Bury Depth of Fire Mains Pipe (Commercial Application)

02/12/2011 7:05 PM

Hi guys, I would like to ask your expert advise. I was working with my head engineer regarding the bury depth for Fire water line mains, we end up arguing with the bury depth of the pipes. My head engineer wanted to lessen the cost of excavation so he decided to install the fire mains pipe about just 3 feet average deep with respect to the pavement elevation. I suggest, a deeper trench about 6 feet but I was a little skeptic, I aint got any references or codes to present him. I believe, there should be a typical depth for the installation of these fire mains, we're on commercial facililty/building construction. I hope you could help me find some reference. Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/12/2011 7:24 PM

I'd go with the head engineer's recommendation. It's obvious you don't know the requirements, if you are asking total strangers for advice.

Cheers.

Reply
Anonymous Poster
#18
In reply to #1

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 8:17 AM

Yes Lynch, don't do any due dilligence for yourself. Believe whatever other people tell you, Bahh sheap.

Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#2

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/12/2011 8:06 PM

I assumed you have some fire hydrants to install. Check the dimensions of your hydrant accessories(spools), you might have ordered a set (elbow & spool in one) fire hydrant accessories, just like some model of CROW fire hydrant. You have a big problem there if depth of trench will not match preferred fire hydrant accessories.

__________________
" To infinity and beyond" - Buzz Lightyear
Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 4:26 AM

Is the pipe flanged or is it spigot-and-socket? If spigot-and-socket then the burying depth will be related to the size of the thrust resistance blocks needed at bends; the greater the depth the less chance there will be for a socket to blow open at the critical moment.

Burying deeper gives greater protection from frost. Frost is a function of latitude, which hasn't been revealed to the forum.

Check local Civils codes for the best practice, and follow them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 2)
Anonymous Poster
#19
In reply to #3

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 8:19 AM

Thrust restraint blocks are out dated in new construction, we use Retainer Glands. Look at MegaLug 1800 series.

Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#22
In reply to #19

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 9:13 AM

Granted that concrete thrust blocks are antiquated and expensive to installed, and that MetaLug mechanical retainer glands (or it's "equivalent".....see, I don't use the word "Equal") are a great option, BUT you must first get the approval of the municipal water dept. or water authority having jurisdiction. You must first win over their minds and hearts in order to get any sort of approval for what is not the norm.

In order to even use MetaLug restraint system you had better be prepared to know the Pros & Cons of using it, let alone knowing how to design it correctly, especially when it comes to tying back into the pipe sections (like PVC C-900 and DIP pipes w/ push-on rubber gasketed joints). Otherwise you're just fooling yourself, and you're design is ripe for possible failure.

I still like concrete thrust blocks at water main and sanitary force main bends. Call me old fashion, but with any sort of mechanical restraint system you are relying solely on the "pipe monkey" down in the trench to get it right by properly tightening the restraint bolts with his handy-dandy socket & ratchet. I have yet to date (nearly 34 years in this Biz) seen any Contractor's pipe crew down in the pipe trench with any type torque wrench assuring that he achieved the required torque values on the locking bolts.....unless you bitch to the foreman or the Contractor's manage loud and clear you'll won't be assured that every bolt has been tightened properly! If you don't, then there's a fairly good chance that the fitting someday into the future will ultimately dislodge itself when there's a pressure surge or a water hammer situation say when the water dept. personnel closes a gate valve or butterfly valve too quickly. Seen it happen all too often over the years as an engineering consultant and as a City Engineer.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Anonymous Poster
#30
In reply to #22

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 10:40 PM

the locking mega-lug nuts break off at the designed torq. If you use mega lugs you must also use restraints on the bell and spigot pipe. Also if you don't have good as builts of the existing water mains you will have to pour thrust blocks. Unless submitted and approved the inspecting authority will not allow mega lugs.

Reply
4
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#4

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 10:29 AM

The depth of pipe bury will depend greatly on where you're located and if you experience below freezing weather conditions in the Winter months. Most often, depth of cover (as measured from the pipe crown to the ground surface) is determined by the historical depth of winter frost penetration into the ground.

Here in upstate New York we typically install our water mains to a minimum 5.0 feet of depth below grade, unless you're located in the Adirondack Mountains and extreme north of the state where at least 6.0 feet of cover is required.

Most state Building Codes in the USA do not dictate minimum water main depth of bury requirements unless it has to do with the installation of water service laterals. Most NY, NJ, VT, RI, MA and CT municipalities follow their own Water Dept. standards and regulations + suggested minimum depth of bury from the state Health Dept. (Bureau of Water Supply, etc.) or other state agency having jurisdiction as well as suggestions made by water engineering (Civil & Environmental) consultants.

