Type 2 Coordination for 3.3 kV Motors

10/13/2009 5:30 AM

I am using 3.3 kV vaccum contactors as DOL starter for one of our project for 3.3 kv motors.

Is there any standard chart for selection of HT fuse & Contactor avaialble (Like LT motors) to ensure type 2 coordination for 3.3 kv motor or high voltage motors.

How to ensure coordination between overload protection & locked rotor protection during starting of HT motors?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#1

Re: Type 2 co-ordination for 3.3 kV Motors

10/13/2009 12:54 PM

I really don't know we are using HT fuse & contactor for HT motor protection.!!!Your vacuum contactor will open on fault wired through relay contacts.Latest relays used in motor protection such as RHO3 will help to do the coordination.

__________________
"Know something about everything and everything about something"
Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#2

Re: Type 2 Coordination for 3.3 kV Motors

10/14/2009 2:15 AM

Relay is not suppose to protect motor from Short circuit. for Protection against Short Circuit, Fuse are must.

Reason is Short circuit capacity of Vacum contactor is ver y less compare to fault level of bus. Hence, contactors are not suppose to clear S/C fault.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#4
In reply to #2

Re: Type 2 Coordination for 3.3 kV Motors

10/18/2009 2:33 AM

Yea,...I agree for LT motors its protected by fuse,contactor.....but in case of HT motors we use VCB breakers for the range upto 11KV.thre we never use HT fuse.....relay will trip breaker on fault whatever the fault is .......vacuum contacotr in your case is nithing but a VCB I think.....pls clarify.

__________________
"Know something about everything and everything about something"
Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#5
In reply to #4

Re: Type 2 Coordination for 3.3 kV Motors

10/19/2009 2:26 AM

It is vacuum contactor. Vacuum Contactors are aslo avaialbe for MV Applications.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#6
In reply to #5

Re: Type 2 Coordination for 3.3 kV Motors

10/19/2009 1:38 PM

But why dont you use VCBs?What application is the motor for?

__________________
"Know something about everything and everything about something"
Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#7
In reply to #6

Re: Type 2 Coordination for 3.3 kV Motors

10/20/2009 2:15 AM

cost & low fault level of the system.

Register to Reply
Active Contributor

Join Date: Aug 2009
Location: India
Posts: 12
#3

Re: Type 2 Coordination for 3.3 kV Motors

10/15/2009 4:54 PM

Hi, Good day.

Generally the HT fuse for HT motor is selected based on the 1.3 to 1.4 times of the full load current of the motor. Little more also depends on the fuse manufacturer. Following link of bussmann fuses will help you in identifying the fuse selection for HT transformer and motor. Hope i have clarified your query.

http://www.bussmann.com/pdf/abe14678-ac07-4a08-8813-faa12ccda82e.pdf

__________________
Mind is like a parachute, no use if you do not open it
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Type 2 Coordination for 3.3 kV Motors

10/21/2009 7:54 AM

Though there are no ready-made Type-2 Co-ordination charts for HT/MV Motors as in the case of LV Motors, the concept to be followed is the same. You have to superimpose the curves of the Overload Relay (may be a motor protection relay's thermal overload element), the HT HRC Fuse and the Vacuum Contactor's Braking Capacity. As in LV Motors, the Over load Relay Curve operating time should be faster for all currents below the breaking capacity of the contactor and the HT HRC Fuse operating time should be faster very near to the breaking capacity of the contactor. That is the cross-over point of the OLR & the Fuse Curve should be well before the contactor breaking capacity.

Reputed Motor Protection Relay Manufacturers would either advise to disable or would disable at the factory itself, the overcurrent(short circuit) element in the motor protection relay if the motor is contactor-fed.

Register to Reply
Anonymous Poster
#9

Re: Type 2 Coordination for 3.3 kV Motors

11/25/2009 8:09 AM

please let us know your address and contact no and SMS to 09326128410, I will clear all of your doubt

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: Type 2 Coordination for 3.3 kV Motors

11/25/2009 4:36 PM

There is an ANSI classification for MV motor starters, and Class E-2 is the standard for most applications. In order to claim a Class E-2 rating, the fuses and contactor must be tested / coordinated together, because unlike LV components, the Vacuum Contactors have a relatively lower Fault Current capacity. So as Electrical Expert said above, you MUST coordinate the breaking / withstand capability of the contactor with the let-through of the fuses, as well as with the OL protection device (Motor Protection relay or Thermal Overload relay). Basically, the OL protection and contactor must be able to interrupt anything up to the let-through of the fuses, the fuses must take care of everything else up to the Available Fualt Current of the system.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 10 comments