DOL Resistance Starting Current

09/08/2010 8:24 PM

DOL starting current of a motor is 90 amperes at 400V if a primary resistance starter is used to bring down the current to 30A what other type of starter will reduce the starting current efficiently to 30A?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: DOL Resistance Starting Current

09/08/2010 11:10 PM

There are many speed controller in the market like Soft starter, Frequency inverter Control drive or speed drive. All these controller can give you a very good starting current to start your motor. They can ramp from zero current up to your motor full load current according to your set time in the inverters.

Check out all these controllers with your local suppliers and ask for their advice which is a best controller for your application.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#2

Re: DOL Resistance Starting Current

09/09/2010 3:41 AM

you can have it by using an open transition RVS (wye-delta) motor control...employing the use of a control transformer tapped either fro 50-60% in wye and 80% in delta..

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#5
In reply to #2

Re: DOL Resistance Starting Current

09/09/2010 10:54 PM

In todays solid state world, Simon's answer is much better.. and cheaper

Register to Reply
Participant

Join Date: Sep 2010
Posts: 4
#3

Re: DOL Resistance Starting Current

09/09/2010 7:54 AM

Except for VFD, all other motor starters will reduce the starting current at the cost of starting torque since they all reduce the voltage supplied to the motor with the consequent reduction in torque by square of the voltage. So the starter you choose would mainly depend on your connected load and its speed-torque curve.

In a VFD, since the frequency is also reduced along with the voltage, the motor starting torque and the starting current would remain the same through out the starting period.

What is your connected load ?

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#4
In reply to #3

Re: DOL Resistance Starting Current

09/09/2010 9:33 AM

What is your connected load ?

A very good question and probably the first thing anyone should ask before deciding which type of system to select.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6
In reply to #3

Re: DOL Resistance Starting Current

09/10/2010 11:38 AM

You can have it set for constant torque but the current is definitely going to vary from start to full speed! You can maintain a V/f ratio...

It is true that the current will be low from zero to rated for the connected load and avoid the DOL surge at start.

Register to Reply
Anonymous Poster
#7

Re: DOL Resistance Starting Current

09/11/2010 8:34 AM

soft starter

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); baxterm (1); edison (1); LAA_Lucke (1); RDGRNR (1); rockraiden (1); Simon Wan (1)

Previous in Forum: Paper Lead Cable   Next in Forum: Suitable Battery for UPS, 120 or 200AH?

Advertisement