A MOVING-COIL INSTRMENT GIVES A FULL-SCALE DEFLECTION WITH A CURRENT OF 15 MA.CALCULATE THE RESISTANCE OF SHUNT NECESSARY TO CONVERT THE INSTRUMENT TO AN AMMETER GIVING A FULL-SCALE DEFLECTION WITH A CURRENT OF 0.1 A; IF THE RESISTANCE OF THE INSTRUMENT IS 4 OHMS.
Good Answers: 1693
Re: Electrical Engineering
09/16/2012 2:13 PM
That's on page 345 of your text book.
Good Answers: 34
09/16/2012 2:24 PM
Is the question complete in itself, to lead us to an answer?
09/16/2012 3:19 PM
Please turn off the all-caps; the forum doesn't like shouting.
09/16/2012 3:26 PM
Choosing a resistance value is pointless in this case as it is impossible to read 0.1A off of a moving coil display with a full scale deflection of 15,000,000 Amps.
09/16/2012 4:13 PM
15 Mega-amps? Jee willikins! You don't half have to invest in some step-up equipment, Mildred!
Good moaning!
Good Answers: 116
09/16/2012 6:59 PM
For a full scale deflection of 15 milliamps [I] with resistance of 4 0hm [R], apply the standard formula for voltage V across a resistor R carrying current I, note the formula assumes units of volts, ohms and amperes :-
V = IR = I x R
Note: this comes from Ohm's Law, I = V/R, by multiplying both sides by R, hence RI = VR/R. Since R/R =1, RI = V and hence V =IR. By similar algebra, R = V/I.
For given values ( 1 milliampere (mA) = 0.001 amperes) of 15 mA and 4 ohms :-
V = 0.015 x 4 = 0.06 volts = 60 millivolts.
To get 0.06 volts at 0.1 amps across a circuit formed by the shunt in parallel with the meter resistance of 4 ohms, then the shunt must drop 0.06 volts at (0.1 - 0.015) = 0.085 amps (the meter carries the rest of the 0.1 amp).
So, applying R = V/I to the shunt of resistance r ohms,
r = 0.06/0.085 = 0.70588 ohms.
Check 0.70588 ohms x 0.085 amps = 0.0599999 volts
In practice, you will find that a 1% accurate shunt is easy to get, the price and availability of an 0.1% accurate shunt is much more challenging, but 0.01% is very rare and expensive. So 0.07059999 ohms as a check result is good enough.
Regards,
67model