Iam working in 132/66kv grid station. there are transformer having specification 40/50 MVA 132/66kv,ONAN/ONAF,YnYno(star/star connectedwith solid grounded),HV side earth connected through CT having ratio 200/1A, provided with all protection system.The full load current on HV side is 218.5A(132KV) & the current on LV (66KV ) side is 437 A.The CTs connected on both side are 800-400-200/1A. The over current setting on HV side is 55%(215A) & on the LV side is 1.05%(420A). the earth fault setting is 10% on HV side & on the LV side is 15%. when we charged the transformer from HV(132KV) side it stood ok.but when we charged the transformer on other side ie 66kv side it show earth fault and transformer trip.After taking all necessary test of transformer,all the test are fond ok & match with factory result .when again the transformer charged it show the same result. the 132kv power is supply from another grid station.what is the problem.Is the problem is rectify by increase the time setting or the earth fault setting or the time setting or the earth fault setting is increased by other station from where 132kv line is coming. Is there is any other problem. plese help me.
with regards