Generator Question

09/23/2012 9:51 AM

is there any chances of winding failure if external supply accidently fed to generator ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: generator

09/23/2012 10:06 AM

Yes. Or, no. It depends on a lot of information that isn't provided.

Register to Reply
Participant

Join Date: Sep 2012
Posts: 2
#3
In reply to #1

Re: generator

09/23/2012 10:29 AM

The Dg was not running Changeover contactor failed and ext voltage fed to dg.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: generator

09/23/2012 11:32 AM

Did the dg quit working after the contactor failed?

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5
In reply to #4

Re: generator

09/23/2012 11:57 AM

Post #3 said: "The Dg was not running"

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #5

Re: generator

09/23/2012 12:06 PM

"What we have here is failure to communicate". The warden in Cool Hand Luke.

I meant does the generator work now, after the incident? Did the incident cause the generator to fail?

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#8
In reply to #7

Re: generator

09/23/2012 12:36 PM

I humbly agree. It appears, the OP is hesitant to crank his generator.

Scenario one: The generator was off. Normally the utility load is connected to common point of changeover switch & the other two ends, at opposite end are for grid & generator out put. Then I don't understand how can this happen?

Scenario two: Same logic, generator running with out put connected to load, when followed, does not help either.

Was grid supply directly fed on purpose, some bizarre experiment, or had I had one too many?

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15
In reply to #3

Re: generator

09/24/2012 5:20 AM

Basic tests.

  1. With generator isolated, measure resistance from each line terminal to neutral. If you do not have an ohmmeter, a lamp and battery will do. If one phase is more than a few ohms (usually far more) or lamp does not light, you have a broken winding. Test field winding resistance also, if accessible.
  2. Turn the engine by hand crank, if available. Decompress by lifting exhaust valve if possible. If the engine can be turned 1 revolution without jamming, sudden resistance or bad noises at least you do not have any seriously loose parts.
  3. If you can't or won't do 2., then you can force the fuel pump to zero delivery and hold it there (many engines have a mechanical stop lever/pull which does this, or a solenoid operated one which can be energised for a few seconds). Operate the electric starter to turn the engine [obviously, this is more risky than 2. above]. If this all sounds good, take off temporary "fixes" and try a start with fuel.
Register to Reply
Commentator

Join Date: Aug 2012
Posts: 68
#2

Re: generator

09/23/2012 10:25 AM

Yes you can rewinding your generator just tell us about the generator .the type .brushless or brush exciter .single or three phase .the frequency 50Hz or 60Hz

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6

Re: generator

09/23/2012 12:05 PM

It's all a matter of scale.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: generator

09/23/2012 12:56 PM

It depends on whether the reverse power relay and circuit breaker (if so equipped) operated successfully.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#10

Re: Generator Question

09/23/2012 1:24 PM

It really gets down to how much luck you have. I've seen generators back-fed to the point they were motoring and they were fine. I've also seen brand new generators get smoked even though the feeder opened on instantaneous. Certainly you should have the windings tested properly if this is a commercial unit. If it's a little home unit and you screwed up on the switching control then figure out what you did wrong and fire it up and see if it still works.

Your statement "The Dg was not running Changeover contactor failed and ext voltage fed to dg" doesn't make sense or at minimum, is missing a lot more information. If you are using contactors then you should have a proper interlock method, preferably mechanical.

I've lost count of how many times I've seen contractors get line and load cabling reversed.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#11

Re: Generator Question

09/23/2012 7:03 PM

Damage is not to the alternator but to the turbine bading, some more info = google

Regards JD.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#12
In reply to #11

Re: Generator Question

09/23/2012 8:54 PM

I didn't know your first name was Paul.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#13
In reply to #12

Re: Generator Question

09/24/2012 1:04 AM

Its not, it's John?

Regards John.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Generator Question

09/24/2012 3:31 AM

Why did the usual circuit protection device(s) fail, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply