Anonymous Poster #1

Exploded GRP Water Tanks

06/25/2012 11:23 PM

We recently had an incident where one of our GRP water tanks exploded and flooded the sorrounding areas with water. The defect liability period of the tank expired two weeks ago and when the main contractor was approached to rectify the problem, he advised that the tank exploded due to being filled with water to overflow level and was therefore not his responsibility. This is the second water tank that has exploded in the last 14 months and we are concerned about the safety of the other tanks in the building. Can someone with technical knowledge on design and construction of GRP tanks give me an insight in what could have caused the failure of these tanks. These tanks are 4 meters high and both tanks seem to have failed on the one meter height from the bottom at which point there is no continuity in the exterior reinforced steel channels. The rest of the 3 meters reinforcement channels are joint to the one meter channels with brackets. your feedback will be much appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Exploded GRP water tanks

06/25/2012 11:44 PM

Maybe this is the sort of tank you should have...You are obviously exceeding the loading capabilities of the design for the age and conditions that are present...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2
In reply to #1

Re: Exploded GRP water tanks

06/26/2012 12:39 AM

Is this the type design you have? What sort of internal support structure do you have?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#7
In reply to #2

Re: Exploded GRP water tanks

06/26/2012 5:55 AM

Thank you for the feeback. Below is more information regarding the issue.

The structure looks more or less the same except that the tank are each 4 meters in height with the lower panels being 1 meter each and the top panel being 2 meters.

The tank the recetnly exploded is a collection tank for grey water and therefore the water entry is purely dependent on the usage of the water in the building and there are therefore no level controls to regulate the water level in the tank.

The panels in both cases where the tanks have exploded have failed at the join located 1 meter above the bottom of the tank. At this point, there is disconuity in the external reinforcement channels which are continous the rest of the three meters to the top. The tank also has an open vent at the top in addition to the access manhole to the tank.

Hope this information helps.

Reply
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#23
In reply to #7

Re: Exploded GRP water tanks

06/27/2012 5:52 AM

Can you be more specific on the construction of the vessel?

By your description thus far it seems that it is constructed of annular rings about a metre high and these are bonded (glued) together to construct a vessel of 4 rings and thus 4metres high.

What is the diameter?

Being greywater it'll have an enclosed top, or lid, so as to allow control of odors.

Are the components of the tank filament spun?

Is it a hand lay up moulded set up built around a male mould? Or a female mould?

Does it have any annular re-inforcement, at or near the obvious joins in the segments? These may be the steel rings you mention.

Is it, in fact, cylindrical? Or square? Made up of modular panels fixed together by various means, and re-inforced by steel beams (girts)?

More info please.

Stu.

__________________
"Nothing, is as it seems." Dr Wally.
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#25
In reply to #7

Re: Exploded GRP water tanks

06/27/2012 6:15 AM

At this point, there is disconuity in the external reinforcement channels which are continous the rest of the three meters to the top.

I reckon your main contractor has these ass about. Should be continuous at the lower level with the extensions at the top or at least staggered around the tank perimeter. What you have here is line of weakness all the way around.

Do you have a copy of the assembly manual?

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#33
In reply to #25

Re: Exploded GRP water tanks

06/28/2012 7:58 AM

I agree with you. It sounds upside down.

__________________
Where's the KaBoom? There should be a KaBoom!
Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#3

Re: Exploded GRP water tanks

06/26/2012 2:01 AM

Note that if tank is filled to overflow level, then it becomes (potentially) a flow restrictor on the pumped fluid. The difference between air departing the vents and water departing the vents could add significant pressure to the tank and the weakest seams fail.

Trapped air is compressible and so a smaller vent can balance large water inflow UNTIL you try to push the water through.

The fact that the tank provider could so easily diagnose the problem (failure cause) and that you are not contesting it also indicates it is highly likely to be the case.

such failure would be seen as tearing and failure of apparently "good" material rather than a fatigue failure where the materials would appear rayed or degraded.

Do you have proper level controls for the tank?

Do they have a reliable backup?

Have they been tested and verified to be effective?

Are you filling the tank to capacity (overflow) and then shutting off teh pumps?

If this has happened multiple times and only for your group as customers of this suppleir, then it is something about your filling and usage process.

Do not be tempted to put in larger vents. The water shock (hammer effect) that will happen as the water hits the full/surcharge condition will still cause failure.

