Anonymous Poster #1

Over Current Check

09/12/2012 1:45 PM

Sir,

I want to check a panel that always tripping due to over current. kindly tell me how to check the actual current passing through which triggered my ckt breaker to trip. by using multimeter.

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: over current check

09/12/2012 1:52 PM

Depending how much current is passing through the circuit, a multimeter probably doesn't have the capacity. You should know this by consulting the operator's manual.

It will also tell you how to check the circuit.

Use a meter with a clamping amp probe. Follow the directions on the meter.

Or, ask someone who is in the same room with you, so they will have sufficient information to teach you.

Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Over Current Check

09/12/2012 4:00 PM

Circuit breakers can trip from over-current or heat...Use a clamp-on amp meter to check for over-current, as stated above, and if current is within circuit limits, then use an infrared temp instrument to check temperature at lugs...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
4
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#3

Re: Over Current Check

09/12/2012 5:23 PM

I suggest you get an electrician

Reply Good Answer (Score 4)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Over Current Check

09/12/2012 5:31 PM

Yes, GA.

If the OP doesn't know how set up a multimeter or other device to measure current then they should not be trying to to do this kind of a test. The life you save may be your own child.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #3

Re: Over Current Check

09/12/2012 5:58 PM

He IS the electrician.

Reply
Guru

Join Date: Jan 2011
Posts: 668
Good Answers: 3
#11
In reply to #5

Re: Over Current Check

09/13/2012 1:20 AM

good one.

Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#16
In reply to #5

Re: Over Current Check

09/13/2012 5:54 AM

Not for long

Reply
Power-User

Join Date: Sep 2008
Posts: 196
Good Answers: 6
#18
In reply to #5

Re: Over Current Check

09/13/2012 8:16 PM

Scary, ain't it?

Reply
Commentator

Join Date: May 2011
Location: Brisbane, Australia
Posts: 62
Good Answers: 3
#6

Re: Over Current Check

09/12/2012 11:18 PM

He'd not even qualify as an electricians assistant in this country. I wonder if there's a Darwin Awards for unqualified people who do their own electrical work?

Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7

Re: Over Current Check

09/12/2012 11:30 PM

This is a joke, right?

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #7

Re: Over Current Check

09/13/2012 5:39 AM

If only it were....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Jun 2011
Posts: 2
#8

Re: Over Current Check

09/13/2012 12:06 AM

Generally in rainy seasons, the dust accumulated on the connectors and terminals absorb moisture and get shorted raising false alarms. This too should be checked in addition to assessing the through current using clamp-on ammeter.

Reply
Active Contributor

Join Date: Jul 2012
Location: kathmandu,nepal
Posts: 13
#9

Re: Over Current Check

09/13/2012 12:39 AM

at first u hav to check the settings of circuit breaker,then u hav to confirm that...what is the actual value of circuit breaking current of CB, apply the clamp-on meter for check the current in that circuit,and here u doesnot mention the voltage level...it may be either low/high voltage circuit.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Over Current Check

09/13/2012 12:50 AM

Use a power analyser or datalogger to record the variation of I,V,pf,W etc and check from the graph at the instant of tripping.

__________________
pnaban
Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#12
In reply to #10

Re: Over Current Check

09/13/2012 2:58 AM

Come on mate! The OP can't operate a multimeter and you are suggesting a power analyser?

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #10

Re: Over Current Check

09/13/2012 3:09 AM

Ye gods...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Oct 2010
Location: Hyd - IND
Posts: 21
#14

Re: Over Current Check

09/13/2012 3:10 AM

please mention clearly the tripping switchgear rating & connected load etc., using multi meter u cant able to measure the current, u need a clamp meter/tong tester to measure and also its impossible to measure instantaneous current/tripping current by clamp meter, normally it will exists micro seconds. please chek the over current setting in your switchgear, normally it will be in % x In. ensure there is no fault in load side.

__________________
Shaju Khan
Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#17

Re: Over Current Check

09/13/2012 11:11 AM

"Anonymous Poster" should not be allowed for initial posts. I think this would deter these type of questions.

I think Lyn does this to spark discourse...not really

Reply
Power-User

Join Date: Dec 2008
Location: Anthem, AZ
Posts: 392
Good Answers: 8
#19

Re: Over Current Check

09/14/2012 1:57 PM

I doubt if your multimeter has the speed to capture that transient (most of them average the data to get a stable reading).

Use a scope with an external trigger which would be fired by your ckt breaker. The scope needs to be set up to capture mostly pre-trigger data so you can see exactly what happened to the current before the breaker tripped.

Reply
Reply to Forum Thread 19 comments