Power Consumption

04/29/2012 1:48 AM

There guys,

Please tell how this three terms relates with each others and how can i use it for wire size computation especially only one or two are mentioned. Is there a formula that connects the three?

1. KVA - power consumption

2. KW - power

3. Amperes - full load current

I have some ideas but i need a concrete one because i am always confused.

Ty in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: power consumption

04/29/2012 8:59 AM

Sigh. Did you at all even try to look up the electrical definition of KVA to amps. If you had you'd notice that KVA is a measurement of apparent power. Apparent power is a magnitude sum in quadrature of real power (KW) and reactive (imaginary) power. Now once you are capable of defining, calculating or measuring the apparent power a circuit will draw from a voltage source then you can identify the magnitude of the current that will flow through your wires. The magnitude of the current flowing through your wires will set a minimum wire thickness your wires must be to prevent catastrophic self heating from Joule heating.

Now I cannot clarify your confusion on these topics by just handing you an answer. You must do some of your own homework or the concept will never sink in. If you follow the links I've provided and study them but still have some confusion I'll gladly help to remove your confusion. I'll know if you studied because you'll start using the correct meanings for terms.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: power consumption

04/29/2012 9:36 AM

Save us all a lot of work in the future.

Use the charts that abound on the web.

American Wire Gauge table and AWG Electrical Current Load Limits ...

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: power consumption

04/29/2012 1:08 PM

Proper conductor sizing is based on only 3 things: amperage, length, and LOCAL CODES. But here's a harsh reality: the fact that you had to ask this question immediately identifies you as someone unqualified to perform this most basic of electrical engineering tasks. Please turn this over to a qualified professional before you cause a fire. This forum, and all others like it, are not a substitute for proper engineering practices.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: power consumption

04/29/2012 1:14 PM

Agreed!

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Power Consumption

04/29/2012 3:26 PM

Single phase KVA = VA/1000.
Three phase KVA = VA√3/1000.
KW = 0.746 HP.
KW = KVA cosφ, where φ = phase angle between V and A; cosφ is also called power factor.

Wire sizing is primarily by amps, but also depends on voltage drop, ambient temperature, cable configuration, and local regulations. [Repeating JRaef.]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #5

Re: Power Consumption

04/30/2012 11:46 AM

Ok, OK,

Proper conductor sizing is based on only 3, no, 5 things: amperage, length (because of voltage drop), ambient temperature, cable configuration and LOCAL CODES. ...

Do I hear 6?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: Power Consumption

04/30/2012 12:06 PM

Lets not forget insulation temperature range. Then again this is a little redundant. All of these attributes should be part of the local codes in the first place.

Then there are the wacky conductor sizing conditions that just aren't in any code book. 500 amperes of pulsed current into an ultra-high vacuum chamber that powers a superconducting kicker magnet for just one microsecond every ten minutes to four hours. Try to find that one in the NFPA 70.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: Power Consumption

04/30/2012 5:57 PM

Article 210.68.A.1 "Wacky conditions"

"You are S.O.L, good luck with that..."

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Power Consumption

04/30/2012 3:18 AM

British Standard 7671 should eliminate all confusion. If it doesn't, then consult a qualified electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2010
Location: UAE
Posts: 50
#10

Re: Power Consumption

05/01/2012 7:43 AM

hi guys,

Thanks for your interesting response. For a non qualified like me can you please tell how much amperes does the machine consumed if the nameplate indicates 10KVA, 400V.

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".