Wire Size and Type

08/14/2011 10:22 PM

I am running a 35 foot line to feed a rectifier. It is a 250 volt AC single phase 30 amp unit. It is designed for 0-6 volt DC / 300 amp output. It will run on a continuous basis.

I am wondering what size and type of wire to install from the utility box to the rectifier? Also, are there any other considerations I need to address?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Feb 2008
Location: East Tenneesse, USA
Posts: 685
Good Answers: 46
#1

Re: Wire Size and Type

08/14/2011 11:09 PM

I'm guessing there a step-down transformer on the AC side of the rectifier.

By the wire-current charts, #8 gauge should not give you any problems on the line side for the distance your going. Just get the appropriate cable insulation for the environment.

The output side I would look at heavy welding cables.

Other considerations, proper sized circuit breaker, proper connections "direct wiring" or "correct electrical plugs/sockets for use", grounding, proper insulating/jack protection of cable unless run in conduit.

Without more info on your setup/needs these are only best practice guides I can think of for now. Others on here may add to this.

__________________
Metal is the material, The forge is life, The anvil and hammer bring character and soul.
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Wire Size and Type

08/15/2011 4:14 AM

All the consideration needed is contained within British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2009
Posts: 43
#3

Re: Wire Size and Type

08/15/2011 9:14 PM

Thanks, that's just what I needed to know. I appreciate the response.

Register to Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#4

Re: Wire Size and Type

08/16/2011 2:20 PM

Good morning,

Refer to NEC Section 350.15 for conductor size and ampacity ratings.

Pay careful attention to the different ampacity rating for different types of conductor insulation, stranded or solid configuration, copper or aluminum, number/quantity of conductors and whether the conductors are in a cable, raceway, or free air.

Example:

On the primary power side the nominal size for copper at 30 amps would be size 10AWG. (Depending on insulation type chosen)

On the secondary power side the nominal size for copper at 300 amps would be 300 kcmil. (Depending on insulation type chosen)

Also: Depending on the rectifier configuration and controls, be careful that whatever you connect the primary source to is not sensitive to noise impingement. If the rectifier does not have proper harmonic frequency and other generated noise filtering capability, the signals induced/injected back into your primary power circuit can cause severe disruption and/or damage to any digital or solid state controls equipment connected to that power supply.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2009
Posts: 43
#5
In reply to #4

Re: Wire Size and Type

08/16/2011 5:56 PM

Thanks, good info.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

AZ Miner (2); metalSmiths (1); PWSlack (1); SHOCKISCAN (1)

Previous in Forum: How to Start Electrical Consultation Business   Next in Forum: Garage Door Opener Electrical Problem

Advertisement