We have a pump connected to a 230 kw motor, 750 kw generator powered and with a Siemens Sirius Soft Starter 3RW44. The 3RW44 soft start is connected to a Siemens 230 kw motor (, 60 Hz, 380 volt, 415A on the plate). We have a 750 KVA Doosen generator connected to a Marelli power unit as the power source (3 phase 380/220 V, 60Hz, RPM : 1800, Amps : 1140, KVA : 750 ,Stand by Kilowatt: 600).
Commissioning of this 3RW44 has failed despite 3 visits from Siemens to calibrate the soft starter 3RW44 with the Siemens motor. We have had this unresolved problem going for 5 months now. (As a commercial shrimp farm, no pumps = no water = no shrimp = no business).
Recently the Siemens engineers said our 750 KVA generator is too small, stating, "The generator rated current is only 1140 A. This may not be sufficient to sustain the inrush current."
The softstart shuts down as we exceed the 110% allowance on the 110 volt supply momentarily as the end of the soft start ramp up. This always happens on switch over to by the softstarter to full pumping mode.
Can an electrical engineer put perspective on this. If we install a bigger generator the generator will run under load and this will damage the generator. Surely they are incorrect? What is the start-up amps and voltage typical for a softstart with a 230 kw motor?