Normally we are using two current transformers for three phase system protection. Why do we use 2 ct's??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Current Transformer

12/01/2010 12:35 AM

Some countries still following the cost reduction concept as they were doing in poor country once even though ecomincally improving like India. we use 3 Cts in each phase.

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#2

Re: Current Transformer

12/02/2010 12:34 PM

Hmm, no answers so far, so I'll step out and make an attempt. It's been a long time, but I vaguely remember working on systems that used only two current transformers on a three phase system. To the best of my recollection, these systems were designed without a current carrying neutral (thus, they were typically not at the final distribution level--oops, but maybe sometimes a similar scheme was used on fairly high HP motors as well (well, motors that used CTs instead of just thermal overloads built into the starter).

Anyway, the basic idea was that monitoring two of the three phases also gives you a good idea of what's happening in the third phase.

Maybe somebody can straighten me out and refresh my memory. ;-)

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#3
In reply to #2

Re: Current Transformer

12/02/2010 12:49 PM

Klocner-Moller designed a motor test panel for me using only two Ct's on phases A and C, feeding a RedLion intelligent ammeter. The selector switch has A,B and C phase positions and it appears to work properly, but I wondered about that to. I haven't looked at the schematic.

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#4
In reply to #3

Re: Current Transformer

12/02/2010 3:27 PM

As long as there is no current carrying neutral, the current in any one phase is the (negative of) the vector sum of the current in the other two phases. So, to read the current in the B phase, you can have a switching arrangement that connects the two current transformers (on phases A and C) in series (iirc).

But, don't create your own switching circuit without knowing exactly what you're doing--a current transformer must always have a load or it will destroy itself and possibly hurt someone. Switches designed for such switching use things like make before break contacts to make sure that there is always some load (or a short, iirc) on each current transformer.

The destruction of a current transformer under no load conditions is because the voltage will tend toward infinity, eventually reaching a level to arc over the insulation somewhere in the circuit.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#5
In reply to #4

Re: Current Transformer

12/02/2010 3:37 PM

Thanks, I knew about open Ct's, I checked the schematic and the switch is indeed M-B-B. You have answered both mine and the OP's question.

__________________
CRTL-Z
Register to Reply
Anonymous Poster
#6

Re: Current Transformer

12/13/2010 9:52 AM

Differential protection

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); rhkramer (2); Unredundant (2)

Previous in Forum: Standard Temprature Correction Factor of Winding Insulation Resistance   Next in Forum: Live Tank Circuit Breakers

Advertisement