VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 9:22 AM

A 132 KW Induction Motor drive a Conveyor Belt consumes 76 % of the rated current (76 % of 233 A) If for the Purpose of Soft Start, VFD (ACS 800) is installed, what additional cost in terms of KWH will be added to the system?

Name Plate: 132 KW, 400V, 50 Hz, D, 233 A, P.F 0.86, 1485 RPM, IMB3

Input Power (Electrical) = 138.82 KW

Output Power (Mechanical) = 132 KW

Efficiency = 95.08 %

Part Load (at 76% i-e 177.08 A) = 105.5 KW

Motor will be operated at 50 Hz. Variable Speed feature of VFD will not be used. VFD installation purpose is Just for Soft Start (to Stop the breakage of Belt.) Belt is approximately 420 m long carrying 540 Tons/Hr of material.

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#1

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 9:32 AM

Here I have made an effort. Your help will be required to make it precise and remove the mistakes I have done here (expecting there will be many). According to my calculation it requires 31 KW additional.

After installation of VFD unit (I consider) three factor that will contribute to additional Cost (in Term of KWH).

1. Motor Efficiency:

Induction Motor Efficiency will drop a bit. I assume the drop in Efficiency to be 1 % . Now Input Power consumption of Motor will become

Input Power (Electrical) = 105.5 * (1.01) = 106.55 KW

2. Drive Efficiency (Losses):

Efficiency of the drives are normally in the range from 85 % to 91 %.I assume this drive to be 88 % efficient. So to get Output Power of 106.55 KW at the output terminal Input Power should be

Input Power (Electrical) = 105.55 * 1.12 = 119.35 KW

VFD Losses = 119.35 – 106.55 = 12.8 KW

3. Air Conditioning Cost:

According to a report by California State University Research Initiative and California Energy Commission Public Interest Research on page no 20 mention a formula for Air Conditioning Power requirement

http://www.itrc.org/reports/vfd/r06004.pdf

KW (Air Conditioning) = (100 % - Drive Efficiency %) * 2 * Input Power

KW(Air Conditioning)= 0.12 * 2 * 119.35 = 28.644 KW

In our country weather remains 60 % hot in a year so KW becomes

KW (Average for a year) =28.644 * 0.6 =17.18 KW

Total Additional Cost:

Total cost = AC Cost + VFD Losses & Drop in Motor Efficiency

Total cost = 17.18 + 13.85 = 31 KW

If the Motor runs for 1 Hour it cost 31 KWH

Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 11:15 AM

I think you are confusing the efficiency of the VFD with that of the mechanical drive components, and unnecessarily adding the latter into the cooling requirements.

The VFD should be around 97% efficient (varies by mfr). If you keep the existing starter as a bypass contactor when the conveyor comes up to speed, you can avoid almost all of this 3% loss, too.

For this application, be sure that the VFD has constant torque capability (conveyors need full or nearly full torque to start.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#3
In reply to #2

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 12:01 PM

Idea of a bypass contactor is a good idea.

Regarding VFD efficiency as

"The VFD should be around 97% efficient (varies by mfr)" I put some of my observations

Example -1.We have 1800 KW Fan 690 V operated. Through transformer 6300 V are converted to 690 V. This fan when I see (on the display of the drive) shows 1270 KW. When I see this Power from the MV panel (Power going out of the transformer) is 1450 KW. so where this power goes i-e 1450 - 1270 = 180 KW.

It means drives take 1450 KW of input power and inverters are going to out 1270 KW. Another explanation is to that whenever Air Conditioning units stop for a an hour there is significant rise in Temperature of Substation.

Example -2:

Same case as above a 2000 KW 690V operated motor. Drive display shows 1340 KW and Power going out of MV Panel (Siprotec Relay 7SJ series) is 1510 KW.

Example -3:

A 550 KW fan is driven by a VFD. ACS800 Panel shows 180 KW and on MV panel (Siprotec Relay 7SJ series) Power was 203 KW.

