i m working with a company, our power factor is going low for few weeks, how can i check capacitor capacity and how much rating capacitor should i install to improve power factor
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing
Re: utility maintenance
05/17/2010 8:21 AM
TYPICAL CALULATIONS ARE GIVEN FOR IMPROVING P.F Q1 TO Q2 FOR 567 KW
CAPACITOR SIZING CALCULATION FOR CAPACITOR BANK
Here,
KW=567.00KW
Q1=0.85
Q2=0.91
C
=KW X (TAN (COS
- Q1) - TAN (COS-Q2) )
=567 X TAN (COS - 0.85) - TAN ( COS-0.91) )
=567 X (0.62 - 0.455)
=567 X 0.165
93.555
KVAR
Good Answers: 244
05/17/2010 6:54 PM
See this recent thread for detail calculation: http://cr4.globalspec.com/thread/54230/Capacitor-value
- MS
Re: Utility Maintenance
05/18/2010 11:11 AM
From your question, I understand that the problem is started for few weeks only. There were no problem before. So that means your existing design for the selection of capacitor bank is correct. Now, how did you find out that power factor is going less. From the Pf meter?...The solution for your problem is not to add capacitors. But you have to find out the reason for this and rectify it. Investigate the type of load and what are those load when you noticed low power factor. Inspect individually these equipments for example motors, UPS, flouresent lamps etc. If really the initial selection of your capacitor bank is correct, you can find the reason of problem from these equipments. Rectify it.....otherwise ill you add capacitors again, if tomorrow the power factor gone less again??, ( or you just posted for getting information of capacitance selection??