Rotor Locked Current

07/21/2011 7:25 AM

what is rotor locked current and how we can calculate it?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Rotor locked current

07/21/2011 7:44 AM

LRA is approximately 6 times the FLA. If you use the NEC 430.251(B) has a table that will give you this figure. Check here about half way down for table 430.251(B)

Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2
In reply to #1

Re: Rotor locked current

07/21/2011 8:14 AM

GA for the excellent link. Thanks.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 4)
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#4
In reply to #1

Re: Rotor locked current

07/21/2011 12:43 PM

That covers majority of motors but not all, there are induction motors in the low power segments specially shaded pole type, which shows locked rotor current in the range of 1.2 to 1.5 times of Full load current.

GA anyway.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Rotor Locked Current

07/21/2011 9:11 AM

Divide the terminal resistance into the applied voltage.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Rotor Locked Current

07/26/2011 10:56 AM

Refer to the motor data sheet.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); kvsridhar (1); PWSlack (1); rakesh_semwal (1); wareagle (1)

Previous in Forum: IEC Surge Test / Fast Transient Test   Next in Forum: Feeder Protection Relay "REF615"

Advertisement