The thermal overload relay (T25DU) curve goes from 1.05 x In to about 10 x In. You can use any value to test it. Not necessarily 1.50 x In. The lower the multiple, longer the time to trip,the more accurate the test.
ABB's superb automated assembly line at Heidelberg has so many quality checks on the way that they have >90% first-pass-yield. The line calibrates the relay at 2 x In. The curve shape having been set by the quality checks, one test point is enough.
You, as a user, should test at two points if you want to test at all. 1.5 x as you are doing, and 6 x In to simulate a locked-rotor condition.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Feed 1.00 x In for 2 hours, then raise the test current to the desired value. This is hot curve testing.
One small thing ...remember, you must use a stabilised current source, single-phase, all three phases of the relay in series. As the relay heats up, its heater resistances increase, so if the current is not automatically increased to compensate, you will get erroneous results.
__________________
Nothing worthwhile can ever be taught, it can only be learnt.
"Almost" Good Answers: