The approach is 2 generators, facility power and a redundant UPS. The boundary conditions are:

1) 208/120 60 Hz critical power to a command and control center (possibly 50Hz-more on that later)

2) facility power is 415/240 50 Hz

3) System(s) to be sheltered in a narrow 40' ISO container (modified/cut as needed for doors, HVAC, etc)

4) estimated critical load 161 KVA (maybe less-as other players suggest otherwise)

With a redundant UPS, one would think that critical power/reliability is all taken care of. Derived design constraints become:

-UPS does frequency conversion (thus bypass is not viable if 60 Hz is the load requirement)

-use transformer to get either facility power or UPS output down to 208/120 (throws a redundant transformer question into the equation (keyed switches, etc)

Next challenge is too many engineers with a hand in the design with requirements/questions such as:

-research closed transition ATS (not need UPS?).

-want bypass (in case UPS [and redundant UPS]) fails (50 Hz to C2 center???)

-growth (scalable UPS)

What statistical foot can I stand on to stop the design reliability configuration insanity? The "what ifs" are just too many to cover. Is a belt, rope and suspenders needed?

__________________
This moment is as it should be.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Belt, rope and suspenders? Statistical insanity for reliable power

09/22/2011 10:20 AM

Redundancy is a factor of the critical nature of the system. I worked on a similar system for the military where they were powering air traffic control radar sites. The nature of the task may have dictated MORE of what you are calling "insanity" than they actually implemented, especially when I wad on the plane heading home, guided by that very system!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#2

Re: Belt, rope and suspenders? Statistical insanity for reliable power

09/22/2011 11:51 AM

I just attended a power systems seminar at Eaton in Pittsburgh. I was really impressed with their state of the art UPS and active power factor correcting equipment. Their UPS can go from standby to full power so fast that it doesn't have to run until needed. I have never seen anything like it.

Without sounding like an endorsement, you should look into what you can learn from them. Growth is not a problem and neither is redundancy if you pick your equipment correctly. Like I tell others, you will have to learn enough to know what you want. Not only will they tell you, they will demonstrate it. Of the nearly 10,000 people that have visited their labs, a common comment went something like "I learned more in 2 hours than I learned an entire semester in college."

The hardest part of finding an answer is knowing where to look!

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#3
In reply to #2

Re: Belt, rope and suspenders? Statistical insanity for reliable power

09/22/2011 12:00 PM

Their UPS can go from standby to full power?

Maybe you mean emergency gen set or something else?

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#12
In reply to #3

Re: Belt, rope and suspenders? Statistical insanity for reliable power

09/23/2011 7:27 AM

No, I mean what I said. Using IGBT transistors and fully charged ultracaps, the switch over time is less than 2 msec to full power.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Feb 2008
Posts: 638
Good Answers: 45
#4
In reply to #2

Re: Belt, rope and suspenders? Statistical insanity for reliable power

09/22/2011 12:17 PM

Ah yes, Eaton has been a player in this design. We are in the midst of trades of floor load, space claim (swtich gear access), wiring simplicity (wireway clutter in small area), air flow/heat dissipation and satisfying "What ifs". What if both generators and the utility power fails? (motorized damper ventilation system to keep UPS from cooking). What if the whole UPS fails? (bypass?). What if the transformer fails?

__________________
This moment is as it should be.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Belt, Rope and Suspenders? Statistical Insanity for Reliable Power

09/22/2011 2:11 PM

There are a few techniques that may help you, Fault Tree Analysis (FTA) and Failure Mode and Effects Analysis (FMEA).

http://en.wikipedia.org/wiki/Failure_mode_and_effects_analysis

http://en.wikipedia.org/wiki/Fault_tree_analysis

The hardest part is finding reliable failure rate data, but at least you'll have some handle on the relative magnitudes of the probabilities involved, and it may help point out some cascading failures that nobody had thought about. Ultimately it will come down to cost, scheduling, and the law of diminishing returns....and don't forget those events known as Black Swans....

"...The Black Swan Theory or Theory of Black Swan Events is a metaphor that encapsulates the concept that The event is a surprise (to the observer) and has a major impact. After the fact, the event is rationalized by hindsight..."

http://en.wikipedia.org/wiki/Black_swan_theory

Good luck!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Belt, Rope and Suspenders? Statistical Insanity for Reliable Power

09/23/2011 12:53 AM

If you have n pieces of equipment to function/malfunction, there will be 2n scenarios to consider....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#7

Re: Belt, Rope and Suspenders? Statistical Insanity for Reliable Power

09/23/2011 1:04 AM

There IS a system that does it all. It is not even new.

