Transformer Question

12/13/2010 4:55 AM

IS IT TECHNICALLY CORRECT THAT A 60 MVA GENERATOR TRANSFORMER HAS NO OLTC FACILITY? PLS JUSTIFY.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: TRANSFORMER

12/13/2010 5:30 AM

Please turn off Caps Lock and define "OLTC".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Aug 2009
Posts: 11
#2

Re: TRANSFORMER

12/13/2010 6:18 AM

By "OLTC" do you mean "ON LOAD TAP CHANGER"? If so, then may i say i have not come across any transformers of that size in our grid without an "OLTC". I think the right word would be "TECHNICALLY CONVENIENT"- it would be hell to correct those low voltage scenarios if it were otherwise.....

__________________
A wise man didn't become wise over night.
Reply
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Transformer Question

12/13/2010 2:45 PM

It is technically COMMON that a generator step-up (GSU) transformer will not have an OLTC (and yes, it is an on-load tap changer), because voltage regulation is not the issue here. However, it would be possible to put one there - it just wouldn't serve any real purpose. The generator regulation should keep it at the appropriate voltage for its generation at any time.

OLTCs are generally used on transformers that feed loads, such as in distribution substations, so as to regulate the distribution voltage under varying load conditions.

__________________
To get the right answers, first you need to ask the right questions.
Reply Good Answer (Score 2)
Commentator

Join Date: Jan 2011
Location: India
Posts: 98
Good Answers: 2
#4

Re: Transformer Question

01/10/2011 4:56 AM

Mostly GSU doesnt have OLTC because it will make the generators to lose synchronism with grid. They all have OFTC ( Off Load Tap Changer)..

Please correct me if I am wrong.

-Vijay

__________________
You don't understand anything until you learn it more than one way.
Reply
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

PeterT (1); PWSlack (1); simbarashe gunzvenzve (1); vijaymail_electrical (1)

Previous in Forum: Real Electrickery   Next in Forum: LT Motor Test

Advertisement