How we can test the vector group of transformer. If the client wants to confirm that the vector group is Dyn11 as indicated in the transformer name plate, how it can be done?
check these
Transformer Vector Group
vector group of transformer
Dear Mr. Johnsly,
In this CR4 Forum itself, plenty of postings made and you can search here in CR4 itself and get the details.
DHAYANANDHAN.S
The following is the procedure for Vector Group Test of a Dyn11 trafo.
i) Bond terminals 1U & 2u with a 2.5 sq.mm Copper wire.
ii) Apply 3 phase 415V, 50 Hz. supply to terminals 1U-1V-1W
iii) Measure the voltages across the following:
1U-1V, 1U-2n, 1V-2n (Equation: 1U-1V = 1U-2n + 1V-2n)
1V-2v & 1V-2W (Equation: 1V-2v = 1V-2w)
1W-2v & 1W-2w (Equation: 1W-2v > 1W-2w)
With the measured voltages, confirm that the equations in the brackets are true. If so, the trafo is Dyn11.