UPS Galaxy3000 20KVA Problem

11/24/2009 3:00 AM

I have a online UPS Galaxy3000 20KVA. It is showing a problem Inverter Ph2 V outside Tolerance. I am checking its LETR board. I am checking its IGBT power module

I have two Questions.

1- If you know the solution of the problem stated above then help me.

2- If you know the checking of IGBT power module BSM35GD120DN2E3224 with multimeter then also help me.

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Nov 2009
Posts: 39
Good Answers: 4
#1

Re: UPS

11/24/2009 3:29 AM

Please give the phase and line voltages of 3 phases. and also furnish the tolenrance what you set. don;t look at the IGBT first, as the chance of IGBT failure is very less.there may be problm with the measuring PT s or the set points or voltage calibration errors.

Please come up with the above details, so that we can give support to sot out

Regards

anand.mandarapu

Register to Reply
Member

Join Date: Nov 2009
Posts: 6
#2
In reply to #1

Re: UPS

11/24/2009 4:39 AM

Phase 1- 222V

Phase 2- 223V

Phase 3- 224V

I don't no how to check and set the tolerance.About two months ago it is working ok I kept it off, now when I turn on the UPS it is showing this fault. nothing is changed

Thanks.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: UPS

11/24/2009 7:39 AM

<...don't know how to check and set the tolerance...>

It will be found within the manufacturer's user manual supplied with the equipment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#4

Re: UPS Galaxy3000 20KVA Problem

11/24/2009 7:32 PM

There are a couple of items I would be checking:-

These UPSs have a Load Balance Tracking system, Check the current (Amps) on each phase, they should be within +/-8% of each other.
Quite often this is a problem on a lightly loaded UPS as it does not take much to exceed the set threshhold.

Next get the Inverter stack checked as a single failed unit in a modular set will also cause this error.

Next Step is to contact APC who now own MGE.

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Member

Join Date: Nov 2009
Posts: 6
#5
In reply to #4

Re: UPS Galaxy3000 20KVA Problem

11/25/2009 1:40 AM

how to check the inverter as in inverter there are IGBTs BSM35GD120DN2E3224 how to check it individually with multimeter

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Ali Saqlain (2); anand.mandarapu (1); PWSlack (1); Sapper (1)