Hi All,

we have issue on the level measurement on the tank.

on this tank we have install radar level ( rosemount ) and mechanical level.

The mechanical level range si 0 to 5M and the radar is 0 to 3.8M the problem is during the commissioning the actual level doesn't tally and both instrument is being calibrate? any advise

The liquid inside the tank is utility water.

Regard

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#1

Re: level measure

07/16/2012 8:32 AM

Describe the tank please - flat, dish or dome bottom? That can make a real difference on level readings especially with radar levels.

Also, this is very similar to having two readouts on an instrument. (local display and HMI from a PLC output) On the same instrument, they are never in agreement. Get two different instruments with different methods of measurement involved, and you create a real problem.

Having experience with radar levels, I would trust the mechanical level first. Radar levels are very good at reading sidewalls and sloping tank bottoms and not the liquid level.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Level Measure

07/16/2012 12:04 PM

Measure the liquid level in the tank with a stick.

Then decide which insturment is more accurate.

Disconnect the unused device to avoid confusion.

A man with two watches is never really sure what time it is.

Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#3

Re: Level Measure

07/16/2012 9:41 PM

I noticed that your ranges are different, thats going to give you different readings.I am not sure what Radar level you are using, but confirm you have the correct DK value and you mapped the tank.If both your levels are set up correctly the readings should be close to each other.

Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#4

Re: Level Measure

07/17/2012 7:35 AM

Just for my education: what does the M stand for?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#5

Re: Level Measure

07/17/2012 10:05 AM

Just curious as to what type of water storage tank you have there. I have lots of questions regarding this tank and the sensor installation.

Is it steel or concrete? EMF effects of steel tanks on the radar RF can play havoc with signal returns. Does it have a roof or not? What is the critical tank overflow elevation relative to the radar antenna elevation? Typical daytime and nighttime temperature ranges this tank sees? Is there a lot of water vapor present between the water surface and the antenna?

Was this a retrofit installation? And did a qualified Rosemount radar antenna technician install the antenna, or did your water dept. staff install it? Was it installed in an existing nozzle location in the roof or the tank sidewall? Was the nozzle too large or too small to properly accept

Was the antenna and the software "calibrated"?

High degrees of water vapor or wetness on the antenna can greatly reduce RF returns. Also, very clean clear waters, free of a high degree of suspended solids, can greatly effect RF returns. It is quite possible that you may be experiencing a higher level of return on a lower stratified water level or even the bottom of the tank or it's sidewall.

I would suggest that you contact Rosemount's technical support hotline or have one of their qualified technicians visit the tank site and render an expert opinion and corrective solutions that are guarantee to make this radar unit function properly. Have them warranty the corrective work for a period of no less than 2 years. They know their product line better than anyone else.

Finally, I would in the time being rely on the accuracy of the mechanical level equipment instead of the radar unit.

Here's a good article URL link regarding radar level sensors:

http://instrumentsignpost.wordpress.com/2010/09/10/radar-level-measurement-best-practice-pauto/

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#6

Re: Level Measure

07/17/2012 11:24 AM

How much offset do you have in the two measurements?

As mentioned; Scaling and ranging very much have an affect on difference in readings.

Changes in atmospheric pressure will affect direct reading mechanical level measurement results whereas they will not affect the RF readings.

Any projections, equipment, metal supports, suspended solids, etc into/inside the tank will also adversely affect the accuracy of an RF instrument.

Rent or buy a portable pressure (Piezo) level detector to measure the level then compare the readings to determine which device is correct.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Level Measure

07/17/2012 11:30 AM

"Rent or buy a portable pressure (Piezo) level detector to measure the level then compare the readings to determine which device is correct."

And what's wrong with using a stick?

Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#8
In reply to #7

Re: Level Measure

07/17/2012 12:12 PM

Absolutely nothing if degree of accuracy is not tight.

Since there is not an acceptable deviation in measurement range nor the difference in the two derived measurements stated, I'm not sure that taking manual readings is acceptable due to the accuracy required/displayed for the application/process.

Depending on the magnitude of the difference in readings between the two devices, the stick used may not have high enough resolution to accurately detect and/or display the resultant to the user.

Given that it appears the tank is at least 5 meters in height. (16.5 Feet)

If the difference in the readings of the two devices is let's say .0015 Meters and the stick cannot or is not inserted at absolutely 90 degrees to the surface, it would be easy for the reading to vary more than .0015M.

Contrarily; if the level accuracy is not critical and deviation is allowed at .01M or greater, then logically the manual reading being displayed would be subject to interpetation by the "reader" and the accuracy of the scaling on the manual level display device would most likely not be anywhere near as accurate as the resolution of the RF device and therefore use of a stick would clearly be acceptable.

Hopefully the poster is knowledgeable enough about the process to make the appropriate determination using the right equipment.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Level Measure

07/17/2012 12:18 PM

After re-reading the original post, several times, methinks you are being generous the poster.

Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#10
In reply to #7

Re: Level Measure

07/18/2012 4:54 AM

GA

Are we saying that "M" should have been "m" i.e. metres? In other words the problem of deciding which device is correct boils down measuring the depth of the tank!!

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Reply
Commentator

Join Date: Aug 2008
Posts: 82
#11

Re: Level Measure

07/25/2012 8:06 AM

Radar level sensor mounted in top ie Inverted height of 3.8M from top . Mech. Level range as 0 M starts from its mounted point in Tank . Relative difference in tank's height , if considered - will you have same problem ? , please .

Reply
Reply to Forum Thread 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

CaptMoosie (1); eltech (1); lyn (3); Phys (1); Randall (2); SHOCKISCAN (2); sivaa (1)

Previous in Forum: Liquid Service   Next in Forum: How ATMEGA16 Works?

Advertisement