I hope this info helps you out.

===signed,

CaptMoosie, LPE/PhD

Civil, Structural, & Environmental Engineer

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply Good Answer (Score 4)
Power-User

Join Date: Aug 2009
Posts: 100
Good Answers: 8
#5

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 10:45 PM

Along with frost protection and uplift/thrust resistance you might want to consider possible conflicts with your other utilities as well as storm drainage. Here in SE Alaska we require a minimum 5' bury whereas further north they require much deeper bury. Since you have some flexibility with depth and alignment on water lines and much less with sewer and storm lines you might opt for deeper bury to avoid them. Be sure and maintain your horizontal separation from sewer wherever possible.

Reply
Anonymous Poster
#7
In reply to #5

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 11:12 PM

Thanks for the very informative response guys, but is there a really good reference regarding this issue. Like recommendations from NFPA or DIPRA or others? My instinct tell me that it should be buried deeper than 3 feet, since we are using push-on type D.I. Pipe and yes, we have unavoidable conflicts with other utilities, which consequently add-up 45 deg. bends- this i feared the most with out being assured that our subcontractor thoroughly installed restrained thrust blocks.

Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#6

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 11:09 PM

If the water in the lines will be static. It will stay that way if buried too shallow at any point along the frozen way..

If the depth of excavation is actually going to be a cause for concern ... money wise.. I can imagine it's a lot of pipe.. Which would increase the opportunity for failure.

Ask if he'll split the difference and go 4'?

As far as listening to the head engineer above all?

If any head engineer's would like to boast about their perfect track record.. I'm sure we would all love to hear about it.

...I've met a few that are perfectly cranky...

__________________
High Tolerance is Beautiful
Reply
Anonymous Poster
#9
In reply to #6

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 11:21 PM

You got my point JE in Chicago. lol. Before he was a little bit cranky making such decision, but i know now he started to realize my point and well, he got his resume updated already, if something goes wrong with the mains fire line on the testing and commissioning, it really cost a lot to rework leaking pipes when the pavement had already been made. That is the worst scenario i could ever imagine, and you know, when you are on a team, a fault of one is a fault of the others. Well, he can not blame me then. But, it will be same shame for our team for that kind of decision.

Reply
Anonymous Poster
#20
In reply to #6

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 8:26 AM

If the water lines will be static? WOW JE did you graduate from middle school?

Length and oppertunity for failure, are you serious? Split the difference and pay more to burry the pipe deeper but still in the frost zone, you should not be allowed to express your opnion.

I see there is no hope for Chicago or its morronic residents. Engineers you have met that are cranky, are so because they have to work with such a dimwitted fool.

Reply Score 1 for Off Topic
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#8

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 11:15 PM

There are codes available for the installation and other details of fire hydrants. You can refer professional bodies such as CIBSE ( U.K) ,NFPA sites to get more details.

Reply
Anonymous Poster
#10

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 11:33 PM

buried depth for electrical is 36" to top of pipe for most electrical utilities here in so cal. Most water here is below frost line. check with your local city water co. and see what they have for their mains and do the same.

Reply
4
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#11

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 11:41 PM

If this installation is in the good old US of A- put the decision on the code books! Go to your local Fire Marshall/Fire Inspector and ask him to look it up in the National Fire Protection Association codes. It will probably say that it must be a certain depth below the frost line. Next go to the construction inspector office or construction code office and ask them the same question and derive from them what the burial depth is. Almost every town/municipality/county/state has an office/agency that determines what the depth of burial of fire water mains has to be. Also, usually they have to inspect the installation prior to backfill in order to make sure you have installed it at least as deep as necessary, have used the right material for it to rest on, have used the correct materials, and that the work meets the standards. If you don't have them inspect it prior to backfill they could make you dig up the fill material so that they can inspect it.

As the local fire chief I once encountered a buried water line which wasn't buried deep enough and it was frozen at the time of the incident. The home was a total loss except for the foundation! By the time a tanker shuttle was established it was only useful for the overhaul and salvage.

If this not the USA, the same suggestion prevails- ask the pros! If the local agency can't help you, consult with a fire protection specialist.

Personally, I don't think this is the correct forum to ask what is necessary for a question such as this where the consequences of a poor installation could be so disastrous or expensive if it is overdone. Why base it on opinions from people whose qualifications you can't verify when the work has already been done for you in the form of local standards? Would you ask them the how to perform cardiac surgery? An improper installation has the same potential for killing people!

