We are having some unexplained issues with our motor controller and 3 phase motors.
We produce a motor controller with two 30 amp three pole relay's. There is no mechanical interlock, but only a 1.5 second delay from our logic board so only 1 relay may be engaged at anytime.
The relay's are confiqured as a reversing contactor with the jumpers hard-wired. We utilize .50-1.0 HP single phase motors and .50-2.0HP three phase motors. The highest current draw for 3 phase motors is approximately 6.0 A. and 12 A. on start. Most of the time our motors draw 1-3 amps.
We have been seeing relay boards returned with 1 or sometimes 2 relay's burned out. When I say burned out, I mean totally destroyed and char-broiled. Other times the relay's survive, but the 25 amp tracking on the board is burned off. This problem has never appeared with single phase motors where there is much higher current draw. Three percent of the units have been returned and 97% are without issues. When the controller is replaced we never see the problem again on that site.
Obviously, the first conclusion is that somehow both relay's had both engaged. With the logic board returned and a new motor controller installed we have not been able to simulate the failure even with 500,000 test cycles. Even with 2 motor lines shorted or a dropped line we do not see the failure. We recommend 10 Amp fused disconnects, but that has been hard to verify and police. Even-so why such a catastrophic when the applied current is lower than the ratings of the relay or board tracking.
Any ideas would be appreciated.