Replacing Old Electric Motors with New

01/31/2012 11:06 AM

We are looking to replace an old (1959) 1000hp motor with a newer motor of the same horsepower. The old motor is of the pedistal bearing type with a 9 inch shaft running at 394 rpm on 4160 volt. A typical over-built steel mill motor. We are looking at newer packaged frame motors and are a little concerned with the difference in size and robustness. (is there such a word?). I have been working with these motors for the past 25 years and I know that there is some difference with "old" verses "new". The torque curve might peak later, is the "new" 1000hp the same as the "old" 1000hp...etc. I am looking for some insight from someone who has done something like this before and might have some words of wisdom that I may not have thought of yet. BTW the loading on the existing motor is about 750hp at a 30% duty cycle. 5 seconds loaded and 10 seconds idling.

Thanks in advance,

Jim

Register to Reply
Pathfinder Tags: horsepower motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Replacing Old Electric Motors with New

01/31/2012 11:59 AM

I have replaced one mill motor similar to the one you describe, pedestal bearings etc. To be honest we went to several manufacturers with the specifications we required and waited for them to do the work. It was then just a case of picking one that suited us best and had the performance guarantees.

Sorry I can't be of more help.

One thing I will add, nobody on the maintenance staff was sorry to lose the pedestal bearings.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
5
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Replacing old electric motors with new.

01/31/2012 12:01 PM

I cannot attest to how well a new, specific manufacturer's motor will work for your specific application. However I can tell you what were the significant improvements and drawbacks over fifty three years that have made the same mechanical power motor such a much smaller size. Three parts of motor design improvements have allowed for most of the improvements in design.

IMHO The most significant change has been the improvements in ferromagnetic design. The core material still saturates with a magnetic field at a little above one Tesla. But the size of the hysteresis loop with the addition of some trace elements have been significantly reduced. Thus hysteresis losses have been decreased. Additionally it has become easier to make thinner lamination pieces so eddy current losses have also been reduced.

The improvement in bearing design have allowed for tighter tolerances of all moving parts. Tighter tolerances permit smaller air gaps between stator and rotor. Less core field strength is then required for the same gap field strength to induce the same net torque.

Lastly improvements in magnetic wire insulation thickness have permitted more windings in the same volume. Thus less current per winding is required to make the same core field strength. Additionally the insulation does not breakdown as easily at high temperature as the old varnishes.

The drawback of all of these improvements is that more often than not there is less of an "over design" to a motor's capability.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 5)
2
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3

Re: Replacing Old Electric Motors with New

01/31/2012 4:11 PM

Not a motor man although I have replaced a few.

You will find Redfred's last comment to be prophetic. No motor built today will last the 53 years your current motor lasted.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Replacing Old Electric Motors with New

01/31/2012 4:46 PM

The largest electric motor I've ever spec'd was 15 HP/50 Hz. So, take my opinion for what it's worth.

But, I will attest that Fred has it right.

We bought a LOT of motors when I built process equipment, and I got to know how they are really built.

Send your requirements out for bid and see what industry has to offer.

Good Luck.

Register to Reply
Member

Join Date: Sep 2010
Posts: 8
#5
In reply to #4

Re: Replacing Old Electric Motors with New

02/01/2012 12:01 AM

I followed up on a replacement similar to what you are looking at. We had replaced an old (1947) GE DC Drive Motor on a Big Betts VTL. The nameplate on the old motor was 50 hp. The local A-B distributor had spec'd out a new 50 hp replacement motor, much smaller in package size and shaft size. The lathe operator couldn't make nearly as aggressive a cut with the new motor as the old one would do day in and day out. I put meters on the drive and tweaked a bit to optimize it. At full rated power, it was only half the motor our Grandpas had made.

Fred is on the right track, you need a conversion factor to take into account the difference in philosophy. It was indeed overbuilt. Back in those days, they built a motor that would win an argument, build a country, or in the case of that old GE motor, win a war.

I'd try to get a performance guarantee from the drive supplier. They will be more likely to make sure you have enough motor.

Robert

Register to Reply
Power-User

Join Date: Jun 2011
Posts: 135
Good Answers: 7
#19
In reply to #5

Re: Replacing Old Electric Motors with New

02/06/2012 3:53 PM

It seems to me that back in the 'old days' that the horsepower ratings were in Clydesdales, now they seem to be Shetland ponies.