Good Luck, old salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply Good Answer (Score 4)
2
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#12

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/13/2011 11:58 PM

Check with your local Fire Department, they should be able to direct you to the relevant regulations.

Reply Good Answer (Score 2)
2
Power-User

Join Date: Nov 2005
Posts: 101
Good Answers: 9
#13

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 1:55 AM

There are two considerations for bury depth of flexible pipe. Probably the primary consideration, because it is applicable almost anywhere in the world, is the vertical soil pressure on the burried pipe. Obviously, the closer the pipe is to the surface, the lower the dead load from soil is on the pipe. However, the impact from live load increases. As the pipe gets deeper in the ground, the impact of live load lessens but the dead load from the soil above the pipe increases. It turns out about the optimal bury depth of flexible pipe for H20 Highway loads is about 5 feet deep. At this depth, the combination of live load and dead load is a minimum. I suggest you use google and look up a a graph of highway loading for buried flexible pipe. An example of the loading curve can be found within the documentation at http://www.pwpipe.com/literature/f/mkt-f-750.pdf. There are similar graphs for E-80 loading which is utilized for loading due to rail roads.

The second consideration that is applicable only has meaning in the areas where frost penetrates the ground during winter. In this case, a water main should be below the extreme frost level to prevent freezing of the water in the buried pipe should the flow of the water approach zero fps, such as at nighttime. Extreme frost depths vary but a good map can be found at http://www.ngs.noaa.gov/PUBS_LIB/GeodeticBMs/images/figure13.gif. The referenced map is for the United States. I am not sure where you are from, but I am sure that if you use Google or a similar search engine you could find a map of your local for frost depths, if it is at all applicable.

Finally, the design of thrust restraint can be a minor but important issue. While there are mechanical joints that use the existing pipe material as thrust restraint, I always recommend somewhat of a belt and suspenders approach, particularlly on short runs of pipe. I recommend restraining joints against undisturbed soil. The less the bury depth is, the greater the chance that the soils has been disturbed. If your water main crosses storm sewers, electric lines, data lines, or gas lines that were installed by trenching, I think it is much cheaper and more thrust restraint can be provided if the water main is located below these buried utilities. This is especially true if you have to regularly lower the water main to cross under buried utilities. Restraining vertical bends in the pipe uses a lot of concrete to construct over bend thrust restraint. Conservatively, the overbend pipe joint relies on the weight of the concrete to prevent the pipe from separating at the overbend joint. All the soil on top of the pipe is disturbed. In horizontal deflection of the water main pipe you can brace the pipe against the existing undisturbed soil. It is really worth the time and effort to minimize the amount of overbend thrust restraints. Look for the section on the design of thrust restraint in http://www.sdwas.com/Documents/Vol1/Downloads/Revisions/VolumeOne_Revisions_09-26-07.pdf

Finally, I recommend that you thoroughly read AWWA standard C150 - Thickness Design of Ductile Iron Pipe or C605of rUnderground Installation of PVC pipe (whichever is appropriate for the material you have selected. Shallower pipe will likely have to have a greater wall thickness due to increased impact loads.

I do not think these AWWA standards are available on-line. You will likely have to purchase them.

I would say good luck, but there is much more than luck involved in good engineering. Take the time to educate yourself.

Reply Good Answer (Score 2)
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#14
In reply to #13

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 2:03 AM

Would that optimum depth vary to a degree with the soil type also?, say mud to gravel, to sand to heavy clay ...

Reply
Member

Join Date: Dec 2011
Posts: 8
#37
In reply to #13

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

12/23/2011 2:08 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply Off Topic (Score 5)
Commentator

Join Date: Jan 2009
Posts: 96
#15

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 7:22 AM

Hi,

If you are in a place where the temperature can drop to sub zero for example, Toronto, you should consider burrying the water pipes below the 'freeze line'. My understanding is that it is about 4' below the ground.

Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#16

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 7:42 AM

We don't know where you're located. Knowing where you're at would probably nail this issue down once and for all, especially if you are in the USA or Canada.

Question #1 for the OP:

Was a Building Permit issued for this work in question? If yes, you may want to consult with the local Building Inspector/Code Enforcement Officer and learn from him/her what the local municipal code and standards are in regard to the minimum depth of cover requirements for water mains and service lines.

If that track doesn't work, then consult the local water department that has jurisdiction over your work, especially since you are tying into one of their water mains to install the fire hydrants and it's service lateral.