Example-4:

A 26KW, 400V, 50 Hz, Y, 48.7A, P.F 0.84, 1460RPM is driven through a VFD. Drive shows 22 % of Power (5.72 KW). When we measure the Power before VFD, current on three phases was 14.2, 14.4, 14.5. Voltage was 230 V (with respect to ground). Now

Input Power to VFD = 3 * 230 *14.4 *0.8 = 7.94 KW

Efficiency = 5.72/7.94 = 71 %

Although P.F is high but I am taking it 0.8

Register to Reply
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#5
In reply to #3

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 12:53 PM

If you are absorbing 110kW then VFD losses will be in the region of 3000W.

I looked up FUJI series and have figures of 2300 and 2500W at 110 and 132kW rated motors (mechanical power ratings, electrically more, of course).

The reduced efficiency of the motor should be partly offset by intelligent motor control at the part load, but I would expect efficiency to be within 1% of the 70% loaded motor data.

Also, there may be further stray losses due to harmonics in the supply side easily identified as cable heating etc.

Therefore, maybe total losses may be 3000-4000W if correctly adjusted.

When I've checked FUJI readouts at water works against mains analysers I found to be very similar (within 1-2%) so I'm not sure why you see such a big difference, but, power is power so I suppose the ABB readout is incorrect or your monitor is over reading?

Soft starts may not like the sustained high torque starting of long, wet conveyor belts and VFD is a good way to start, bypass if no speed control is needed then removes the VFD losses (or it can be used to start the next conveyor??)

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 12:04 PM

If you are concerned about throughput efficiency and you are not planning to vary the speed, do not use a VFD as a soft starter. Use a soft starter, they are different. A VFD will have losses even at full speed, a soft starter will not and it will cost roughly 20% of the price of a similar VFD (percentage varies with size, but this applies to the size you stated).

If you can vary the speed, and it is a centrifugal load such as a pump or fan, the savings in throughput energy reduction more than makes up for the small losses in the VFD. If it is not a centrifugal load, you will not save energy but you may consider varying the speed for other reasons, some of which may end up with net efficiencies in other areas. But only a careful evaluation of all aspects can determine that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#6
In reply to #4

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 1:16 PM

"A VFD will have losses even at full speed, a soft starter will not and it will cost roughly 20% of the price of a similar VFD (percentage varies with size, but this applies to the size you stated)."

As you are quite right there. Application is not a variable torque Load i-e Fan or Pump etc. Application is a conveyor Belt. It is approximately 420 m long and it is fully covered.

If we install a Soft Starter and Power Fails (due to some reason) and Belt at the time of failure is full of material. When the Power comes back, We have't an empty belt. At that stage could Soft Starter Provide enough torque to run the Belt.

In our neighbouring Factory, they put Soft Starter on Bucket Elevators (Constant Torque Load). The bucket Elevators took material high up to 105 m. When ever Power fails same sort of situation occur. After each half hour they gave command to the motor, Five to six Buckets get empty and tripping occur. To recover the system to the normal state it took about 6 to 9 Hours.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 2:13 PM

As you are quite right there. Application is not a variable torque Load i-e Fan or Pump etc. Application is a conveyor Belt. It is approximately 420 m long and it is fully covered.

If we install a Soft Starter and Power Fails (due to some reason) and Belt at the time of failure is full of material. When the Power comes back, We have't an empty belt. At that stage could Soft Starter Provide enough torque to run the Belt.

In our neighbouring Factory, they put Soft Starter on Bucket Elevators (Constant Torque Load). The bucket Elevators took material high up to 105 m. When ever Power fails same sort of situation occur. After each half hour they gave command to the motor, Five to six Buckets get empty and tripping occur. To recover the system to the normal state it took about 6 to 9 Hours.

You have several issues here.

Do you NEED to vary the speed? If so, you need a VFD, not a soft starter. The other issues become less relevant.

The scenario you describe at your other plant shows a lack of forethought. A good quality soft starter should offer the ability to increase the starting torque in the form of a 2nd ramp profile that you can select as a "loaded restart" scenario. So for example if you normally use 350% current limit and a 20 second ramp to start unloaded, if you have a shutdown, an operator selects Ramp 2 and the soft starter provides 450% or 500% or 550% current for 3 seconds or 5 seconds or 1 second, whatever it takes to accelerate the loaded conveyor. Either that, or use a bypass DOL starter for that scenario.

