I have replaced a 37 kw, 415V old induction motor which was drawing 40A, 415V, on loading and 30A in decoupled condition.
with a 15 kw, 415V motor which is drawing now 22A on loading and 12A in decoupled condition.
I want to know the actual kw, I saved. Assume PF of 0.85 at MCC bus.
As we know, the power factor of motor varies as per the loading of motor, so we can not calculate kw by simply measuring current.
Is there any thumb rule to calculate kw of motor on no-load condition by measuring its current? or any standard chart is there for motor current vs PF?
I found a chart which indicates 0.35 PF at no load, 0.7 PF on 50% load and .85 PF on 100% load. But my old motor was drawing 50% current on no load!