Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 7:13 AM

This has been bothering me for a while, i know that you use 600v/1100v cables on 415v systems, in the UK these cables comply with BS7870-3.40. What is the reason these cables are not called 415v?

Register to Reply
Pathfinder Tags: Cables 600v 1100v
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 11:42 AM

The 600/1100 is the insulation voltage rating of the cable. It has nothing to do with the system on which they are used. In the US, the 600v cable is used with 120v, 240v 208v and 480 v systems.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 2:33 PM

The insulation may also need to be rated for peak voltage rather than RMS. [?]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
2
Power-User

Join Date: May 2012
Posts: 159
Good Answers: 14
#7
In reply to #2

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 11:01 PM

exactly; that 415 V is RMS, sort of an average. The peak voltage is 1.414 times that. engineering also requires a safety margin. Not sure why anyone would lose sleep over this. Over-engineering is better than under-engineering

Register to Reply Good Answer (Score 2)
2
Associate

Join Date: Jun 2011
Location: ROUEN (in NORMANDY), 120 km from Paris, France, Europe, Earth, Sun Sytem, Milky Way, Universe.
Posts: 39
Good Answers: 3
#3

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 3:14 PM

Hello, Malby, how do you do?

1_600 volts is for Neutral or Earthing wires, 1000 volts for Phase wires (or said conductors).

2_Generally, 1000 V cables are foreseen to 660 V maximum service voltage (where neutral is 660/√2 = 467 Volts maximum of service voltage (in fact in 660 V system, Neutral is 400 Volts at maximum - compatible with 600 Volts of Neutral conductor insulation) This is for combustion of insulation and lightning protection level admittance reasons.

3_You are able to call them 415 V cables inside your schemes, but for the reasons above described, cable founders engrave '600/1000 V' to let the installator choosing a range of network voltages (under the phases and the neutral above-described voltages) This is why you are, outside your personal schemes, not granted to engrave '415 volts cable' on the external layer, except on your sticked labels (for numbering your scheme-cables, according to the possibility of pulling-off them).

4_I am retired but, as far I am concerned, Phase insulation rating is 1000 Volts and not 1100 V - May be a brand new mode!)

5_ 415 Volts is a network service voltage, 600/1000V an insulation voltage.

Have a good day, BRZK

__________________
That's all, Folks. Take some time to learn where you live...
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 4:02 PM

Quote brzk "1_600 volts is for Neutral or Earthing wires, 1000 volts for Phase wires (or said conductors)."


Not in the US. As I said, 600 v conductors are used for 120v, 208v, 240v, and 480v systems. Earthing, grounding or bonding conductors can be insulated or bare. Grounded neutral conductors are insulated with 600 v insulation.

Register to Reply
Associate

Join Date: Jun 2011
Location: ROUEN (in NORMANDY), 120 km from Paris, France, Europe, Earth, Sun Sytem, Milky Way, Universe.
Posts: 39
Good Answers: 3
#5
In reply to #4

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 4:12 PM

Hello WarEagle,

OK, noted. General European rules are quite different.

Except to put metal of swgr to earth and for earthing of outward installations, bare conductors are forbidden ( exception: power copper or aluminium busbars) because of pregnant lighning protection. Thank you for your kind answer, BRZK

__________________
That's all, Folks. Take some time to learn where you live...
Register to Reply
Participant

Join Date: Jun 2012
Location: Australia
Posts: 4
Good Answers: 1
#9
In reply to #4

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/16/2012 12:13 AM

They were not talking about US. They were talking about Europe. No-one cares about US voltages. Question asked for BS/IEC, not NEMA/IEEE

Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 10:25 PM

You are refering to BS7671.

The UK also uses 550V and 660V for industrial, so where do we set the standard?

I was brought up with 550V as the standard voltage on all our plants.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/15/2012 11:11 PM

BS 7671 gives current ratings of LV cables with pvc/xlpe insulation,copper/aluminium conductors,armoured/non-armoured finish made to BS6004,6231,6346,7629,5467,7211, 6724,6007,6883,6207,6500 but voltage ratings are not given. Cable manufacturers indicate voltage ratings in their price list and literature. In some tender documents 300/500V too was mentioned. I wonder why BS7671 or On site guide didn't advise appropriate voltage rating for selecting cable for 230V single phase and 400V 3phase use. As Megger tests are done at twice rated voltage 400V cable should withstand nearly 1000V.

__________________
pnaban
Register to Reply
Associate

Join Date: Jun 2011
Posts: 33
#10

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/16/2012 3:09 AM

Thanks for your thoughts, my main issue was recognising that the rated voltage is actually the insulation rating and calculated using the peak not RMS value. Thanks also for the ref to the BS7671! :) Hope this thread helps others too!

Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#11

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/16/2012 3:37 AM

I'm no Electrical engineer but I would think that if you used a 415v cable supply, by the time the power gets where it's needed the drop in voltage will affect the plant or whatever you're running, it's better to over supply & transform down to what you need, also you can supply more than one location with the one supply. If anyone disputes this please refer to the first few words of this reply.

Bazzer.

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/16/2012 5:55 AM

660/1100V refers to phase to earth (660V) and phase to phase (1100V).

So given a fault situation phase to phase voltage could appear as phase to earth. It would be an unusual fault on a star / neutral grounded system, but quite feasible with a delta system.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member

Join Date: Dec 2007
Location: Sydney Australia
Posts: 480
Good Answers: 35
#13

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

06/19/2012 12:16 AM

Think about it.... When you perform your insulation test, What voltage do you set the meter for???

For 240V circuits, we test at 500V.

For 415V Circuits, We test at 1000V.

The insulation has to be rated to twice the voltage of the circuit.

This also identifies whether the cable you have at hand is suitable for LV, HV or not at all!

Regards,
Sapper

__________________
It's all about the Boom! - MythBusters
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Utility Cables - Why 600v/1100v Cables are Used for 415v System?

10/18/2023 7:07 AM

Presumably because if they were, and the transmitted voltage were to rise by say 10%, then they would be under-rated.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bazzer Englander (1); brzk (2); cheeseslicer (1); jerrys (1); malby (1); pnaban (1); PWSlack (1); Sapper (1); TonyS (2); Tornado (1); wareagle (2)