It only requires, that the non-interruptible equipment be DC powered. That is common in today's 48VDC medium voltage distribution fed from batteries / rectifier. It takes a generator / flywheel / diesel combination. In a power failure it takes less than a second to have it up and running. AC etc. can be sequenced on later. Odd equipment needing other power handled with inverters at all time on from the batteries.

Obviously, one can overcomplicate: what if battery fails, what if diesel fails, etc. Fukushima reminds us, perversely, that there is no end to the what ifs's. One has to terminate the what if chain at a certain point, firmly.

Register to Reply
2
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#8

Re: Belt, Rope and Suspenders? Statistical Insanity for Reliable Power

09/23/2011 1:28 AM

About UPS systems - a post by one of the regulars from a web site where I am a moderator -

There are 3 basic types of UPS systems.

1. Is what is called a Stand By UPS. These are the chaep ones you buy at a box store, plug into the wall, and then plug in your puter. All they are is a cheap battery charger and a electronic relay with a really crappy inverter, and a very cheesy 12 volt battery. Under normal operating conditions your puter is connected directly to the utility power, and th e is just sitting there doing nothing but standing by waiting for th epower to go out and keep the battery charged up.

When the power goes out, the electronic relay (static switch) operates to turn on the inverter which is already connected to the battery. It is fast enough to turn on to keep the puter power supply on while it switches. It is only made so when the power goes off, you can save your work and shut down until commercial power is restored.

2. The next step up is a Line Interactive (Single Conversion) is simular to the Stand By in that commercial power is fed directly to th eload equipment through a magnetic transformer. Regulation and continuous power to the equipment loads is acheived through the use of a Buck-Boost Inverter through the Magnetic Transformer. If there is any kind of disturbance like over voltage, the inverter will Buck the voltage down. If there is say a sag in voltage th einverter will Boost the voltage. If there is a failure of commercial power the inverter takes over completely.

The Line Interactive UPS are fairly expensive starting at around $1500 for a small one like 1000 Watt, and can run up into 100's of thousands for a large Mega Watt unit. The batteries are in a seperate container or located on battery racks and can be sized for whatever you can afford. Battery voltage can be anywhere from 12 volts to 600 volts

3. Is the Static or Dual Conversion UPS. These are the Cadillac of UPS systems used in mission critical environments like banks, data centers, and telephone offices. Dual Conversion means the AC power is ran to a rectifier to convert to DC to keep batteries charged, and supply DC power to the inverters. So the flow is AC to DC to AC. The inverters always online on and being powered by the either the rectifiers under normal operating conditions, and batteries if power fails.

As an added safety feature the Static UPS has a Static Bypass Switch in the event the UPS fails, or needs to be taken off line for maintenace. When in bypass the equipment then is connected directly to commercial power.

Static UPS systems are very expensive starting in the 10's of thousands for a small system of say 5000 watts for a single phase units, up to millions for a large Mega-Watts unit. The batteries are separate like the Line Interactive and can be as large as you can afford. Battery voltages will be 48 volts up to 600 volts.

So there is UPS 101 for ya.

Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: Belt, Rope and Suspenders? Statistical Insanity for Reliable Power

09/23/2011 2:21 AM

Belt, rope, suspenders?--you forgot the skyhook.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#10
In reply to #9

Re: Belt, Rope and Suspenders? Statistical Insanity for Reliable Power

09/23/2011 3:26 AM

I heard Siemens made them. Special order only though.

They come from the same shop as glass to wood welding electrode I believe. Wonderful stuff!

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#11

Re: Belt, Rope and Suspenders? Statistical Insanity for Reliable Power

09/23/2011 3:55 AM

Yep, mine was a Siemens one. Batteries rated for submarine use. Considering the savings of not having service outage, pretty reasonable at the price. Two New York blackouts with no interruption. Not bad.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

JRaef (1); leveles (2); NotUrOrdinaryJoe (2); RAMConsult (1); russ123 (3); szwasta (1); Tornado (2)

Previous in Forum: SVL   Next in Forum: Connect Three Phase Motor to Single Phase Supply

Advertisement