I have installed an electric wire underfloor heating wire under a tile floor. My resistance through the wires was about 43 ohms at the beginning of the installation. After checking resistance after laying about 20 tiles I found an infinity reading indicating a broken wire. The two resistive conductors are twined in a single jacket and they are spliced together at the far end to complete the circuit. I can access the two wires feeding the loop and right now I can still get at the end of the wire where they have spliced the two wires together. How would I locate the break? Everything is under about 3/8" of ceramic tile. Is there an RF tester for such a problem?
Re: non contact circuit continuity tester
10/20/2009 12:02 AM
Why didn't you try to find out where it was at that time?
10/20/2009 8:20 AM
Mike,thanks for the reply. I did try to find some physical indication of where the open was but since the tiles are over the wire the only indication that I had was when I tested, by then the adhesive had set. Since then I have found out there is an audible monitor that you can put on the wires that will sound immediately when continuity is lost. The question remains, how do I find the fault now?
Good Answers: 18
Re: Non Contact Circuit Continuity Tester
10/20/2009 11:34 AM
See Livewire and ECM ECM explains the use of Time-Domain Reflectometry (time of flight and return echo) and Thumping (high voltage pulsing).
Other methods which aren't as accurate is to take both wire ends loose and connect only one to 120 volts (or whatever your service is) and use a sniffer type voltage detector such as this Greenlee GT-16. This device is adjustable and will detect the presence of voltage on a wire from some distance, but since the sensitivity is adjustable, you should be able to determine within an inch or two the location of the fault.
10/20/2009 5:06 PM
Yes I can do that. Never thought of feeding in 120V. I'll try that. It doesn't matter if I am an inch or two away, the fault should be be either under one tile or two adjoining tiles. The company that manufactures the cable sends a rep , at a cost, and he pumps in enough voltage to cause an arc. Then they scan with infra red scope to see the hot spot on the tile. I'll try myself first to see if I can locate it. Thanks. GA
Good Answers: 39
10/20/2009 11:17 PM
Most telephone installers have an inductive tracer sometimes called a 'fox & hound' or similar. Very cheap, sold at Home Depot and most electrical wholesalers I have used the same one for almost 15 years now tracing broken wires on boats. also at home. Only time it gets confused is if wire runs parallel with conductive metal pipes for long distance. Powered by 9V battery.
http://www.mcmelectronics.com/product/72-6966&cid it includes a continuity checker when you can connect to the wires as you described.
Elnav
Good Answers: 123
10/20/2009 11:39 PM
GA and a good tool. I have used it for years with great results. And affordable too.
Bob
10/21/2009 5:51 AM
Regards.
This type of Testers are used to detect the Short-Circuits in a open-cables while walking & not in open-faults. May be of little use in burried cables.
Moreover a separate tone generator is required to use.
Haajee
10/21/2009 8:31 AM
I'll get to Home Depot today to try one. I do have a cheap one from Princess Auto. it may help as long as it will work from about 1/2" from the wire as that is about the thickness of the tile.
10/21/2009 5:59 AM
Regards.
A GA for good info links.
But I think that TDR is not is normally for Transmission Cables & a costly solution.
Of course TDR can be used for such problem faults.
10/21/2009 12:33 PM
GA. You said to connect 120V to only one wire. You should specify that it must be the hot side of the 120 V (black wire, shorter flat hole in the US), and that it will only find the break if the break is in that wire. if the break is not found on the first trace along the cable, then the hot side of the 120V would have to be connected to the other wire and repeat the trace. Power line frequency has the advantage of practically no inductive/capacitive coupling to the other parallel wire. The audio and especially RF frequencies will have such coupling, which may make it harder to find the break.
Fluke has the "VoltAlert" which is similar to the Greenlee unit, for under $30. Mine is an early one, and has to be within about an inch to 'see' 120V. There is a newer model that works at lower voltage, so should see 120V from a little farther away.
I use mine every Christmas to find the failed lamps in series Christmas light strings.
Among other places, the Flukes are sold at Sears and Graingers. I'm pretty sure I've seen a cheaper version from China at Home Depot.
