Help Required for Determining Elec. Load for Roof De-Icing Cables

02/01/2011 1:03 PM

Hello Guys & Gals,

First, some background information:

I need some help from some of you electrical engineers guru's out there regarding the calculation of the electrical load for roof and gutter de-icing cables. I've been experiencing a lot of ice dam formations along my house roof eaves, gutters and gutter downspouts, resulting in some water penetration under our asphalt shingles and getting into the house that is resulting in some limited damage so far. It's been a cray winter here in upstate NY and we've now experienced no less than 9 snow and ice storms resulting in a layering effect of alternating ice and snow layers. I've removed most of snow and ice with a snow rake, used in combination with a water high pressure washer to try to break up the 8-inch thick ice dams atop of the eaves and rain gutters....a heck of a lot of backbreaking work......a real aerobic exercise regime!

I've already figured that I need to install at least 800 Lineal Feet of heating cables to cover all the eaves, rain gutters, and gutter downspouts. Of course I am going to install a automatic de-icer cable controllers (Temperature and moisture sensor type, UL and CSA listed). The cables I'm looking at to purchase are rated at 5 Watts per Linear Foot (some other manufacturers have 8 W/LF rated cables, but the cost is prohibitive). Also, since I've got so many runs of these cables I know that I'll need to install tee junctions and inline splices (available in kit form) or install several waterproof junction boxes for branch lines. I will also be installing a GFI and shut off switch in a exterior wall-mounted waterproof enclosure. Except the new circuit breaker, shutoff switch and GFI work which will be installed by a Licensed Electrician, I will be installing the heating cables and the controller units.

What I need help with:

Since I'm not an Electrical Engineer & my EE calculation skills are so rusty (actually crappy is what comes to mind...too many years since college electrical courses!). I need some expert assistance calculating the required electrical service cable between the circuit breaker panel and the automatic controller units.....per NEC Standard I need help in determining the type of cable and conductor size please. It'll be mostly attached to exterior wall siding except when it is installed down in the basement along the ceiling joists on its run from the circuit breaker panel inside a metal electrical conduit.....just to double check my Electrician's work.

Additionally, since I'm going to draw 4,000W of power (conservative at this moment and may actually be less), what size Circuit Breaker (Amperage) is required to be installed for this work? There's plenty of vacant room in the panel to install this breaker. The Voltage will be standard 120 VAC. I do have 220 VAC Grid service coming into the panel. Additionally FYI, I have a year old 7.56 kW DC Solar PV system with 2 Inverters, DC meter, and shuts offs which is tied into the same circuit breaker panel if that matters any...my guess is that it is probably not. The main Grid meter was installed by the power company and is the reverse-metering type.

Can you provide a sample calculation and/or NEC reference on how the new circuit breaker size was determined?

Thanks in advance for any assistance and suggestions that you can provide, and please have a great day!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/01/2011 1:43 PM

Hey Capt,

Sorry to hear about your ice problems.

4000W / 120V = 33.33 Amps

4000W / 220V = 18.18 Amps

At 120V go with a 40A CB, 2 #10 and #12 Grnd

At 220V go with a 25A CB and 3 #12

NEC Article 310

Hope this helps - Good Luck

I hope this blizzard we are experiencing right now peters out before it gets your way Gotta keep going out to brush the snow off the satt dish or I lose my internet

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#2
In reply to #1

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/01/2011 2:21 PM

Hey there KJK/USA,

Many thanks for the help! You're a life saver!!!!

Geeessshh, the comps are as simple as that? LOL My gray matter has turned to mush in regard to EE calcs.....been 27 years since my last Electrical Engineering course during my BSE college years. I suppose if you don't use it yo lose it! I really lost it BIGTIME and the electrical textbooks are safely tucked away in one of the large plastic tote boxes down in the basement...somewhere as there's a lot of them there unmarked from the last move.

Be safe and warm in this blizzard, especially clearing the snow and freezing rain off that antenna! We have the Dish Network for cable TV and I'm constantly clearing the snow off the antenna as well as the roof.....can't reach the antenna with my 28 foot long snow rake pole (chimney mounted) so I have resort to throwing snowballs at it! LMAO Ohhhh my aching arm and shoulder! I half expect to lose the signal any moment now since we're getting a heavy snowfall mixed with freezing rain now...about 3-4 inches per hour. YUKKKKKKK

Luckily, our Net is via the underground telephone lines here. Problem will be that the Grid will come crashing down on account of the freezing rain taking out the trees, power lines, and telephone lines. Thank goodness I have a standby 15 kW GenSet on auto switch just in case. It'll power up the entire house, and then some!

Again, thank you for your assistance KJK!

===CaptMoosie

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#5
In reply to #2

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 9:56 AM

If I may add, since your system is capable, it will be more advisable to go for a 220 volts system rather than 110 volt. Not only it will require a much smaller wire gauge and lower CB amperage, the 220 volt heating system will also add a balanced loading to the existing electrical system.

