Characteristics of Equal Percentage Control Valve

11/19/2010 11:41 PM

Hi,

-What happens if the control valve is %EP, but we install a linear cam positioner or vice versa? what happens to the process?

-during normal process if DCS sends signal of say 60% to an equal percentage valve , what will be the local reading?will it be at 60% opening or different?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: characteristics of equal percentage control valve

11/20/2010 12:10 AM

Well you may get a throttle control capability, but it will all depend on a whole variety of other characteristics that you haven't mentioned. Here are a few of the parameters that must be known to attempt any calculation:

  • Pressure differential
  • Fluid viscosity
  • Piping diameter before and after throttle valve
  • Actual throttle range of opening

Now I'm certain that there are other pertinent parameters that one should know to answer this. Particularly when %EP exceeds MGH. This will clearly happen when the DCS attempts to put a Z domain pole inside the unit circle. This will certainly make this FUBAR.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#2

Re: Chareteristics of Equal Percentage Control Valve

11/20/2010 6:20 PM

>What happens if the control valve is %EP, but we install a linear cam positioner

I assume %EP means equal percentage which I notate as =%.

This is a typical configuration. The valve's trim is =% and since the positioner is linear, then the valve stem responsds in a linear fashion to the control signal. The flow depends on the process conditions, but the trim produces a flow rate with an =% flow profile.

>vice versa

If the valve trim is linear and the positioner is =%, then the valve stem position will not be the same as the control signal (in percent). It will have some relationship similar to the values in the table, (there are other =% curves than that shown in the table; travel of 0-1.0 is 0-100%)

The process response will not be identical because the valve trim is so different, but this combination will mimic the =% valve.

>during normal process if DCS sends signal of say 60% to an equal percentage valve , what will be the local reading? Will it be at 60% opening or different?

I have no idea what the value the local reading shows, but if you're talking about the valve stem position, it will be different than the control signal.

If the =% valve has a linear positioner with a 60% control signal, then the valve stem should be at 60% travel.

But the valve will not be at 60% of maximum flow rate, because 60% travel is only 25% of maximum flow rate for =% trim.

To get 60% of max flow rate from the valve the control system would have to call for something greater than 80% with its control signal.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Chareteristics of Equal Percentage Control Valve

11/22/2010 10:56 AM

<...What happens if the control valve is %EP, but we install a linear cam positioner or vice versa? what happens to the process?...>

Well, if the equal percentage characteristic is provided by the valve trim, then absolutely nothing.

<...during normal process if DCS sends signal of say 60% to an equal percentage valve , what will be the local reading?will it be at 60% opening or different?...>

It will be at 60% opening, though the flow through the valve will be determined by a function of the valve trim characteristics, the fluid properties, the upstream and downstream conditions and other characteristics, such as the piping configuration.

Ordinarily, the position of a valve is of secondary interest to what the process is doing and how the control loop is behaving.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#4

Re: Chareteristics of Equal Percentage Control Valve

11/22/2010 7:57 PM

Notice the flow response difference for a valve with =% trim, which in one case has a linear positioner, in the other case an =% positioner:

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Nov 2010
Posts: 18
#5
In reply to #4

Re: Chareteristics of Equal Percentage Control Valve

11/22/2010 9:39 PM

Hi bud,

can u share the response for a quick opening valve using a quick open positioner?

Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#6

Re: Characteristics of Equal Percentage Control Valve

11/22/2010 10:43 PM
Register to Reply