Inverter-Motor

11/22/2011 7:46 AM

I have observed in some inverters that they have mentioned only input dc voltage, current RMS, and power, but nothing about output 3 phase voltage?Does this mean we can connect load of any voltage?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: inverter-motor

11/22/2011 8:11 AM

In general, the rated voltage of the output appliance needs to equal or exceed the supply input voltage. Further details may be found in the inverter manufacturer's application data.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Inverter-Motor

11/22/2011 10:06 AM

The output AC voltage would be in proportion to the output frequency, subjected to the maximum input voltage.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Inverter-Motor

11/22/2011 10:38 AM

Inverters, plus rectifiers for DC, can be designed to convert from any voltage, AC or DC, to any other voltage, also AC or DC, at any desired frequency. The output power can never exceed the input power, but efficiencies can be high, with a small proportion of the power dissipated as waste heat.

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2011
Posts: 3
#4

Re: Inverter-Motor

11/22/2011 12:02 PM

Maximum inverter output voltage is a function of the DC bus voltage. Essentially, the RMS inverter output voltage is limited to DC bus voltage x 0.7072. For a motor requiring, for example, 380V at 50Hz, the DC bus voltage needs to be not less than 537V. It can be higher, but not (significantly) lower.

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#5

Re: Inverter-Motor

11/22/2011 11:36 PM

Within limits - yes. The inverter can run motors of the same voltage as the 3 phase input down to about 1/4 voltage. Lower voltage motors may cause problems with insulation breakdown if they are of old design as the inverter "pulses" quite high voltage even though the "RMS" is carefully controlled.

When you set up the inverter, you will have to enter the nominal motor voltage with a few other parameters.

__________________
johny451
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#6

Re: Inverter-Motor

11/23/2011 12:30 AM

Thank you for the comments. But what i m asking is that the inverter specifies only input voltage dc, Max 2min RMS current and rated power, nothing about "ac output voltage". If i need to connect a device of a particular voltage, how can i know whether the inverter is suitable for it?

for eg: if the inverter is of 48VDC input , 200A (RMS) max, 10KVA and i want to connect an induction motor of 400Vac 3 phase with 5KW power.As you can see here inverter doesnt specifies whether it is for a 400VAC output? Is it related to the power between the inverter and the motor? i m not sure please help me with this.....

Register to Reply
Power-User

Join Date: Jan 2009
Posts: 250
Good Answers: 7
#7
In reply to #6

Re: Inverter-Motor

11/23/2011 5:43 AM

Dear Sujinvipin,

output voltage is supposed to be the mains voltage where the inverter is sold. Probably 230 V in your case, hence 400 V phase-to-phase (check motor windings and how voltage is specified - star or delta? What is the starting system?). Voltage is not power dependent.

kbaker, max rms ouptut voltage can reach DCbus x 0.8166 (less the voltage drops on the IGBTs).

brgds

Snel

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #6

Re: Inverter-Motor

11/23/2011 9:31 AM

Reading the manual would help.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#8

Re: Inverter-Motor

11/23/2011 5:49 AM

In the case of a 48 DC volt input voltage, the DC voltage will be 48 Vdc.

The output ac voltage will be maximum 33 Vac (i.e. 48 * 0.7071).

The motor you can connect to this inverter will be

  • a 19/33 V delta / wye motor (connected in wye) or
  • a 33/57 V delta / wye motor (connected in delta).

If you use a motor 400V ac, this will not work, the voltage supply at the motor terminals is to low which results in a lower magnetic flux and a very low output torque.

There are two solutions :

  • rewinding the motor at a lower voltage or
  • using a step-up transformer 33 to 400 V between inverter and motor.
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Aug 2011
Posts: 93
#9

Re: Inverter-Motor

11/23/2011 6:27 AM

Is it possible to connect a 50Vac induction motor?

By the way can you please explain about the specification of

19/33V delta/wye (connected in wye) and 33/57V delta/wye (connected in delta) i didnt understand clearly.

