Adapter Current Transformer

05/10/2010 7:16 AM

POWER TRANSFORMER RATIO : 154/34,5kV 16/20MVA

PRIMARY CURRENT TRANSFORMER : 100/5

SECONDARY CURRENT TRANSFORMER : 1000/5

PRIMARY CURRENT RATIO : 74,98A(FULL LOAD)

SECONDARY CURRENT RATIO : 366,58A(FULL LOAD)

AS YOU SEE FROM THE IMAGE THAT WE WANT TO PLACE A MECHANICAL DIFERANTIAL RELAY TO THE SYSTEM FOR TRANSFORMER PROTECTION.AND BY THE DIFERANTIAL OF THE PRIMARY AND SECONDARY CURRENTS WE DECIDE TO PLACE AN ADAPTER CURRENT TRANSFORMER.

I WANT TO ASK THAT ;

HOW CAN WE CHOOSE THE ADAPTER CURRENT TRANSFORMER?AND WHERE DO WE PLACE THE ADAPTER CURRENT TRANSFORMER(BOTH THE PRIMARY AND SECONDARY SIDES OR ONLY ONE SIDE)

THANKS ADVANCE,BEST REGARDS.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Adapter Current Transformer

05/10/2010 4:20 PM

Current differential relays provide adjustment taps (actually internal auxiliary CTs) for just this purpose. They are used for balancing the currents from the transformer primary and secondary CTs to match them, so the differential current is as close to zero (within some tolerance) under non-fault conditions. The relay instructions should explain how to choose the taps. External auxiliary CTs should not be necessary.

That said, you should get a qualified protection engineer to develop the proper settings for your transformer protective relays. Setting them incorrectly can leave you with a very expensive piece of junk leaking out all of its magic smoke.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#2

Re: Adapter Current Transformer

05/17/2010 2:29 AM

I think matching current transformers, also known as (Interposing Current Transformers) "ICT", are to be installed at both sides of the transformer to match the two secondary currents of the main current transformers (100/5 & 1000/5) which enter the differential relay.

Here is a rough calculation of the required ICTs based on that your differential relay is 5A relay.

At HV side of the power transformer:

The primary current of the main CT= 20 MVA/154*√3= 74.9 A

The corresponding secondary current due to the CT 100/5 A = 3.745 A

Thus, you will need ICT of ratio 3.745/5 A at the HV side.

At MV side of the power transformer:

The primary current of the main CT= 20MVA/34.5*√3= 334.7 A

The corresponding secondary current due to the CT 1000/5 A =1.673 A

Thus, you will need ICT of ratio 1.673/5A at the MV side.

It is to be noted that if your power transformer is designed for overloading (e.g. 10% overload), this % of overloading should be considered in the calculations.

Regards,

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Adapter Current Transformer

05/18/2010 6:07 AM

I prefer that ICT 1,673 / 3,745 A. You can use that only one side at LV side.

Is there any objection ?

Best regards...

Register to Reply
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#4
In reply to #3

Re: Adapter Current Transformer

05/18/2010 7:00 AM

Yes, you can; however, you will not reach the max. relay current (5A).

Best regards...