CB Making Capacity Rating

11/17/2011 12:01 AM

Good day to all.

My question is, what is the reason for specifying a making capacity. I understand the breaking capacity needs is specified since at larger or very large currents the CB might not be able to break the current due to the arcing or damage to the contacts, but what are making capacities trying to limit.

Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: CB Making Capacity Rating

11/17/2011 12:29 AM

Making current is an asymmetric one with a peak which can be as high as 220% of the steady state RMS current that the CB may be called upon to break. It may happen that the CB is unable to close and latch onto such a current. Some modern compact CBs, which cannot make and latch onto such high currents, have a "Making-current-release" which delatches the mechanism above the CB's max making capacity.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#2

Re: CB Making Capacity Rating

11/17/2011 1:16 AM

making capacity is represented as the Value of prospective making current that a switching device is capable of making at a stated voltage under prescribed conditions of use and behaviour. Reference is generally made to the short-circuit making capacity Icm (it is the Value indicating the capacity of the device to make and carry a high current without repulsion of the contacts. It is expressed in kA peak.)

Making capacity specifies the breaker's ability to withstand and close successfully against the effects of electromagnetic forces.These forces are proportional to the square of maximum instantaneous current on closing.

also have a look at these links for more understanding.

http://cr4.globalspec.com/thread/37632

http://cr4.globalspec.com/thread/69716

__________________
shamith gambhir, electrical engineer
Register to Reply Good Answer (Score 2)
3
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: CB Making Capacity Rating

11/17/2011 2:37 AM

Let us think, practically! Assume that you are undertaking a maintenance work during a plant shut-dwon. And, during this maintenance, your technician forgetfully leaves a screw driver across the three-phase bus bars, thus creating an unintentional phase-phase short circuit. Now, post maintenance, you are attempting to close the breaker, unaware of the unintentional short created. Now, what would happen? As the contacts of the breaker attemp to close, a very huge short circuit current would try to establish between these contacts. And, there would be huge electro-dynamic forces generated between these contacts, tempting the CB to explode. If the CB is not having a capacity to make or switch-on such short circuit currents, then the CB for sure, would damage, even damaging the installation and perhaps the operating personnel. Hence, a making capacity is specified for every circuit breaker.

This specification would tell the maximum peak current that the circuit breaker is capable of making, under specified conditions, without causing any damage to itself or to the operator or to the installation.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jun 2008
Posts: 14
#5
In reply to #3

Re: CB Making Capacity Rating

11/17/2011 2:50 AM

Ok, thank you. I'm getting the drift. Would appreciate if you may refer readings on how short-circuit generates this electro-dynamic forces, does this have to do with the contact voltage. What indeed would the contact voltage be if there exist a fault?

Thanks.

Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: CB Making Capacity Rating

11/17/2011 5:38 AM

All damaging effects of a short circuit are proportional to its square. Voltage does not contribute in these, it will come into the picture when breaking happens.

An excellent paper on the SC effects from Schneider Electric here...

ect162

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: CB Making Capacity Rating

11/17/2011 8:27 AM

If you study the paper ECT162, you may quickly lose interest that it is all about busbars, and not about the contacts of the CB. Please look this image near the end of the paper...it gives the calculation of the 'crowd effect repulsion' that happens between butt contacts. (Curiously, the Ragnar Holm formula is missing in the English version, it is there in the French version)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8
In reply to #3

Re: CB Making Capacity Rating

11/17/2011 12:14 PM

You made me chuckle with your comment about the screwdriver. While I was an apprentice we had just installed a new panel, the bars had been split in to sections during testing. Testing finished the fishplate joints were replaced, the foreman decided (wrongly) to energise without a final test. As I was the newbie I was given the honour to close the ACB. So I charged the breaker and pressed the close P/B, the room lit up! While we were in recovery mode one of the sparks walked in and came out with the classic question, "anyone seen my 3/8th spanner!" "No but we know where it ******* was!" He beat a hasty retreat.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13
In reply to #8

Re: CB Making Capacity Rating

11/18/2011 8:34 PM

That vindicates my stand! Thanks, Tony!

Register to Reply
Associate

Join Date: Jun 2019
Posts: 50
Good Answers: 1
#14
In reply to #3

Re: CB Making Capacity Rating

06/29/2019 6:27 AM

The making current of the circuit breaker is always more than the breaking current. To understand why making current capacity of the breaker should be more than its breaking current capacity, let's discuss how fault current behaves,what is the characteristics of the fault current.
When the fault occur in the electrical network ,the AC and DC current is present. The DC current magnitude is about 60 to 80 % of the AC current.

The peak value of the current during sub-transient period is
= 1.414 x I x 1.8
= 2.55 x I

Read More:https://sdvelectrical.blogspot.com/2019/06/why-making-current-of-circuit-breaker-is-more-than-breaking-current.html

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#15
In reply to #14

Re: CB Making Capacity Rating

06/29/2019 7:25 AM

The calculation is not as simple as you have projected.