10/21/2009 8:25 PM
WOW, where have I been Hiding? I just returned from my local Home Depot. My Fluke is probably 10 years old, and only works down to 90V, if I recall correctly. The Greenlee supposedly works down to 5V, and is only $16, so I bought one. I'm anxious to try it! If there had been one made in USA, I'd have gladly paid twice as much, but no such luck!
10/22/2009 11:48 AM
DOUBLE WOW! In one case the Greenlee was able to indicate the presence of 120V 60Hz from about a foot and a half away through air, and could easily trace the path of a 3-wire 120V cable behind drywall, from several inches away from the wall. It could not trace the same cable from the outside, which is no surprise, as there is a layer of aluminum foil on the insulation. I'm really impressed!
Good Answers: 93
10/22/2009 5:47 AM
Yes, that's the one I was thinking of in my post #10.
I know the British Post Office used a system based, I think, on a Wheatstone bridge arrangement for finding underground cable breaks. The only reason I know about this is because I have copies of a series of patents from between 1917 & 1927, held by my great grandfather when he was a Post office engineer. These relate to fault finding & ways of multiplexing telephone lines and, rather oddly a design for a car petrol gauge.
6
Re: Non-Contact Circuit Continuity Tester
10/21/2009 2:37 AM
-Use a battery-powered portable AM/FM radio set to AM tuned between stations. Adjust the volume loud enough to just hear background noise (hiss). If you have an earphone for the unit, great, that will make discernment of the wire break easier. Holding the radio an inch above the floor, follow along the path of the cable buried in the floor until a peak in the noise is heard from the radio. This is of course done with power applied to the circuit under test. The point in space where the heating cable break is will be broadside to the loopstick antenna inside the portable radio so orientating the radio back and forth in the area near to the spot noted will allow you to zero in. Don't be inclined to try adjusting the tuning or volume of the radio from the setting you started out from. The radio noise generated from the break in the live circuit will be greatest right where it is. For this test, leave the far end of the heating cable connected as you've mentioned. I've used this method to find cable breaks in concealed non-metallic cables, as an electrical contractor and it has never failed me.
10/21/2009 8:27 AM
I'll see if I can get this method to work. Sounds reasonable. As long as I can get to within a foot of the break I can take up a few tiles.
Good Answers: 123
10/21/2009 9:06 AM
Welcome to the insanity. Nice answer.
Bob
Good Answers: 97
10/21/2009 2:57 AM
You can use a short wave or "CB" radio, noticeable interference will correspond with the break just wave the antenna over the tile.
Good Answers: 93
10/21/2009 5:58 AM
How about one of these non-contact voltage testers? The one I have will find a break in a mains cable just by running the tester along the cable. It will also find live cables in cavity walls. The one I have linked to is a really cheap version, there are better ones from Fluke.
10/21/2009 8:44 AM
Looks much like the cheap ones available at Home Depot here. I'm getting one today to try.
10/21/2009 6:27 AM
Do you know fairly accurately how the wires are routed?
What about a cheap capacitance meter: measure the capacitance of about 1 yard of twisted conductors; then measure the capacitance between the two wires feeding the loop. That will tell you the approximate distance to the break.
The problem with all the RF "sniffers" is that the wires are capacitively coupled so if the break is only in one wire the whole cable will sing.
Good Answers: 53
10/21/2009 7:54 AM
This technique works with shielded cable but I'm not so sure with twisted wire. Basically you measure the capacitance at both ends and the ratio between C1 and C2 will give you the same ratio in distance units. No harm in trying.
regards,
Vulcan
10/21/2009 8:22 AM
My heating wire is actually not as you have drawn. There are only two ends. The circuit is simply one wire in a loop. It is resistive wire and the two loose ends are connected to 240v. It would not help to know the distance to the break because the wire is weaved back and forth across a 20'X 10' room about 4"-6" apart. I can only get to within about 1/2" of the wire with a tester where it is under the floor.