__________________
It gets interesting when you put fuel and oxygen in the same molecule, without allowing them to react, YET!
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jul 2011
Location: UK
Posts: 18
#6

Re: Replacing Old Electric Motors with New

02/01/2012 3:53 AM

I would agree with the above comments but make a further observation in that in some instances it was possible to continually overload older motors and "get away with it". Considering there are now many hand held instruments now available that will measure electrical power utilised directly, I also would check the power (or if no suitable meters check the voltage & current) being taken by the motor and use this figure rather than just what is on the name plate.

You might even find that a smaller rated motor would do and save some energy (efficiency of motors being best at nominal power conditions)!

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#7

Re: Replacing Old Electric Motors with New

02/01/2012 5:25 AM

Why not using a gear motor if you only need 394 RPM ?

Register to Reply
Member

Join Date: Jan 2012
Posts: 5
#8

Re: Replacing Old Electric Motors with New

02/01/2012 8:13 AM

Hey guys, Thanks for all the comments and Fred is right on. Like I say, I have been working with and on this motor for 25 years. I have replaced a number of large mill type pedestal motors up to 1000hp in the past but they were all DC and there was a coorelation in DC concerning shaft size...etc. Some of the original motors were from the 1920's!!! The main reason that I cannot use a gearmotor for a replacement is that they are not made in this HP size. I've never heard of one or seen one being advertised and I usually watch what is available. Also, There is a gear reduction after the motor. This is for a slitting rolling stand in a steel mill. Very slow. Also the motor is across the line start and there is no "drive" associated with it. I would like to change that in the future but that is not on the burner right now. I am mainly concerned with the running torque of the newer motors verses the older motors. The original motor was a 1.25 S.F. and you never see that anymore. Unfortunatly there was only one of these motors made and I've been given a ballpark quote of 1/2 million for a new one. I am sure that one of the newer frame motors will work fine. I will need to make a transition base for it and a new coupling half but thats about all. Fortunatly we are only pulling 750 HP out of it right now so I think that the newer motor should work. I just hope we don't start seeing snapped shafts!..Thanks all.

Jim

Register to Reply
Associate

Join Date: Aug 2011
Posts: 41
#9

Re: Replacing Old Electric Motors with New

02/01/2012 11:41 AM

You might want to consider a complete teardown and recondition at a qualified motor repair facility. Some of the bigger shops GE etc. are very experienced and do excellent work. Why discard something that is apparently working well for you to take a chance on something that may or may not work as well. I find that with many industrial products constructed today that quality is not always a first priority.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2012
Posts: 5
#10
In reply to #9

Re: Replacing Old Electric Motors with New

02/01/2012 12:00 PM

I have already contacted some motor shops in the area. The motor is wound with form wound coils and a sample is necessary for the coil shop to make coils. They are talking 4 weeks down on straight time and 2-3 weeks down on full overtime rush basis. We have already cut out 2 groups of coils due to insulation failure on two seperate occasions and I know that this motor has got one foot on a banana peel. Unfortunatly, A steel mill cannot shut down for 3 weeks let alone 4. I use large motor shops all the time and we really have no control over their timing. The motor I am looking at using as a replacement is not a new motor and is heading for the motor shop before coming here to be retrofitted. It is a Reliance which was a pretty good manufacturer and I am guessing that the motor is about 20 years old. We will not be discarding the old motor. I will probably have it rewound with all the bells and whistles but it will be somewhere in the area of $80,000.00. I will feel better knowing that I have a spare available as we never did before. I just can't take the 3-4 week hit that a rewind is going to take. Big boss won't like that!

Jim

Register to Reply
2
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#11
In reply to #10

Re: Replacing Old Electric Motors with New

02/01/2012 1:08 PM

Over the last 20 years I've replaced or rebuilt half a dozen motors of similar size, mainly pulverizers & combustion fans in power plants. I must say I'm surprised you don't have a spare for this motor, since you say you can't stand a 3-4 week outage.

As others have said, modern motors are built much closer to the nominal spec than older units. I would not be overly concerned about the stator windings, other than to make certain that the replacement is designed for the environment. Steel mills are typically very dirty with abrasive and corrosive material in the atmosphere. They're also very hot places, so you'll need to verify the max ambient rating of the replacement is high enough for its new life.

