Anonymous Poster

You think you have seen it all with electricity?

11/22/2010 11:47 PM

This is really cool. Never ever seen lights do this. http://www.maintenancegeeks.com/forums/21-electrical-distribution/74-you-think-you-have-seen-it-all-with-electricity#74

Reply
User-tagged by 5 users
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: You think you have seen it all with electricity?

11/22/2010 11:52 PM

The "link" didn't work.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#2
In reply to #1

Re: You think you have seen it all with electricity?

11/22/2010 11:58 PM

http://www.maintenancegeeks.com/forums/21-electrical-distribution/74-you-think-you-have-seen-it-all-with-electricity?limit=6&start=6

Reply Score 1 for Good Answer
2
Guru
Canada - Member - New Member

Join Date: Sep 2007
Location: GTA Canada
Posts: 722
Good Answers: 23
#3

Re: You think you have seen it all with electricity?

11/23/2010 2:06 AM

Yes - that link as shown in #2 works fine!

I've come across this problem before, after one of our labs was re-lamped with new T-8 fixtures, with electronic ballasts (7 4' fixtures on each row; 6 rows) 347V. The contractor had mixed up the regular house power lighting neutral with the 'emergency' lighting neutral, which are supplied by separate transformers.

The funny thing was that the effect was intermittent, as most times the lights worked fine, however, every once in a while the same disco floor flashing would happen, leaving us scratching our heads, wondering what was happening.

After detective troubleshooting, we split up the mixed (crossed) neutrals to their proper assigned fixtures, and that fixed the problem. Hope this helps for your situation - Loupy.

__________________
Have a Happy! ;-)
Reply Good Answer (Score 2)
Participant

Join Date: Oct 2010
Posts: 2
#4
In reply to #3

Re: You think you have seen it all with electricity?

11/23/2010 6:02 PM

I have seen that video. I like that site, it has some good information along with documentation: user manuals........

Reply
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Loupy (1); Ouch_that_hurt (1); Tornado (1)

Previous in Forum: Earth Resistance   Next in Forum: AC or DC Current- Which is Most Fatal?

Advertisement