A VFD is NOT necessarily going to solve that problem. The difference in accelerating a load with a VFD vs a Soft Starter is, you can trade a longer acceleration time with a VFD without overloading the motor. But if you need full Break Down Torque from the motor to accelerate it fully loaded, only a Vector Drive is going to be capable of that, and only for a limited amount of time, and you are STILL going to need high current to accomplish it. The amount of line current will be less however, so that helps if you have a severely limited supply source. That is about the only legitimate reason to use a VFD as a soft starter.

Re: Bypassing a VFD. Be careful. Most PWM drives cannot be simply bypassed by closing a shorting contactor as you do with a Soft Starter. Remember that in a VFD, the line is converted to DC and re-created back into a NEW SOURCE of AC power going to the motor. There is NO relationship to the line phase angle and the load phase angle. So if you connect them out of synchronicity, you create huge voltage spikes that will fry the VFD transistors. it's the same as connecting two generators that are not synchronized. Some VFDs have ways around this, it's called "synchronous transfer" where the VFD monitors the line input sine waves and makes its output sine waves match before allowing the contactor to close. But very few VFDs have that capability and the ones that do are usually very expensive. The only alternative is to have a set of interlocked isolation contactors and you disconnect the VFD output from the motor before closing the bypass starter. But this inherently must be an open transfer scheme, so in the case of a conveyor, it will most likely slow down in the transition and a spike will occur when you reconnect. Something to consider.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Member
Ireland - Member - New Member

Join Date: Nov 2009
Posts: 9
Good Answers: 2
#8
In reply to #7

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 6:02 PM

'The difference in accelerating a load with a VFD vs a Soft Starter is, you can trade a longer acceleration time with a VFD without overloading the motor. But if you need full Break Down Torque from the motor to accelerate it fully loaded, only a Vector Drive is going to be capable of that, and only for a limited amount of time, and you are STILL going to need high current to accomplish it. The amount of line current will be less however, so that helps if you have a severely limited supply source. That is about the only legitimate reason to use a VFD as a soft starter.'

Really a VFD does not start like a soft starter or else you could simply make the soft start ramp longer? A VFD accesses the other end of the slip curve, the pullout torque, which is why it's so good and an efficient way to start. The soft start accesses stall and pullup torques which are much lower generally, hence the danger of overloading or overheating the motor during prolonged starting. Also, long conveyors take some time to start in the conditions described, the front might start but the tail end is much later! And high stiction loads whilst it's all breaking free.

'The only alternative is to have a set of interlocked isolation contactors and you disconnect the VFD output from the motor before closing the bypass starter. But this inherently must be an open transfer scheme, so in the case of a conveyor, it will most likely slow down in the transition and a spike will occur when you reconnect'

Of course you could overspeed the conveyor a little to take account of the small slowdown so the re-connection of the mains is at the correct rotational speed still on a decent part of the slip curve so that current is normal where the supply meets this speed, couldn't you?

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/14/2011 7:41 PM

Of course you could overspeed the conveyor a little to take account of the small slowdown so the re-connection of the mains is at the correct rotational speed still on a decent part of the slip curve so that current is normal where the supply meets this speed, couldn't you?

Yes, through trial and error and if the load was EXACTLY the same every time. I have seen it work at commissioning, then 5 days later it no longer works.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Member
Ireland - Member - New Member

Join Date: Nov 2009
Posts: 9
Good Answers: 2
#10
In reply to #9

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/15/2011 5:38 AM

Maybe the load compensation (slip) may help to keep the rotational speed more similar in different situations?

If it's a little bit too fast it's OK so long as you don't go above the synchronous speed of the mains frequency.

However, I haven't done this on a conveyor application, most leave the VFD in circuit!

Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#11

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/15/2011 9:45 AM

You do need a VFD or VSD.. whatever you want to call it for two reasons

1. Yes it can be used as a soft start, with the correct drive torque is not an issue.

2. A soft start only limits the inrush current, not frequency and soft starts are, in my application, are used where the supply is flakey (please ask if you need a further explanation on my use of "flakey")

A VSD will RAMP up to speed and provide the motor with the required starting current up to reach full speed. If your belt does stop when full, then this is when you want a SLOW/RAMPED start.

I worked in what was the largest steal works in Europe at the time and the raw material feed belt for the largest blast furnace in Europe was over 1.5Km long reaching a height of 100m plus, it used 3 large motors to start the belt and once started one would drop out. These were controlled by what was the forerunner of todays VSD's.