10/21/2009 11:12 AM
Back in the 60's or thereabouts, there was a heating system called Ceilheat which worked just this way. There were numerous failures which lead to the system falling out of favor and home buyers demanding a more reliable system but you may be able to google Ceilheat and find a contractor/installer that can find your location reliably. (By the way, I am betting on your connection point to the contactor or controller, or an open at your short at the far end, a broken wire after it is installed is a mite rare...)
10/21/2009 6:22 PM
I had a fairly cheap little led flashlight from fluke that had a voltage tester on it until it got broken. It would indicate which side of the outlet was hot by an LED that glowed red when you passed it by the slot. It would glow blue (i think) for ground side. You only had to be in the proximity of voltage for it to glow. If you had something like this you could follow the wire from above the tile until the LED stopped glowing red and started glowing blue only. Here's a link to one: http://www.toolup.com/fluke/lvd2.html
Always use protection.
10/22/2009 7:22 PM
Well, I bought a tester and tried it on a few things around the house. It really worked well. Then I tried it on the floor heating. It worked a bit but you could not rely on the result, too sketchy. Then I realized probably why it doesn't work on the heating wire. The problem is that the heating wire inside the sheath is arranged as a twisted pair of conductors unlike the side by side in a normal piece of house wiring conductor. Any EMF present is minimized by the arrangement and the sensor of the probe doesn't see a lot of EMF. It worked well down to the connection to the twisted resistive cable but after that not well at all. I'm out of ideas. Anybody else?
10/23/2009 4:21 AM
How did you connect mains to the loose wires?
1.) Live to one and neutral to the other. OR
2.) Live to both shorted together.
If you get different results there may still be a way. Can you get hold of some resistors, and a mains transformer (a shaver socket will do)?
10/23/2009 8:15 AM
Live to one, neutral to the other. Then also live to one only at a time and no difference in readings.
10/23/2009 8:18 AM
I'll have to try live to both shorted together today. That should eliminate some of the twisted pair shielding.
10/23/2009 2:27 PM
Live to both shorted together will virtually guarantee failure (unless both wires are broken), because the good wire will carry the signal past the break in the bad wire.
I just did a bit of experimenting, and with the Greenlee, I was able to adjust the sensitivity until I could trace a twisted pair (actually three twisted conductors - a standard computer power cable; hot, neutral, and ground, plugged in, but no load) behind a 3/8" ceramic tile and a 3/8 layer of wood. The minimum sensitivity that detects the signal will pulse on (when the hot wire is closest) and off as you run along the cable. There should be a pretty regular separation distance between on pulses. Increasing the sensitivity should increase the on portion and decrease the off portion.
Good Answers: 18
10/23/2009 2:34 PM
Ya' mean your heater (resistive) wire is twisted??? I have seen non-resistive, twisted wire connected to a long, single, resistive wire that's serpintine-laid under tile and returned to neutral, but I've never seen twisted resistive wire.
10/22/2009 8:06 PM
There is a piece of test equipment available, it is called a TDR. Time Domain Reflectometer. This piece of kit will tell you exactly where the break is in the cable to the millimeter.
These are not cheep, try to borrow one or possibly hire it.
Regards
Steve
10/22/2009 8:31 PM
Guest, I read up on the TDR. Unfortunately you would have to know where the cable is located under the floor. The TDR gives you the distance to the fault but if I don't know exactly where the cables are under the floor the fault distance from the test site doesn't tell me where in the floor it is. Thanks for the info.
Good Answers: 15
10/23/2009 6:26 PM
I've laid under floor heating in two houses. And there is an obvious requirement to know where the wires (pipes in my case) are, as you must space them +/- equidistantly to get an even heat distribution.
Given that it seems to me that Vulcan's idea should get you close. You do say you can get to the splice, and therefore we suppose, split it.
Regards
Chas
10/23/2009 7:57 PM
Yes I probably could split the splice.
Good Answers: 15
10/24/2009 11:46 AM
OK, if you split the splice then with Vulcan's idea you can determine the %age along the cable where the break is. If you then "retrace" your cable route you will find approx the position. Yo may also be able to use one of the other methods suggested as confirmation before you start ruining the new floor.
Good practice is to take a pic of all installations before they are covered. if you have a pic it will help a lot
regards
chas