It depends upon the system X/R ratio too.

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 14
#4

Re: CB Making Capacity Rating

11/17/2011 2:44 AM

Thanks for the responses.

My confusion is that, we have breaking capacities since the current would want to persist in the form of arc, but why does the same current "resist being made". When contact is open, no current exist, current will only flow once contact is made, once it is made and a fault still exist, it now needs to be broken (interrupting capacity).

Hope you may enlighten.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #4

Re: CB Making Capacity Rating

11/17/2011 1:29 PM

That a breaker can "close onto a fault of its maximum breaking capacity and break it" is fundamental - because the age-old inclination when a trip has occurred is to re-close the breaker, to see if it was a transient fault e.g. lightning strike.

Closing capacity is easy if it is a resistive load, but for example, a motor load may routinely take many times running current each time it is started, so a closing rating good for thousands of closures becomes necessary.

Register to Reply
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#10

Re: CB Making Capacity Rating

11/17/2011 10:58 PM

Making capacity of a circuit breaker is its capacity to close the circuit breaker under fault condition. This is expressed in terms of peak value (first cycle peak) and comprises of both AC and DC component.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#11

Re: CB Making Capacity Rating

11/18/2011 3:04 AM

i could not resist amplifying this aspect of making capacity, especially important for ACBs which need to have a 1 second short-circuit withstand capacity Icw (for time-based discrimination). The big, robust (and expensive) old ACBs could make, latch and trip right up to their maximum SC capacities with no problem. As technology improved, many things changed. Short circuit levels went up. Space becoming more expensive, compact devices became essential. New materials (plastics and metals) made this compactness possible. Microprocessor-based relays made the ACBs much more intelligent.

The compactness came with a compromise. The ACBs could withstand high SC currents for 1 sec due to some very intelligent force-compensating contact designs. But the ACBs could not close and latch onto the same high SC current !!! The closing energy input to the system was carefully designed for low bounce, long life etc, so it is usually inadequate to latch the ACB. So, if the ACB closes onto a high fault(higher than its max making capacity), the contacts will keep getting repelled and try to reclose, resulting in possible destruction of the ACB. Such ACBs are fitted with Making-current-releases, so that the mechanism is delatched as soon as the contacts touch at such high fault levels.

Here is an extract from Schneider ACB catalogue. Note that the "Make-and-latch" value of the SC current is lower than the 1sec Withsstand value. (Meaning that the ACB, if already closed, can withstand the SC, but cannot close onto that SC)

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#12

Re: CB Making Capacity Rating

11/18/2011 11:46 AM

There are cases where a breaker is combined with fuses, such that the breaker can make/carry extreme fault currents - but not break them, that task is done by the fuse. The two being co-ordinated, so that the CB safely clears faults for which the fuse does not blow.

Register to Reply
Active Contributor

Join Date: Jun 2019
Posts: 12
#16

Re: CB Making Capacity Rating

08/25/2019 5:44 AM

Making current capacity is about 2.55 times of the breaking current capacity. When fault occurs the current waveform is not symmetrical about its axis and during sub transient period the current has AC and DC components. If the circuit breaker is closed at fault the breaker must be capable to clear the fault.b The link may be useful for better understanding about making and breaking capacity of the circuit breaker.

Making and Breaking Capacity of Circuit Breaker

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#17

Re: CB Making Capacity Rating

08/29/2019 11:54 AM

A key element, mentioned in post #2 by SHAMITHGAMBHIR1, is that the contacts will attempt to repel one another under high fault conditions. This phenomenon is actually useful in opening a breaker during a fault because it speeds up the process of getting to where the arc is quenched. But if closing into a fault, that can cause the contacts to bounce and make matters worse. So the closing capacity has a lot to do with the ability of the breaker to withstand those physical forces on the contacts themselves

Breaking capacity has has more to do with opening time and arc quenching capability while holding together under the physical strain of the magnetic forces taking place between poles.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: Jun 2019
Posts: 12
#18

Re: CB Making Capacity Rating

01/27/2020 6:41 AM

The circuit breaker breaking capacity is expressed in RMS value. The circuit breaker of 21 kA (rms) breaking capacity can interrupt that much fault current safely. However, if the breaker is again switched in fault condition. The Peak current will be very high and it will be about 2.55 times of the breaking current capacity. The breaker should be capable to interrupt the fault current if it is switched on when the fault exist downstream of the breaker.

Making current capacity of the breaker(kA-Peak) = 2.55 x Symmetrical breaking current capacity

Read More:Making and Breaking Capacity of Circuit Breaker

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19

Re: CB Making Capacity Rating

01/27/2020 4:54 PM

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); debata07 (1); electricalexpert65 (3); JRaef (2); kvsridhar (4); Louwel (2); Rajesh52 (1); SHAMITHGAMBHIR1 (1); TonyS (1); vimal76 (2)