My telecom crew did a great job of installing 10,000 foot run of single phase airguard single conductor/concentric neutral power cable from a mountain-top microwave tower site to a new generator building at the base of the mountain where the fuel tanks can be replenished from a railcar tanker. I hired a licensed electrical contractor (jry splicer + apprentice) to install splices and terminate the cables with 15kV-rated elbow connectors. In line were two rural 7.5kVa power step-up/down transformers. When we progressed to test phase and applied 240V from the new genset, the far end result was 560+ Volts from the secondary taps. Tap adjustments had been made to bring the output voltage down. Top site transformer is designed for a 480V secondary output. To compensate, we added a new dry transformer rated for 600V primary input and achieved the desired 240/120V output from its secondary for service voltages.
Problem: The genset is pushing 280V to compensate for a load which was not expected (I am not an Electrical engineer). Tested with no load, Main breaker open, it was producing the correct 240V output. Readings taken show a 63-Amp load with the 7.5kV distribution line (3 transformers, no load), exceeding the genset capacity of 48-Amps. This remote site experienced -25 degrees for a week, site visit showed the genset spewing oil due to no load. It has to be run to keep the lower site batteries up and not freezing. I need answers quickly, so I can send a crew out with the necessary components to correct the problem and get the system running. We continue to transport fuel/oil to the top site genset to keep the microwave system running.
Power distribution line is 1/0 Copper + concentric neutral - Single phase. I initially calculated a 2 to 4 amp no load condition. Baffled and need help.