N+1 refers to the redundancy built into the design.
'N' = Maximum load or rated loading for the site. Say 2 X 1.5MVA Diesel Generators for example.
'+1" = enough generator capacity to support that load if one unit fails. In this example that would be a third 1.5MVA Diesel Generator
So if you require 6 Generators then you install 7 for an N+1, for N+2 you you need to install 8 in this example.
As for N-1...Translates to lights out.... If you need 6MVA and you have less generator capacity than 6MVA, the generators will all trip out on overload.
The only way an N-1 could work would be load-shedding, where non-critical and non-important system are not covered by the Generators and allowed to remain powered off until the mains power is restored.
Regards,
Sapper
__________________
It's all about the Boom! - MythBusters
No, because then you would need 4 generators instead of 3, 5 instead of 4 and so on.
It is better to go with the minimum number of larger generators so that the Generators are running in the minimum load sweet spot (35-45%) rather than having more generators and they are all running at 25% well below the minimum.
As per previous discussions, diesel generators will have a minimum load requirement to prevent glazing of bores, damaged seals etc.
Regards,
Sapper
__________________
It's all about the Boom! - MythBusters
You don't need 4,3 would be ok because most probably only 1(N/2) may breakdown & the standby set will take over. Meanwhile you repair the defective one and keep it ready as standby.
I must respectfully disagree with portions of your statement. N-1 is standard terminology for determining the reliability of a system in contingency analysis, where 'N' is the total number of installed units. With N-1 design, the lost of the most critical (usually the largest) single component of a system will not cause any loss of function.
For generation, a system designed to N-1 reliability should be able to supply all loads within voltage and frequency tolerances after losing the largest single generator. For a transmission grid, loss of the most heavily loaded line will not cause overloading of any other line or a voltage deviation beyond design tolerance. Critical data centers are often designed to N/2 level, meaning loss of 50% of any particular component (generator, chiller, server, UPS, etc.) will not cause loss of data or reduce processing capacity below unrestricted operational requirements.
After reading the links you provided, seems I learnt something today... Thanks.
In data centres, redundancy is only referred to as "N+1,2,3etc"
In Power generation and distribution systems, seems that redundancy is defined as either "N+" or "N/" or "N-" depending on perspective, design and possible where you got your higher learning from.
Always a good day when you learn something!
Regards,
Sapper.
__________________
It's all about the Boom! - MythBusters
Computer data or voice or video could be recorded or stored using standby power but electrical energy storage is the biggest challenge requiring spare capacity or standby.
If I were you, I'd do a quick search for "N-1 generators". You won't find any, but you may find an explaination of "N" numbers as they relate to multiple generators.
You should know this for your next client, in case you are pressed for time.
N-1 is common when referring to electrical redundancy in transmission and distribution sysstems. I would read the customer as meaning that they want N+1 mechanical redundancy.
N-1 or N+1 terms have different references. When the operations engineer says N-1 design, he is meaning that the system is stable with trip of one of the machines.
When the designer says N+1,he is meaning that if N machines are required to supply the load, one additional (N+1) machine has been included in the design.
Thus, we can say for Operation security under N-1 contingency (loss or trip of one of the machines), the system needs to be designed with N+1 (required no. of machines to meet the load + 1 extra) machines.
two synchronised generators each capable of supporting the full load and thereby running at 50% each under normal operation and any one at 100% in the event of a single failure. would be N-1.
one generator operating at 100% with a standby unit of the same capacity waiting to take the full load in the event of the first croaking would be N+1
You could have N-1 capacity with N+1 redundancy. eg two 50% synched generators with a 50% standby.
(%s for illustration only)
I think I got this right......