Hi,
I am looking for information on French and American electrical standards and legislation relating to ungrounded dc floating supply systems, specifically relating to earth monitor protection systems. We have a production system manufactured by a French/American company which is a process electrodialysis installation, it has a 550v floating d.c. supply and load current of 400 amps. I am struggling to convince the suppliers of the requirement/ need to provide, what I believe to be basic personnel protection.
In the UK the wiring regulations covers this installation requirement under section 411 Protective Measure: Automatic Disconnection of supply, which more less states for an I.T. (floating) supply an earth monitor must be provided which must alarm when one pole develops an earth fault and disconnect the supply when the second pole becomes earthed.
I beleive that in the USA this requirement is covered in NEC 250.4 (B) but I am not sure whether or not this is regulatory requirement, I don't know anything about the French standards of protection.
If anybody has any information that might assist me in convincing the equipement manufacturer that this protection is essential please let me know.
regards