__________________
Just an Engineer from the land down under.
Reply
Power-User

Join Date: Dec 2008
Location: Australia
Posts: 143
Good Answers: 24
#8
In reply to #3

Re: Exploded GRP water tanks

06/26/2012 6:07 AM

A repeated failure of this type I find very strange.

Even operating the tank at over flow level is part of the tank design and shouldn't cause failure. The over flow is there to prevent overfilling.

I believe there is an Australian Standard (certainly I had to prove to mining clients once) that a tank couldn't possibly over-pressure (by 10kPag greater than atmosphere). The common rule of thumb I use is to make the overflow line diameter 150% of the incoming line - therefore not possible to have any significant pressure drop (and I would assume tank manufacturers / system designers would also do something similar).

Having said that if the overflow / vent is not properly designed, perhaps overpressure caused it. But I would like to see the full system design to be certain of this (P&ID, Process flow diagram, mass balances, tank deisgn specifications, etc).

Regarding other tanks onsite, as I can only think this is either a system design problem, or a manufacturer problem. And assuming same desing engineer and same manufacturer for all tanks, then there is definite doubt over the other tanks onsite.

Suggest bringing in an experienced process design form for an audit. Any of the engineering consultancies will be able to find the cause of this. If it then is tank manufacturer issue, then it is money well spent in ammunition against the tank manufacturer (warranty or not - bad publicity hurts).

Good luck,

Anthony

Reply Score 1 for Good Answer
Anonymous Poster #1
#9
In reply to #3

Re: Exploded GRP water tanks

06/26/2012 6:08 AM

Thank you for the information. The tank is for collecting grey water and does not therefore have level control as water flows freely from all points in the building.

The defect liability period for this tank only expired two weeks ago which was one year since handover from the main contractor and the tank should be therefore be relatively new. Overflow of the tank as highlighted in my mail is only based on hearsay and no supporting evidence from the contractor. I however want to establish the technical aspects behind the tank's structure and construction which could have been linked to the explosion before addresing the entire issue.

The explosion of the first tank happened a short period before handover last year and was therefore still with the main contractor and was rebuild by them.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #9

Re: Exploded GRP water tanks

06/26/2012 6:17 AM

Obtain a copy of the witnessed hydraulic test record/certificate for the tank. Find out how and why this test level/pressure (same thing - P=ρgh and all that) could have been exceeded. Something is wrong at process design stage for this to have been able to happen.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jan 2011
Posts: 668
Good Answers: 3
#4

Re: Exploded GRP water tanks

06/26/2012 3:05 AM

are the tanks subject to wide temerature changes? if so. do the tanks have relief valves?

Reply
Anonymous Poster #1
#12
In reply to #4

Re: Exploded GRP water tanks

06/26/2012 6:19 AM

The tanks are installed inside the building and hence not subject to wide temperature change.

They also have ope vent pipes and the access manhole covers are also not sealed as the rooms are always locked and can be easily lifted which can also help to act as a pressure relieve.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Exploded GRP water tanks

06/26/2012 3:19 AM

While replacing or repairing the tank, invest in overfill protection/prevention instrumentation and controls immediately.

This facility has been subject to the scrutiny of a HazOp Study, hasn't it? Why was this possibility not considered as part of that study?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#6

Re: Exploded GRP water tanks

06/26/2012 4:14 AM

It would be a good idea to immediately:

1. Take steps to lower current fluid levels in all tanks you have of this type that are near capacity.

2. Implement operational / procedural limits restricting capacity to each tank of this type.

The other comments are excellent, and I also suspect the tank ruptures are related to overpressure resulting from making vents designed for air deal with pumped liquid....

....but that's just a guess from the luxurious vantage point of not being in your shoes. A thorough investigation needs to be done, until that is accomplished you are essentially flying blind and cannot even begin to effectively devise a long term solution.

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #6

Re: Exploded GRP water tanks

06/26/2012 6:09 AM

If filling the tank can lead to the tank bursting, the possibility of its collapse while being drained must be considered too:

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#13

Re: Exploded GRP Water Tanks

06/26/2012 10:34 PM

AP,

Whatever the tank is constructed from, when the level reaches "overflow" it is merely full.

If the tank can't stand the loads of being full, then it's a substandard, poorly constructed tank.