It used HUGE SCR's the size of a small dinner plate and the heat was unbearable, no-one asked about the losses

The point is, so you have losses, weight those againest not starting the belt, not feeding whatever it is that the belts feeds, the cost of repairing the broken belt, broken drive shafts etc, etc and then decide what you need.

I would say IHMO that in this case you need a VSD, and NOT a soft start, as the ramp up time can be controlled, to put less mechcanial strain on the belt etc.. and DO NOT think about a shorting contactor, and also think about harmonics. You can buy drives with almost zero harmonics

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#12
In reply to #11

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/15/2011 9:56 AM

GA This is also my opinion for this type of application, the VFD is far more suitable and sure than a soft start in starting in all my experience in quarries and mines etc.

__________________
Something new every day!
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/15/2011 4:01 PM

To all those who believe in magic and that a VFD is the answer to everything:

I love VFDs, I use VFDs, I know more about VFDs than most of the people I have ever worked with. One thing I have learned is the exact opposite of my tongue in cheek statement above; that VFDs are NOT suitable for every application, in fact no technology is suitable for every application.

A VFD has a very finite amount of current it can safely deliver. For Constant Torque, or "Heavy Duty" applications, that is 150% rated current for 60 seconds. I do not know of any VFD capable of higher than that without over sizing and for sure the ACS800 is rated that way.

Vector (and in this case DTC) drives can in theory make the motor create up to 300% of FLT (typical BDT on a Design B motor is 220%), so in that way the VFD is for sure better than a soft starter. But to do that the current needs to go to 150%. THEY CANNOT DO IT INDEFINITELY. So it's not really correct to say that a VFD can make the motor operate at BDT without stating the time qualifier. For some I have used, the 60 seconds at 150% must be followed by at least 5 minutes at 85-87% rated current. I seriously doubt you can start a loaded conveyor with that. So to be safe, one should always consider that the VFD is capable of 100% FLT continuously when using it as a soft start device. In some loads, such as inertia loads, that's perfectly acceptable and desirable. The short burst of high torque is also great for high friction loads, such as cranes and hoists. But when you have a high friction AND high inertia load, such as a loaded conveyor, it's not always guaranteed to work and for sure it isn't a simple thing. There are many many issues to consider.

On a separate note:

Many people have had bad experiences with soft starters, I feel that is mainly because they used some favorite brand that had severe limitations rather than approach the job with an open mind and consider the proper product to do the job. I know there are good options out there that could do this job in all likelihood. For a 132kW load, a VFD is a very expensive experiment. I would invest in hiring someone with SKM or ETAP software to do a Transient Motor Starting Analysis and see if it could be done with a soft starter for 1/5 the price, 5X the MTBF and 1/10 the MTTR. That's all I'm getting at.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#14

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/16/2011 4:10 AM

So, if my estimate at 3000W losses in the cabinet are realistic, and your cooling costs this x2 but with 60% weighting, then I'd estimate that extra losses are

3000 + (3000 x 2 x 60%) + harmonic losses in the motor + line

say 6600W + 1000W+1000W

about 9kW per hour run??

nothing's for free!! Anecdotally, many claim reduceed costs as the displacement pf is improved using a VFD.

How often does it start? This is an energy efficient part compared to other methods.

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2011
Location: Pakistan
Posts: 126
#15
In reply to #14

Re: VFD & Energy Saving-1: Cost of a Soft Start

02/16/2011 9:13 AM

Not so interested in motors (ops, slip of the toungue :) but putting up VFD definition might simplify....

(Source is an internet downloaded book/handout pages called Motor Control Centers:)

VFDs are also referre to as AC drives. A typical AC drive receives 480 VAC, 3 phase, 60 Hz input power which is used to START and STOP a motor and control the operation of the motor throughout the SPEED RANGE.

Reduced-voltage soft-start motor-starting controls, such as the Furnace Nordic reduced-voltage controllers, provides a SMOOTH START while minimizing the high starting current and TORQUE associated with across-the-line motor starting.

Hoping that would help, if not, then I might have a second input here. Hehehehehe....

__________________
--
Register to Reply Score 2 for Off Topic
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

abasins (1); Aghvel Niazi (3); brich (1); Carol (2); JRaef (4); MalcolmK (3); Tornado (1)