__________________
vsar
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#3

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 7:45 AM

The ice on the roof is caused by the heat from the attic melting the snow in the upper section of the roof. The water then drains down to the lower part of the roof that is usually cooler and freezes. This produce ice jams and icicles. Adding heaters might help reduce the symptom but will not solve the problem.

It would be a better investment to add insulation in the attic and improve its ventilation. You would then save energy (summer and winter) in the next 20 years instead of spending it.

In Canada, we use R-40 as a minimum for ceilings and place large ventilation chimney to draw the warm air from the attic. Here are a few links:

http://www.joneakes.com/jons-fixit-database/1497

http://www.polarcentral.com/maxivent.htm

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#4
In reply to #3

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 9:48 AM

Trouble is that pesky sun hits the roof, and causes melt. But its true, that since I properly ventilated the attic, the ice dams are much less of a problem. Upstate NY and Southern Ontario (where I live) are pretty close together, and both get the most miserable wet snow imaginable. A drive through the countryside towards Potsdam will take you past several buildings which have collapsed due to ice build up. They get hit worse than Canada does! Go figure.

__________________
If it was easy anybody could do it.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#6
In reply to #4

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 10:42 AM

You are correct that the sun has something to do with it but when the roof is well ventilated, the melting only happens in the above freezing days where the ice doesn't form in the eaves. Unless a cold front comes rapidly, the day's melted show has time to drain (mostly) before freezing.

I used to own an old house that made icicles in the end of winter. I built my new home with good roof ventilation and insulation. This has eliminated the icicles where my neighbor's older home still have them. On my new house, only the eaves through fill with ice. I am planning to paint the inside black this summer to see if I will get enough thermal gain to keep them dry in the winter. I want to use passive solar heating...

This all to say that I understand how difficult it is to implement the real solution but it works.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#17
In reply to #6

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/03/2011 1:33 PM

The other contributor to ice buildup on the edge of the roof is heat escaping from windows (yes, even the newer thermal windows are still "holes in the wall" compared to real insulation!) and along the interface of the top of the wall stud plate and the rafters. There is often quite a lot of heat escaping at that junction, either by air leakage.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#7
In reply to #3

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 11:44 AM

Unless the gas furnace vent exits the roof where the problem exists, as it does on my roof. All the attic insulation in the world will not stop the melting created by the gas furnace vent. I get a massive build up down roof from this problem.

Question for the Canadien - My local is not too different than yours, as the only thing between me and your country is a "great" big lake. I have given up on rain gutters because of 5 months of lake effect snow and below freezing weather. Do they still install them up there?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#9
In reply to #7

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 2:43 PM

Yes. But I am not convinced that they are that useful when the house is on a hill with good drainage.

On flat surfaces or even worst when the yard slopes toward the house (actually a common problem), moving the water away from the foundation is important. Unfortunately, the gutters bring other problems...

I am still looking for a good way to clean them or prevent leaves accumulation.

Regards.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#8

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 11:48 AM

Hello All,

Thanks for the valuable insights guys.

Unfortunately, I can't get up into the attic like I wish I could because I need to lose some more weight and it's a tight fit up there getting through the 24" x 24" ceiling door. Then there's dealing with the wooden roof scissor-trusses spaced @ 24-inches o/c. As far as I can tell I only have roughly 4-inch depth of fiberglass batte insulation between the truss bottom chords. I have no idea of whats in the roof eaves. I suspect that there's probably very little insulation there in the eaves as they only extend out 18-inches from the exterior wall face and are approximately 4-inches deep. I desperately need to find a way into the attic or hire a Contractor to blow some more loose insulation into the attic space. BTW, this is a very well-built modular pre-fab house built in 1986. A new very high quality 30-year asphalt shingle roof was installed 3 years ago. We never had any previous ice dam problems until this Winter, but then again they were mostly mild winters with very little snow fall accumulations, unlike what we have experienced this Winter.

I do know that we have a very good continuously vented roof ridge and eave soffit vents, so air circulation is probably not the culprit. Snow and ice tend to stay on top of the roof for a very long time, even when we have sunny days. Lately we have been clobbered by a series of snow and snow/freezing rain storms the past 45 days or so....we just went through Winter storm #10. Where I cannot reach the upper reaches of the roof with my 24-foot long roof rake I have about 24-inches of standing alternating ice and storm layers. The bottom-most layer over most of the roof is a compacted layer of ice that's well-adhered to the new shingles, unless I was able to break it free with my high pressure power washer...max. pressure is around 1,750 psi. I have it hooked up to a 30-foot long telescoping fiberglass pole where the rubber hose runs up it's interior and is topped with a high pressure fan pattern brass nozzle (or other type sometimes). Ice and now removal has been tedious and somewhat ineffective, with the end result being that I get soaked to the bone even wearing my old water resistant US Army Artic gear. Plus I get frozen pretty quickly, especially my hands! ACCKKKKK!!!

