power factor correction

11/11/2009 10:40 AM

Why does the capactr need to be in paralell rather than in series in order to improve the power factor

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: power factor correction

11/11/2009 12:04 PM

Consider the capacitor requirement- It will be much higher if the capacitor is connected in series. (I have done a rough calculation, and in that it is almost 3.5 times)

In case of series connection, the whole current has to pass through the capacitor- not only reactive, which anyway it has to accommodate but active too.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: power factor correction

11/12/2009 2:54 AM

Because if the capacitor is in series, the equipment will not run.

http://en.wikipedia.org/wiki/Power_factor_correction

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#3
In reply to #2

Re: power factor correction

11/12/2009 3:34 AM

Series compensation do exist and are the preferable ones in certain cases (eg transmission lines) for obvious reasons.

For other certain cases too these are used

Reply
Member

Join Date: Nov 2009
Posts: 7
#4

Re: power factor correction

11/15/2009 10:24 AM

When we add a capacitor in series with transmession line , the total impedance of the line (Xt) reduce , therefore voltage drop reduce , i.e. voltge regulation improved , also reactive power is reduce.

Adding capacitor in parallel with load to reduce the current needed (for the same power consumed) , therefore power fctor improved .