Register to Reply
Power-User

Join Date: Jan 2009
Posts: 250
Good Answers: 7
#10
In reply to #9

Re: Inverter-Motor

11/23/2011 6:37 AM

The inverter will give you some defined voltage. If you need a different voltage, you may use a transformer (with heavy duty insulation to whitstand the weird waveform you get from an inverter).

brgds

Snel

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#11
In reply to #9

Re: Inverter-Motor

11/23/2011 8:09 AM

You can connect a 50 Vac motor, but the output power will we lower

I guess only 43% of the original output power.

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#12

Re: Inverter-Motor

11/23/2011 8:51 AM

Inverter specification as i have given indicates 2 min max RMS current,does it mean the current it delivers at starting for 2min and then return to normal. in case of induction motors connected to the inverter output , does this mean starting or locked rotor current ?

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#15
In reply to #12

Re: Inverter-Motor

11/23/2011 10:56 AM

If the inverter is capable to deliver 200 A rms during 2 min, and there is no additional information like S2 - 2 min or S6 - 20% Then I would use this inverter only during maximum 2 minutes.

Depending on the actual mechanical load of the connected motor, this motor will need less of more current. This current has to be supplied by the inverter.

The internal temperature of the inverter will rise as a result of inefficiencies. This temperature rise will limit the number of practical applications.

You can use this inverter for an application that only needs power during a short time, like an door opener that moves the heavy door only in the morning to open the gate and in the evening to close the gate.

It can only deliver power during 2 minutes, and when is delivers power, the output current must be limited to max 200 A rms.

I hope you see the difference between an application that has a 20 % duty cycle or an application with a 100% duty cycle.

100% duty cycle indicates continuous use, like a pump that runs for hours.

Register to Reply
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#14

Re: Inverter-Motor

11/23/2011 10:24 AM

You bet you can, don't forget to wear your PPE..

__________________
It's not Rocket Science
Register to Reply
Power-User

Join Date: Nov 2009
Location: Nnewi,Anambra,Nigeria
Posts: 146
#16

Re: Inverter-Motor

11/23/2011 8:48 PM

No you cant connect to any voltage.The inverter manufacturer must have specifications for the output voltages and power.Check for the output voltage and power rating in the manual,or supply the input and measure the output voltage for single or three phase.You should contact the manufacturer as well to be sure.Avoid making wrong connections that may damage the inverter or your load.

Patrick whowha

__________________
Patrick Whowha
Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#17

Re: Inverter-Motor

11/24/2011 12:26 AM

Rudy.leurs,

In an inverter specification i have seen, Peak current= 450A rms(2min) , Boost current= 540A(10sec) & continues current=180Arms(60sec),

So according to this data, doesnt it mean that the peak or max current is just happening at the initial start up, just as i told previously as Starting current ?

Secondly, can you tell me what is "Boost current" ?

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#18
In reply to #17

Re: Inverter-Motor

11/25/2011 5:09 AM

Boost current or boost as used in an inverter is the possibility to allow a larger current than normally suspected at low speed.

At low speed, the drives output voltage is also low. (the ratio Voltage / frequency must be kept constant.)

But this low voltage is devided over

  • the ohmic resistance of the motor windings and the ohmic resistance of the supply leads between motor and inverter
  • the rest of the voltage is used to create magnetic flux (which results in torque)

Because the voltage over supply leads and motor winding is almost constant, there is almost no voltage left over to create torque.

With the boost function you can increase the output voltage to overcome this fysical problem.

In your example, boost current = 540A (10 sec) , you have to be sure that acceleration has finished before the 10 seconds are passed. Additionally, you can increase the output voltage during boost which results in an higher current and motor torque. The limit will be 540 A

After start up, you current must decrease to maximum 180 A rms and the drive must be switched off within 60 seconds.

Keep in mind that this means that you can not drive a load for a longer time than one minute.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#19

Re: Inverter-Motor

11/25/2011 5:17 AM

Everybody is guessing in circles now. Please provide a URL to YOUR invertor's specifications so that some science can be applied to obtaining an answer for you.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); Johny451 (1); kbaker (1); Patrick Whowha (1); PWSlack (2); Rockyscience (1); rudy.leurs (4); Snel (2); SolarEagle (1); sujinvipin (4); Wal (1)

Previous in Forum: Buchholz Relay Trip Signal   Next in Forum: Are Harmonics Blowing up my Capacitors?

Advertisement