Previous in Forum: IEC 60898   Next in Forum: How Do I Calculate Max Load on my 1000 KVA Transformer?
Close
Close
Close
2 comments
Rate Comments: Nested
Anonymous Poster

Reverse Power Relay Problem.

02/18/2011 2:13 AM

WE have Installed New 750KVA T/C and IT's HT ,LT panel and Overhead Line (4KM) for our Construction Load of Township.

In LT Panel there is a ACB (L&T U Power 2000Amp) and 6 Distributed Feeder ( Min 250 Amp and Max 600 Amp).

We are Facing Following from In LT panel.

=When we charged T/C and HT and LT panel at first time We got announication of RPR Relay (c&S, Bp1-R ,5Amp). After reseting The Relay We charged Distribution Line.

= Right Now in Distribution Line Load is very Low Total Load on LT Panel is 100Amp and LT panel works well.

=But After Thee Day We are facing a problem when Power supply from Uper stream (From Power Supply Company) goes out at that Breaker goes OFF . When Supply goes ON from Uper stream We get Announciation of RPR .

= At that time We have to reset the RPR Relay and ON the ACB and Power remains Stable. We have observed that Only When Supply of Uper Stream goes OFF we get Announciation of RPR otherwise nothing goes wrong from RPR Relay.

=We belive that due to heavy inrush current RPR may operate but When supply goes of ACB goes OFF and when We get supply from uper stream at that Time Distribution Load is not in Picture (ACB OFF at that time) eventhough RPR goes ON ???

=We have also incrase setting of PR> from 5% to 20% (Max 30% in dial) and Time Delay from 5 Sec to 20 Sec but Still problems is continious.

What should we do?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate
India - Member - New Member

Join Date: Oct 2009
Location: INDIA
Posts: 49
Good Answers: 1
#1

Re: Reverse Power Relay Problem.

02/18/2011 10:38 AM

you have not mentioned the back up power status. if you are using any back up power for relay operations you may face this problem.

according to your statments i have concluded that you have connected relay before breaker try once by connecting relay after breaker

__________________
key questions why, what & how - just think
Reply
Anonymous Poster
#2
In reply to #1

Re: Reverse Power Relay Problem.

02/19/2011 12:47 AM

Thanks for Relpay,

Yes We have connected CT for RPR before ACB. Required to clarify the Effect of RPR connected before ACB and After ACB.

Thaks in Advance