Can any body tell me how to select CT for the measurement of DC current accurately, & with which parameter consideration.
Best Regard's
Ankur Malviya
Pathfinder Tags: Current Transformer
Re: DC Sence Current Transformer Selection
08/24/2012 10:05 AM
Rather than a CT, use a low resistance shunt and a voltmeter.
Good Answers: 34
08/24/2012 10:16 AM
How can you use a CT (current transformer) for measuring DC amps? Does a transformer work in DC circuits?
Good Answers: 73
08/24/2012 12:16 PM
There are a few Hall effect sensors that may read the DC component. A current transformer will not work because it will magnetize in the direction of the DC current flow in about 8 mSec.
For a CT to perform properly, you need to use it on alternating current. Specifically, it needs to be nearly the opposite polarity about half of the time or it will saturate in one direction and yield no signal.
Voltage across a small known value resistor (0.1 ohm?) is actually very accurate for calculating current as long as you are not heating it significantly.
Good Answers: 34
Re: DC Sense Current Transformer Selection
08/24/2012 12:44 PM
I agree wuth you.
Good Answers: 804
08/24/2012 1:03 PM
There are indeed DC "CT"s that look just like AC CTs, but you have to accept the alternate meaning of "CT" to be Current Transducer.
http://www.veris.com/docs/app/vn38.pdf
Good Answers: 34
08/24/2012 1:13 PM
The OP's Tag says current Transformer.
Thank you for the explanation & the link.
Good Answers: 804
08/24/2012 7:27 PM
Oops, you are correct. My mistake...
India - Member - New Member
Good Answers: 164
08/25/2012 4:49 PM
Er.. "DC Current Transformer" seems an acceptable term, at least in the US Patent Office...
http://www.freepatentsonline.com/20120063055.pdf
Anyway, i have seen several massive DCCTs 180,000/5A DC in a caustic soda plant (which used electrolysis). Don't ask me how they work though, i never bothered to find out in detail. This was in 1972 at Kota, Rajasthan.
Nothing worthwhile can ever be taught, it can only be learnt.
08/25/2012 4:56 PM
Welcome to the U.S.! Are you visiting, or staying for a time?
Good Answers: 164
08/25/2012 8:14 PM
i came at the end of May, mainly to play with my new granddaughter Hope to leave by mid-Nov, staying a few days short of the full 6 months allowed. My fifth trip since '82. America has sure changed in many ways, more of it in a good way, from a foreigner's perspective. The one downside is how expensive everything has become....
08/25/2012 9:16 PM
If there is any way that you could make it to Ketchikan (petrol > US$4), you will be a most welcomed guest! All love to your granddaughter and family.
Good Answers: 164
08/25/2012 9:37 PM
Wow... makes me feel very welcome, very warm. Thank you, friend ! Alas, i am not allowed to drive here (by my son and d-i-l, not the US DMV)so, i have to depend on them for even going a couple of miles But let me take a raincheck on it, i hope to come again sometime...here is a picture of my angel....
Good Answers: 169
08/29/2012 9:57 AM
KVS! Your lil' angel is so cute! My blessings to her!
Good Answers: 164
08/29/2012 10:30 AM
Thanks EE65 ! i will surely convey your message to the proud parents ....
Register to Reply 14 comments
electricalexpert65 (1); Joshi (3); JRaef (2); kvsridhar (4); NotUrOrdinaryJoe (1); Tornado (3)