Question #2: Obviously you were probably required to wet-tap the existing water main so as to install the fire hydrant service line, so EXACTLY what was the depth of the existing water main where the tap was performed? If it's greater than 3 feet of cover, then that will form a basis of your next argument with the "Head Engineer". Note: most water departments require that one of their personnel be present at the time any Contractor (or anyone else for that matter) even excavates in the vicinity of an existing water main within a public Right-Of-Way, and in your case they were most likely present for any "Wet-Tapping" of the main. Find out from the Inspector on the project site who that head of the water department is as well as who from that department witnessed the main tapping. Also, you may want to ask if anyone measured the depth of bury of the existing main, and what if any discussions were recorded in the official project Inspection/Field Observations Report in regard to minimum depth of cover requirements the water dept. employee may have talked about during his field visit.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Anonymous Poster
#17

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 8:15 AM

In New England the minimum burrial depth without insultaing the main is 4.5 feet. This is due to the expected frost depth at 4-feet. What are your winters like? If your in FL than 3-ft is fine and a ductile iron pipe can withstand the HS-20 loading at that depth. Look up your frost zone, then burry the pipe a foot deeper or so. Insulation is MORE costly than an extra 2 feet of gravel backfill.

Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#21

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 8:55 AM

If ignorance is bliss, why aren't more people happy?

If water is moving at a velocity around 6 feet per second or more, burial depth could be at frost line. If the water is not moving, for example in a static fire line, NFPA 14 requires burial at least one foot below frost line. There is a chart of the USA within the NFPA appendix, but a much better bet is to discuss with local underground utility contractors, the local fire department authority, or local building officials. Typically, local required foundation depths will be at or below frost line, so that might be a safe reference point.

If you do not bury the pipe deep enough at the start, you will dig it up a few times (to repair frozen pipes) before deciding to bury it again at the correct depth!

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply
Anonymous Poster
#23

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 9:33 AM

Water pipes will freeze in winter at a depth of 7 feet in North Dakota if they don't have constant flow. As was mentioned by others...the Depth will depend on where these will be buried. Three feet will suffice in the warmer climates...but is far too shallow for the colder ones.

"Typical" as you describe will vary by the local climate.

Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#24

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 9:47 AM

I do not where this job is. The only concern is frost heave.

For this part of Canada we have had a very cold winter with several mild spells.

Most buried items that are less than three feet are moving. A lot of our roads now have speed bumps. The region is going nuts trying to keep with water main breaks.

It may cost more to go deeper, but it will be better if your in a frost zone.

Side note: About twenty years ago an engineer decided to bury a gas line above the minimum depth, in Toronto. Later, during new construction a back hoe hit it. The gas seeped thru and abandoned conduit into a building complex. Eight people died from the explosion.

Always ere on the side of caution. At least you will sleep better at night!

Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#26
In reply to #24

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 5:07 PM

All the discussion of the frost depth raises another question in my thinking:

Putting the fire main below the frost depth is obvious and logical - but what about the tap points or risers, how are they managed to stop them freezing up?

I have always lived in either a tropical or temperate climate that does not experience these problems, so I was wondering ......

Thanks

Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#27
In reply to #26

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 7:07 PM

WAWAUS, tap points, which are known here in the NE USA as wet-tapped corporation stops. They're the connection point at the main for the service laterals conveying water to the customer.

Usually we do not use riser sections here unless the water mains are over 10 feet of bury depth. Both the corp. stops and the service laterals are keep below the frost penetration depth (and plus some more for extra measure) same as the water main.

I hope that answers your question.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#28
In reply to #27

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 7:51 PM

I was thinking more in terms of fire hydrants.... where rapid access by the fire brigade is required in all weathers at all times of year...

Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#31
In reply to #28

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 11:24 PM

Fire hydrant valves are located at the bottom of the riser, well below the frost line. The the valve stem, usually with a pentagon shaped top on it, extends down through the fire hydrant to the valve located at the bottom of the hydrant.

Hydrants also have a drain located there which is also controlled by the valve stem. In the fully closed position the drain opening allows the hydrant body to drain to the subsurface. As the hydrant is opened the supply opens and water rises to the hydrant body. Until the hydrant is fully opened both the drain is open and the supply to the hydrant body is being supplied with water. When the valve is fully opened the drain is closed. This is why whenever firefighters open a hydrant they always open it all the way, usually about twenty plus turns of the valve stem. To leave the valve in a partially open position will cause the drain hole to flush away the subsoil around the hydrant.