As you implied in your comment about snapped shafts, the biggest concern is the cycling nature of the load. Torquing and relieving the shaft four times a minute will cause a lot more fatigue than most motors are designed to withstand. If the replacement is designed for a similar cycling load you should be okay. If the rotor cage is removed during the rebuild you may want to consider having the shaft tested for structural integrity. There are many options for testing. I prefer magnetic particle, dye penetrant or ultrasound testing, depending on the material under test. Search for a non-destructive testing firm in your area.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#13
In reply to #11

Re: Replacing Old Electric Motors with New

02/01/2012 11:17 PM

As the new motors are smaller than old ones,the inertia of rotor will be lesser than old one. If we consider the rotor as an energy storing flywheel,the new rotor will have less energy stored and therefore less efficient in handling load fluctuation or variation or even starting. Even the rotor shaft will be smaller and will it withstand the torsional forces required during starting?. Depending on the application,choice of the new motor should be done.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#14
In reply to #13

Re: Replacing Old Electric Motors with New

02/02/2012 5:36 AM

Justifiably remark Pnaban, GA from me.

Register to Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#15
In reply to #13

Re: Replacing Old Electric Motors with New

02/02/2012 7:15 AM

You make some good point, pnaban. The rotor will probably be somewhat smaller, although most of the size reduction in modern motors is in the stator, not the rotor. High-grade electrical steel has allowed designers to significantly reduce the mass of the stator punchings. The lower reluctance in the steel also means less copper in the windings.

Mass reduction in motors of this size is often accomplished by using a hollow shaft, but that may actually work against him in a cycling torque application like this one. One good thing in GopelT's application is that mill motors are usually started without process load, so the starting torque is minimal.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Register to Reply
Associate

Join Date: Aug 2011
Posts: 41
#12
In reply to #10

Re: Replacing Old Electric Motors with New

02/01/2012 3:18 PM

If you are going to go with a new motor I recommend getting the motor mfg's representative in to look at the application and if they want to bid ask for a guarantee that the motor to be supplied will work without problems. Put the monkey on their backs, CYA is always best.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#16
In reply to #10

Re: Replacing Old Electric Motors with New

02/03/2012 10:02 PM

Why don't you give full nameplate details of motor such as-make,country/year of manufacture,model/type, rated Amp,No-load Amp,PF,SF,Standard(BS/NEMA/VDE/IEC etc),Design code,Code letter(LRA/FLA),type of starter used etc?.

__________________
pnaban
Register to Reply
Member

Join Date: Sep 2010
Posts: 8
#17
In reply to #16

Re: Replacing Old Electric Motors with New

02/03/2012 11:09 PM

Yep. I want to see the Locked Rotor KW on that big bad boy!

Register to Reply
Member

Join Date: Jan 2012
Posts: 5
#18
In reply to #16

Re: Replacing Old Electric Motors with New

02/04/2012 12:06 PM

Hey Pnaban....You are spoiled. You guys actually have nemeplates on your motors? I have all the specs that came with this motor but you have to understand that this old motor was made during the days that all mill type motors and I daresay all motors over 400 series frames were made to order and there were no standards above a certain frame size. There might have been standards within a company (GE's MCE and MCF motors for example.) Therefore useful info that is normally found on a nameplate goes out the window on these guys. I can tell you that it is 1000 hp, 132 FLA, 394 rpm and 1.25 SF. There was only one of these made.....EVER. That was confirmed in 1986. We use an Allis chalmers FVR movable starter for this fellow and it is configured across the line start at 4160 volt. Really dims the lights. For those of you that have dealt with steel mill motors you know what I am talking about. Our mill was built in 1893. I have had the pleasure of working on some really unique motors because of this. Until recently we had 2 1000hp Kramer sets here made by GE in 1928. Ever heard of one of those? Thanks for all the good advice. I picked up a couple of tidbits I hadn't considered. We will be doing this job pretty soon and I would like to post the results later so you guys know what happened.

Thanks,

Jim

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

FEBalicki (2); GopelT (3); Lapin (1); lyn (1); machine builder (1); pnaban (2); pwr2thepeople (2); redfred (1); rudy.leurs (2); Scoutryder (2); TonyS (1); WJMFIRE (1)