Yusef, I think I know what building that you are describing up near Potsdam! I frequently have to drive up there as my 2nd daughter is currently attending SUNY at Potsdam.....I'm the Bus Service for her and her buddies!!! LOL It's a long long freaking drive from here (down in the Mid-Hudson River Valley). I personally feel that the Snow Load Map included in the New York State Building Code should be bumped up another 10 PSF, with no reduction permitted whatsoever in the superimposed design snow loads used for design roofs, especially for prefabricated wooden roofs. Over the past 34 years I've forensically investigated dozens of damaged and collapsed roofs, both for residences and commercial/business buildings.

FYI, this morning I posted a thread in this forum regarding the issue of leaking roofs and the need for new snow and ice removal technologies, with a corollary blurb busting on "Phil the Groundhog". Please check it out!

Keep warm and safe folks!

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
2
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#10
In reply to #8

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 2:56 PM

I have no idea of whats in the roof eaves. I suspect that there's probably very little insulation there in the eaves as they only extend out 18-inches from the exterior wall face and are approximately 4-inches deep.

There shouldn't be any insulation in the eaves. They must be vented and allow the air to flow into the attic.

I desperately need to find a way into the attic or hire a Contractor to blow some more loose insulation into the attic space.

Probably a good investment to add 4+ inches of insulation. Make sure that you don't stop air circulation from the eaves.

I do know that we have a very good continuously vented roof ridge and eave soffit vents, so air circulation is probably not the culprit.

My neighbor has one of those. It is covered with snow and rendered mostly useless. It only works once enough heat has seeped from the house to melt chimneys in the snow.

unless I was able to break it free with my high pressure power washer...max. pressure is around 1,750 psi.

Do not spray water on the roof, you will make the problem worst unless you clean all the snow. The snow will act like a big sponge and increase its weight. A pressure washer would probably damage the shingle.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Good Answer (Score 2)
Anonymous Poster
#12
In reply to #10

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/03/2011 12:43 AM

Perhaps he should look at salt, or some other chemical fix?

Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#15
In reply to #8

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/03/2011 10:03 AM

When you put on a roof, you should roll out a couple of layers of "ice and rain barrier" onto the plywood. It is a wide black rubber sheet, sticky on one side. It is required by code up here, but because it is "up there" out of sight, often they skip it. Beats tar paper all hollow. Then you have to put up shingles or steel on top of that.

You tell me you have fairly new shingles. So ripping out the shingles and nailing up the correct roof material may not be cost effective. (Heck, I put up steel right over top of my crappy old ashphalt shingles, and that roof will not leak while I am alive!) If you are getting leaks, the roofers did not install the ice and rain barrier. Personally, I don't trust the the heaters. They can fail on you when you most need them, and they are a continual drain on an increasingly fragile and overextended electrical grid. Mine were on there when I bought the place, and they quit working after about 5 years....weather will do that to electrical joints.

Oh, and your snow rake won't be useful once you have stuff up there....be it solar panels, or ice dam busters. My neighour dumped a bag of salt on it last winter. Fixed the problem, but killed all his wife's flowers.... grrr.

Anyway, just chatting...not really suggesting anything. Roofs are near and dear to my heart...I seem to be spending a fair amount of time up on roofs fixing problems that should not be there in the first place.

__________________
If it was easy anybody could do it.
Register to Reply
Power-User
Canada - Member -

Join Date: Sep 2006
Location: Canada
Posts: 435
Good Answers: 4
#16
In reply to #15

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/03/2011 12:02 PM

"I seem to be spending a fair amount of time up on roofs fixing problems that should not be there in the first place."

Is this the kind of time you spend on the roof?

http://www.youtube.com/watch?v=U9hbNeA_aH4

__________________
Handle every stressful situation like a dog. If you can't eat it or play with it, just pee on it and walk away. - unknown.
Register to Reply
Anonymous Poster
#11

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/02/2011 10:56 PM

power=voltage x current [A]

the circuit braker shall be about 50% more

.

Register to Reply
Anonymous Poster
#13

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/03/2011 4:26 AM

HEY YOU ARE NOT THAT BAD ,HOW DID YOU COME UP WITH 4000W IN THE FIRST PLACE

JS

Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#14
In reply to #13

Re: Help Required for Determining Elec. Load for Roof De-Icing Cables

02/03/2011 8:31 AM

Dear Guest,

To arrive at the 4,000 Watt figure I knew I needed no less than 800 linear feet of de-icing cables to cover all of the eaves and partial up the roof (serpentine pattern) + cable draped over the roof ridge vents (currently water is entering through them....backed up ice there too), + back and forth runs of cables in all of the rain gutters & gutter downspouts.

The de-icing cables I'm purchasing are rated at 5 Water per LF.

Total P = 800 L.F. * 5 W/L.F. = 4,000 W

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); CaptMoosie (3); KJK/USA (1); marcot (4); PeterT (1); Phys (1); Rick@cae (1); vsar (1); Yusef1 (2)

Previous in Forum: Unbalance Current Calculation?   Next in Forum: Relay Rating

Advertisement