If you see water coming up around a hydrant body it is a good bet that the hydrant isn't open all the way or there is a leak in the hydrant below the dirt surface.

The reason for so many turns of the valve is because you have at least a 6" diameter supply at possibly in excess of 100psi, which requires a lot of force to close the valve. Also it prevents hydraulic hammer actions in the water line from occurring from the valve being opened too fast or closed too fast.

Whenever a ball valve is placed in a fire water supply pipe it usually has an operator on it that requires more than 6 complete turns to open/close it so that it is opened/closed slowly to prevent water hammer.

Good Luck, old salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#33
In reply to #31

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/15/2011 1:15 AM

Old Salt,

Thank you that was very helpful and informative

Bill

Reply Off Topic (Score 5)
Commentator

Join Date: Feb 2008
Posts: 69
Good Answers: 2
#25

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 9:54 AM

Many references, standards, and local regulations etc. discuss minimum depths for water etc. pipelines, and as noted on this thread any applicable requirements should be consulted. I noticed one of the latter local requirements on the web in an area referred to a standard and was worded, "The 2010 Edition of NFPA 24, Section 10.4.3, requires that the depth of cover for fire service main pipe be not less than 2 ½ ft. or 1 ft. below the frost line for the locality. Where frost is not a factor, the 2 ½ ft. depth of cover is required to protect the pipe from mechanical damage." [The specific standard referred to there is of course for private fire service mains.]

Reply
Anonymous Poster
#29

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 9:03 PM

Thanks all you guys for very informative answers, we are actually in a temperate climate zone, no so frost are to be expected. The only thing i worry is for the push-on ductile pipes to be properly restrained and kept at depth where there should be no possibilities of joint movement. Anyway, now after seeing a lot of your reactions and advise, i realized the facts of bury depths for fire mains.

Anyway just curios, at below freeze zone its alright to locate fire mains even dry type or flooded type? Either of the two is ok? How common is dry type fire main compare to the wet/flooded type in the US. What is the most preferred type?

Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#32
In reply to #29

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/14/2011 11:32 PM

Wet is preferred due to faster supply time to the fire. Dry systems require the water to fill the supply pipes before there is any water to put on the fire.

Dry sprinkler systems are sometimes used for areas that are not heated. They are usually kept to a minimum due to the delayed supply of water, the higher initial cost of installation, higher maintenance costs, the need for an air compressor to maintain the system pressure and finally the higher costs of periodically testing the system (it must be drained and refilled with air).

Some systems use an anti-freeze/water solution in the exposed piping to prevent freezing. Once the head opens the solution, which is non-flammable at its concentration, flows out and is followed by water which continues to flow until the system is shut down.l

Good Luck, old salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply Score 1 for Good Answer
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#34
In reply to #32

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/17/2011 9:11 AM

They use a non flammable solution in the sprinkler lines? I never would have guessed..

__________________
High Tolerance is Beautiful
Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#35
In reply to #34

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/17/2011 1:39 PM

If you want a good laugh, then here it is.

Large box chain store, with a drive in freezer. Note, the floor is isolated and keep at freezer temp.

The freezer had a modified wet sprinkler system. Some twit with a fork-lift managed to shear off two of the sprinkler heads. These were thirty feet up at the ceiling.

The ice plugs held back the water and prevented the alarms from tripping. For how long this situation had been, I do not know.

One day the main door was left open, resulting in the evaporator coils icing up.

The solution was to run the defrost cycle for multiple times.

The result was the ice plugs let loose.

This is where the fun began!

1: no one in the store knew where the sprinkler control room was and or had a key for it, when found

2: the store was evacuated

3: the fire department showed up and had a good laugh.

4: the best part was that they used the floor cleaner machine was used to suck up all the water

5: the machine flash froze to the floor, and than by the time they had the sprinkler shut down it had a one foot coating of ice.

6: as there was a million dollar plus stock in the freezer it could not be shut down.

7: it took close to two weeks for them to chisel it out and extract it.

It was all I could do to hold it together!

Reply Off Topic (Score 5)
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#36
In reply to #34

Re: Bury Depth of Fire Mains Pipe (Commercial Application)

02/18/2011 8:36 PM

Not all anti-freeze solutions are non flammable. There was a recent blurb warning about use of anti-freeze that I need to dig up.

http://www.koverholt.com/2010/02/24/flammable-antifreeze-in-fire-sprinklers/

www.nfpa.org/assets/files//PDF/Research/RFAntifreezeSprinklers.pdf

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply
Reply to Forum Thread 37 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: