Generator Amps Needed: Siemens Soft Starter Sirius 3RW44 to Start 230 kw Motor?

08/02/2010 2:11 AM

We have a pump connected to a 230 kw motor, 750 kw generator powered and with a Siemens Sirius Soft Starter 3RW44. The 3RW44 soft start is connected to a Siemens 230 kw motor (, 60 Hz, 380 volt, 415A on the plate). We have a 750 KVA Doosen generator connected to a Marelli power unit as the power source (3 phase 380/220 V, 60Hz, RPM : 1800, Amps : 1140, KVA : 750 ,Stand by Kilowatt: 600).

Commissioning of this 3RW44 has failed despite 3 visits from Siemens to calibrate the soft starter 3RW44 with the Siemens motor. We have had this unresolved problem going for 5 months now. (As a commercial shrimp farm, no pumps = no water = no shrimp = no business).

Recently the Siemens engineers said our 750 KVA generator is too small, stating, "The generator rated current is only 1140 A. This may not be sufficient to sustain the inrush current."

The softstart shuts down as we exceed the 110% allowance on the 110 volt supply momentarily as the end of the soft start ramp up. This always happens on switch over to by the softstarter to full pumping mode.

Can an electrical engineer put perspective on this. If we install a bigger generator the generator will run under load and this will damage the generator. Surely they are incorrect? What is the start-up amps and voltage typical for a softstart with a 230 kw motor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 2:52 AM

I have some doubts about the entire rationale here, but I don't yet see the total picture. The pump motor is about 38% of the genset kw capacity, so I am surprised that it won't start, especially with a soft starter. Does this genset have other loads on it? If so, maybe they could be disabled momentarily while starting the big motor, and then brought back on line.

You don't mention the FLA of the motor, which should be about 450A; rough guess. Once again, it seems that the genset's rated 1140A should be able to handle this on a soft start.

If the pump is the only load on the engine, why not skip all the electrical confetti and just drive the pump directly? No motor, no starter, substantial money savings.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Aug 2010
Posts: 4
#2
In reply to #1

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 3:16 AM

This is the only load on the generator. The startup amps on a direct drive is definitely too high for the generator (apparently "typically five to six times the full load amps (FLA) of the motor"), so we need a "soft start". I am not sure what the FLA would be on this motor. The plate on the motor has 415A. I assume this is the amps required to run the electric motor.

Register to Reply
Associate

Join Date: Dec 2006
Location: Doha Qatar
Posts: 43
#3
In reply to #2

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 3:31 AM

well you can test your gensets load carrying capacity on saorate load bank, may be your genset is not able to take load its rated for?

may have some problem in alternator chek its no load full load voltages and currents, if all is well than its not genset problem

__________________
Please save the power for Next Generation- Do ur bit
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#4

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 3:51 AM

I don know much abt siemens soft starter , but i know abt ABB or schneider soft starters....i believe they r very much similar............check this link on soft starter common settings.....u may get some hint....

http://www05.abb.com/global/scot/scot209.nsf/veritydisplay/2985284834bcff7fc1256f3a00274038/$File/1SFC132002M0201.pdf

__________________
shamith gambhir, electrical engineer
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#5

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 9:12 AM

I am surprised that Siemens engineers failed to setup a softstarter.

750KW genset is more than enough to start a 230KW motor with a softstart .....You or the comission engineer should check carrefully the parameters of the softstart, you may set a longer start time with a current limit within the safe limit of the generator, when driving a pump, special setting of the sofstart should be performed, enabling a high torque at startup.

if still failed, you should consider using a VVF in lieu of softstart, starting current will be as low as the nominal current of the motor...

__________________
dont say it, write it
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 12:22 PM

I am very familiar with the Siemens 3RW44 soft starter and I can tell you from here what the likely problem is.

If it is tripping at 110% current, that says to me that someone selected your soft starter as a "light duty" application, even though the Siemens literature doesn't specifically state that; and therein lies the flaw. The 3RW44 can be purchased based upon the expected starting duty of the load application. You have to pay careful attention to the specifications pages of their catalog, not just the selection guide, which is optimized to offer the least expensive option.

So the problem has nothing to do with the generator size, that should be plenty of capacity to do the job. The problem is, someone probably selected the cheapest sizing selection for the stated motor power and the soft starter itself is incapable of delivering enough power for a long enough time to suit your needs and is shutting down to protect itself.

You didn't state the size (part number) of the 3RW44 nor the type of "pump" you are trying to start; not all pumps have the same requirements. If you let me know all of the information you have I can tell you which starter you should have used.

If it turns out you have the right version after all, then the other less likely situation is that you have an older (or cheap) generator with an AVR (Automatic Voltage regulator) that is being affected by the harmonics created by the soft starter when ramping the motor. This used to be a very common problem, but years ago the generator mfrs figured out that they had to add filtering to the AVR circuit. Old units may not have that filtering, cheap ones sometimes don't bother as well.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2010
Posts: 4
#7
In reply to #6

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 2:33 PM

Hi JRaef:

Siemens technician has the soft as 3RW4447-6BC34.

The pump is a floating pump connected to the motor by a chain. Pump is the axial flow type, so drives water and has no suction head. 2.7 m3/sec delivery, 5 m total dynamic head, 480 rpm.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #7

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/02/2010 6:04 PM

OK, so that unit is rated for, at best, 432A but that's at 40C, 10 second maximum ramp at 300% current limit. If the ambient is 50C, it's only rated for 385A under the same starting conditions. If the ramp time goes out to 15 seconds, it's rating drops to 402A @ 40C / 385@50C and at 30 seconds ramp time it can only take 285A@40C / 260A@50C.

But from your post in another forum it is tripping on Over Voltage, so more likely it's a problem with the AVR filtering in my opinion.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Aug 2010
Posts: 4
#9
In reply to #8

Re: Generator Amps needed: Siemens soft starter Sirius 3RW44 to start 230 kw motor?

08/03/2010 1:12 AM

Thanks so for for this help. I have made more ground here in 2 days than in the last 4 months!

I am waiting for the AVR specification from the generator supplier.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (2); Le_Noble (1); msmir116 (1); SHAMITHGAMBHIR1 (1); Tornado (1); Zaidevans (3)