No matter what the warranty period, to fail in service means that it had a latent defect, which is squarely the responsibility of the maker.

Sue 'em. Including collateral damage.

Then get product from a tank maker who knows what he is doing.

Cheers,

Stu

(Engineer + 30years in GRP constructions)

__________________
"Nothing, is as it seems." Dr Wally.
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#21
In reply to #13

Re: Exploded GRP Water Tanks

06/27/2012 5:32 AM

Caution: that is why the witnessed test report/certificate is of value. It would determine which party is going to win and which is going to lose - if it ever gets to litigation as a result of its uncovery, that is.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
2
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#14

Re: Exploded GRP Water Tanks

06/26/2012 10:55 PM

Generally speaking, the highest lateral pressure in a rectangular tank will be at approximately 1/3 the height of the water in the tank. The lack of continuity at the 1 meter level in the exterior reinforced channels suggests that the reinforcement is failing when the tanks are about 3/4 full. The discontinuity in the steel channels would be the first place I would look for a design flaw...

Reply Good Answer (Score 2)
Active Contributor

Join Date: Aug 2011
Posts: 17
#15

Re: Exploded GRP Water Tanks

06/27/2012 12:10 AM

Dear Friend, In case the tank is of depth/height 4m, the ideal configuration is to have 2m ht. X 2 panels or bottom panel of 2m & above panels of 1m each. The reason of panel tank failure occured due to it's liquid column. Since at overflow level, maximum pressure was exerted at 2/3rd depth, a panel of 1m failed as the pressure was exerted at the joint. This would be the only reason causing multiple failures. Other causes mentioned in other replies are also important design considerations but to my mind, the principal cause is using 1m panel in a 4m ht. of tank.

Reply
2
Guru

Join Date: Jan 2008
Location: "Springwood", North Tamborine Mountain. Qld. OZ.
Posts: 837
Good Answers: 28
#19
In reply to #15

Re: Exploded GRP Water Tanks

06/27/2012 12:56 AM

Man,

A tank is a tank is a tank is a tank.

All the musing in the world don't overcome the fact that it was: 1. designed wrongly, 2. made poorly and failed because of these factors.

A tank is supposed to be filled to full.

Someone said that 4m is an unusuallly large GRP tank. BS.

I installed a tank farm including vessels 5mdia x 10mhigh.

Properly designed, made (in China) and not failed.

We did have a failure of a PE tank on the same site, which was found to have a fault in the moulding process and was replaced by the maker FOC.

He had to. Wouldn't have got paid otherwise.

Without access to detailed construction drawings, lay-up analysis, test report, transport report, and site installation details we have no idea why this thing failed.

Properly constructed GRP does NOT fail.

Stu.

__________________
"Nothing, is as it seems." Dr Wally.
Reply Good Answer (Score 2)
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#26
In reply to #19

Re: Exploded GRP Water Tanks

06/27/2012 6:45 AM

5M Dia and 10M high is a cylindrical tank.Cylindrical tanks are available in all heights and diameters. Panel tanks of GRP are not generally available at 4M height. It appears a manufacturer has stretched the design to unrealistic levels causing failure.

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#27
In reply to #26

Re: Exploded GRP Water Tanks

06/27/2012 7:22 AM

That would explain the 1m extensions....

Maybe these failures are actually a design feature to prevent overflow.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Active Contributor

Join Date: Aug 2011
Posts: 17
#16

Re: Exploded GRP Water Tanks

06/27/2012 12:13 AM

I guess you may consider buckling of the joint owing to pressure of liquid depth as a cause.

Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#17

Re: Exploded GRP Water Tanks

06/27/2012 12:19 AM

Four meter is an unusual height for GRP tanks. Maximum 3m height is advised. The tank should not explode by filling to overflow level. the test pressure for the tank should be higher than the height of the tank. Another important point is temperature of water. GRP is very sensitive to water temperature and its strength will come down drastically as the temperature rises above 20 deg C which is generally the design temperature. If you have higher water temperature then you should set the overflow level lower but you will sacrifice the storage volume.

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#18
In reply to #17

Re: Exploded GRP Water Tanks

06/27/2012 12:52 AM

Seriously now...20ºC?

It doesn't get that cold here.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#20

Re: Exploded GRP Water Tanks

06/27/2012 3:58 AM

What have your insurers got to say about the tank failure?

