air fit for human consumption. AHas an analysis been done? In a continuous duct a blower of a given power will move the same quantity of air. It is easy to lay in a cable to conduct electric power to the point of use from point of generation. May be best to locate the blower in the duct at the tunnel bottom.

Assuming you have enough cold rock mass to cool the warm air entering the tunnel, check if enough surface area is available to transfer the required amount of heat. For an off the cuff estimate one can take it that 75 BTU/hr/square foot can be transferred.

For the temperature conditions given this translates to roughly 1cu.ft/hr/sqft air at 100 deg cooled to 64 deg. Knowing the rate of air flow required the required heat transfer area can be estimated.

Caution: There is no active cooling of the rock mass. You may be gradually heating up the tunnel walls and end up with diminishing returns.

Bioramani

__________________
bioramani
Register to Reply
Commentator

Join Date: Jun 2009
Posts: 58
Good Answers: 1
#15

Re: Moving Air Through a Conduit

07/28/2009 7:27 AM

If you can find one of these in an auction somewhere it would work quite nicely. I bought one for $25.00 four years ago. They where very popular in the high tech industry. It is a water-to-water chilling system. You would connect city water to one side and your system water on the other. Inside there are two motor & pumps and some well insulated coils that act as the heat exchanger. You could probably make this something like this yourself.

They come with 2 positive displacement pumps. Search for auctions on the Coolflow System I, II, III & IV, you might find one for cheap. I got this one from a Nortel Networks auction, now they are bankrupt or "Nowhere Networks". I didn't realize it's potential when I bought it. At the time, I just couldn't see the logic in connecting up to the city supply and having the water running all the time, the I realized it was for systems that already had a chilled water supply. The positive displacement pumps made it a great buy.

http://www.thermo.com/eThermo/CMA/PDFs/Various/File_26289.pdf

You could also try using a thermolator (water temperature controller) they are used primarily in the plastics industry. There are lots of used ones on the market. They are primarily used for heating the water, but you could just disconnect the heaters and connect to the cooling valve.

http://www.advantageengineering.com/temperatureControllers/SKVE/skveGeneral.php

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#16

Re: Moving Air Through a Conduit

07/28/2009 10:29 AM

the nights can be hard to rest or sleep

There is an abundance of solar energy at th 36' 5'er? What Arizona are you in with solar energy at night?

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply Off Topic (Score 5)
Commentator
Popular Science - Cosmology - New Member United States - Member - New Member

Join Date: Aug 2008
Location: Dublin, GA, USA
Posts: 69
#17

Re: Moving Air Through a Conduit

07/28/2009 10:50 AM

An inexpensive alternative is to utilize a car radiator. My friend used this setup but with wood-fired hot water instead to heat his 1200 sq. ft. home during Georgia winters.

Place the radiator just inside the return air duct of the trailer A/C system and plumb it with 3/4" garden hose (inflow and outflow reducing adapters needed of course). A small water fountain, large aquarium, or swimming pool pump would be the source of constant, low-flow water movement from the 64 degree pond through the radiator.

Register to Reply
Associate

Join Date: Jan 2009
Posts: 43
#19

Re: Moving Air Through a Conduit

07/29/2009 12:34 AM

It is clear that water is the way to go. I will digest as much as I can, the information and resources everyone has offered.

I would like to keep it as simple as possible. I just realized the trailer and quarters I'm trying to cool sits between the tunnel entrance and the pond. The water could easily pass through the trailer on it's way to the pond. There is no more then a 12' lift to the trailer and then down and into the pond.

It seems with a 12 volt (battery recharged by solar) system of water pump, some type of fan and device to run it through it could continue to cool the sleeping & living quarters 24/7.

I really do appreciate all the input and will post the resulting ?system?.

AZ Miner

Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#21
In reply to #19

Re: Moving Air Through a Conduit

07/29/2009 1:37 AM
__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Power-User
United States - Member - Donald here, Campbell Lighting Co. Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Sep 2006
Location: central arkansas
Posts: 337
#20

Re: Moving Air Through a Conduit

07/29/2009 1:20 AM

I have read most of the replys, and honestly to not claim to be an expert in moving air... However, I am an expert when it comes to many phases of practical Lighting.

And seeing as how we have our lighting fixtures in thousands of Chicken Houses, worldwide, I just wanted to pass this on:

Every single Chicken House in the USA, uses negative air.

They Do NOT push air, they pull it..

Wonder why???

Donald

__________________
Check out our home page for specs on "Soft Neon"
Register to Reply
Guru
Popular Science - Weaponology - bwire Hobbies - Car Customizing - New Member

Join Date: Dec 2007
Location: Upper Mid-west USA
Posts: 7498
Good Answers: 97
#22
In reply to #20

Re: Moving Air Through a Conduit

07/29/2009 1:38 AM

They're hen houses

__________________
If death came with a warning there would be a whole lot less of it.
Register to Reply
Power-User
New Zealand - Member - Member Australia - Member - Member

Join Date: Oct 2008
Location: Auckland, New Zealand
Posts: 463
Good Answers: 43
#23
In reply to #20

Re: Moving Air Through a Conduit

07/29/2009 1:42 AM

It's a lot easier to collect and treat the airborne chicken dust, feathers and odours at the exhaust of the ventilation fan than the multitude of openings in the chicken houses. On fan startup in a pressurised application you could coat the neighbourhood with all sorts of chicken bits.

Register to Reply
Power-User
New Zealand - Member - Member Australia - Member - Member

Join Date: Oct 2008
Location: Auckland, New Zealand
Posts: 463
Good Answers: 43
#24
In reply to #23

Re: Moving Air Through a Conduit

07/29/2009 1:49 AM

It's a lot easier to collect and treat the airborne chicken dust, feathers and odours at the exhaust of the ventilation fan than the multitude of openings in the chicken hen houses. On fan startup in a pressurised application you could coat the neighbourhood with all sorts of chicken chook bits.

Register to Reply
Commentator

Join Date: May 2009
Posts: 64
Good Answers: 6
#25
In reply to #20

Re: Moving Air Through a Conduit

07/29/2009 1:57 AM

Negative air is commonly used in exhaust systems. Exhaust systems come in various configurations from panel fans mounted on walls, to ducted with branch lines sized accordingly.

Exhaust systems are used usually to remove odours and heat from point sources. In a chicken house I am sure that it is for odour removal. Bear in mind that the building will also require some make up air to balance the exhaust air.

For the OP's system, negative air would be problematic. Any air leakage (likely considerable in this case) in the built ducting would introduce hot air into the cold air stream which would be unacceptable.

Also, under negative pressure, the duct walls will cave inwards reducing air flow as the cross-sectional area of any built duct would be reduced and increase resistance to airflow thus requiring additional power to overcome the additional resistance caused by negative pressure. When we design ducted exhaust systems we take these factors into consideration.

Everything is contextual given the circumstances. Your experience in chicken farming does not translate well to this application. As a mechanical engineer I would not try to design the lighting for a chicken farm.

Cheers

Register to Reply
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

aurizon (1); AussieBob (3); AZ Miner (3); bioramani (2); bwire (4); Campbell Lighting (1); dadw5boys (1); Duane Tilden (3); Greenja (2); HUX (1); lyn (1); muzza (1); Stubby (1); user-deleted-1105 (2)

Previous in Forum: Dry Cups and Liquid Cups   Next in Forum: Guests as Trolls

Advertisement