UPS Neutral

07/15/2011 5:28 AM

Why UPS output panels require Double Nutral.

Kindly explain

Regards

Murali

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#1

Re: UPS nutral

07/15/2011 11:36 AM

Two is better than one (cheaper and easier to work with). Harmonic "control".

Register to Reply
4
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: UPS nutral

07/15/2011 6:28 PM

Non-linear loads cause harmonics in the power system. In 3-phase, 4-wire systems, the triplen harmonics (every 3rd odd multiple of the base frequency) are additive in the neutral connection. This causes excessive losses and heating of the neutral. By doubling the size of the neutral, the impedance (and therefore the losses and the heating) are reduced.

Emerson has a good explanation here.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Good Answer (Score 4)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: UPS nutral

07/15/2011 11:21 PM

GA to you, and thanks for the excellent link.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: UPS Neutral

07/27/2011 9:46 AM

To carry the real "RMS" Neutral Current, which includes Triplen Harmonic Currents too, which accumulate in the Neutral, apart from the Fundamental Frequency Current. The true RMSNeutral Current can go as high as 200% of the phase current. And, any UPS is the main source of such triplen harmonic currents. Hence, the UPS Neutral is sized 200% (Double Neutral) so that it does not overheat even in the above situation.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

cuba_pete (1); electricalexpert65 (1); kvsridhar (1); pwr2thepeople (1)

Previous in Forum: Current Capacity of al./cu. Strips   Next in Forum: Why The Middle Phase Excitation Current Always Lower On Transformer

Advertisement