Like others have said, the tank has to be able to survive being filled to the brim.

Interesting (bog actually) how the portion of the tank with the greatest loading is the least reinforced.

Better get a lawyer son.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Anonymous Poster #1
#22

Re: Exploded GRP Water Tanks

06/27/2012 5:45 AM

Dear All, Thank you for your valued feedback. It has been great help. As I am writting to you now, I have just come from clearing water from another plantroom which has been flooded after another grey water tank busted three hours ago.

We have contacted the main contractor and he has reluctantly agreed to call the manufacturer to investigate this failure. Coincidentally, the tank that busted today is the same size as the one that failed last week and it has also failed at the 1 meter height. I hope that the matter will be investigated in details and necessary action taked to reinforce or replace the remaining GRP water tanks.

This forum has been great help.

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#24
In reply to #22

Re: Exploded GRP Water Tanks

06/27/2012 6:06 AM

Reluctant? Scared shitless more likely.

If your main contractor has any nads then he should be giving the tank supplier a bollocking right about now.

One failing is a coincidence, but this many???!!!!

How many tanks are left? Are you bracing them up with timbers and straps?

Please accept my empathetic commiserations mate!

Grey water has a higher SG than clean water right.......hmmm.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru

Join Date: Jun 2006
Posts: 501
Good Answers: 8
#28

Re: Exploded GRP Water Tanks

06/27/2012 7:56 AM

Well regardless your next step is to get a good NDE company to do weld examanation as well as taking thickness reading to check for corrosion. While the forum can speculate, there is no substitute for real information.

Reply
3
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#29

Re: Exploded GRP Water Tanks

06/27/2012 8:07 AM

From what little we know of the actual design and erection of this tank it seems to me to be either:

1. A design flaw, especially in light of the dis-continuous steel girts at the bottom of the tank, where the highest lateral water pressure is occurring. The design of the girts is to take up the lateral load and act as a "tension ring".

and/or

2. There is a construction/erection error that lead to the failure.

In any case IF I were you I'd hire a qualified Structural Forensic Engineer to uncover the reasons behind the failures. I wouldn't rely on the tank manufacturer or the Contractor who installed them to discover the whole truth of the failures, because they have "vested" interests to cover their respective butts and pass on the liability and any future tank problems onto you, the Owner. Ask the Engineer for an Engineering Report. Also, inquire if they're capable of providing "EXPERT WITNESS" testimony in the event you decide you must recover "damages" in a court of law. After all, you have already spent big money buying and constructing these tanks in your facility. Therefore, cover your ass appropriately!

===signed,

CaptMoosie, PhD, PE

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply Good Answer (Score 3)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#30
In reply to #29

Re: Exploded GRP Water Tanks

06/27/2012 11:03 AM

and then there's the clean up costs.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Anonymous Poster #1
#31

Re: Exploded GRP Water Tanks

06/27/2012 2:22 PM

Once again thank you. Additionally the idea of involving a third party engineer to investigate the entire installation is a great idea. We have an other 5 tanks which are 4 meters high each, 2 tanks which are 2 meters high each and 8 tanks which are three meters high. Your feedback has been great help.

Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#32
In reply to #31

Re: Exploded GRP Water Tanks

06/27/2012 3:18 PM

You're very welcome AP #1.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#34

Re: Exploded GRP Water Tanks

06/28/2012 2:50 PM

My opinion is: the tank was designed as a 2 meter high module by the manufacturer. Supporting tie rods are located at the mid high point. By stacking 2 modules to create one tank, the juncture between the lower 2 panels becomes a weak point because the 2 meter high tank was designed to a 2 meter head. Stacking the modules increases the load on the bottom module to over 8 times. I'm making an assumption here based on the sketch provided by Solar Eagle. I'm not sure about the 8X, but 4X at least which should be enough for failure to occur.

__________________
Mr.Ron from South Ms.
Reply
Reply to Forum Thread 34 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ajwinemaker (1); Anonymous Poster (5); CaptMoosie (2); cwarner7_11 (1); durtieduck (1); JIMRAT (1); jmart23 (1); Just an Engineer (1); Learner42 (2); PWSlack (4); ronseto (1); SolarEagle (2); Stueywright (3); truth is not a compromise (1); TRV (2); Wal (6)